Excessive Condensation - Revisited

16 years ago

I started a thread a few weeks ago about excessive condensation forming on the supply plenum and the first 1' - 2' of supply duct off the supply plenum and on the humidifier's bypass duct. This on my new Carrier HP, oil furnace and coil.

The installer came back and verified the charge and added insulation to the supply plenum only. My equipment is in the basement of my home. Next week I will have a new dehumidifier and condensate pump to help reduce the basement humidifier.

The problem continues. I would like to describe the conditions and see if you can tell me if they sound proper.

The basement temp and humidity are both in the mid 60s. The upstairs house thermostat is set for 75 degrees at night and 76 degrees during the day. The unit has a dehumidification mode which I have turned Off because of suspicions I have that that was contributing to the condensation problem. The basement has a newly installed return and I keep the two basement supply registers shut.

It has been in the low 80s here in the DC area the past few days. The thermostat typically reaches the daytime set point (76) in the early afternoon and the heat pump runs to bring down the temperature. After an hour or so the inside fan goes to a very low speed and continues running for hours. (Remember, I have turned Off the Dehumidification feature.)

Two things particularly confuse me:

1) The continued running of the HP with very low air-flow would seem to be the cause of the condensate forming. I don't understand why it is running all that time as the set temperature has already been reached.

2) At the outside unit, condensation is saturating the mulch on one side. The lines attach to the outside unit at the corner adjacent to the wet area. Is this normal?

I will of course tyalk to the installer on Monday, but I'd greatly value your input.

Comments (13)

  • 16 years ago

    The source of the condensation outside is seen to condensation forming on the metal "device" (Valve) at the point where the large insulated tube connects to the unit.

  • 16 years ago

    the suction line (the big copper line) should be insulated from the indoor coil to the outdoor unit at the service valve (brass looking thing). The service valve will sweat and once inside the unit, most mfg do not insulate the suction line and it will sweat also. Normal.

  • 16 years ago

    Tnx Doug,

    The suction line is insulated right up to the (sweating) valve.

    What about the HP running for hours while at the set temperature and the dehumidification feature turned off?

  • 16 years ago

    The indoor blower should only run when the compressor is on, a one minute slowdown period after that if you have a var spd blower, or you have the FAN set at ON on the tstat. Outside of that I would have it looked at, preferably cold inside, compressor off, and the tech seeing the indoor blower running. As an aside, I see this contributing to indoor humidity, but not excess condensation. The blowing air would actually dry out the coil slowly. The condensate is formed by warm air going across the cold indoor coil.

  • 16 years ago

    I should have better identified my setup. New Carrier Equipment. Oil Furnace and Heat Pump. Two stage HP. Variable speed blower. I will verify what is happening, but what I believe I am seeing is that the Heat Pump comes on to cool the house late in the morning. It runs at Single Stage for a while and then shifts to two stages of cooling. What happens next is that it goes back to single stage, very low fan speed, and stays that way for hours and hours.

    If the inside humidity was high, this is what I would expect. However, the inside humidity is low (~45%), the set point is the default 60%. And, I turned the dehumidification feature Off at the tstat.

    The fan is in Auto.

    During those hours that the Heat Pump is running, condensation is forming on the outside of the Supply Plenum and the adjacent supply ducts immediately off the Supply Plenum.

    What I don't understand is why is the HP continuing to run for hours after reaching the set temperature. This is my first heat pump and I have no experience whatsoever as to what is normal.

  • 16 years ago

    I feel your pain. That's a nice system there. For one thing, the low speed running "forever" is undoubtedly why you have alot of condensate. That coil is COLD and since theres no time off, the plenum is colder than normal IMO, even the insulation you have can't handle it. We need to find out why it runs for hours on low speed. Lower 80's outside is hardly any heat load at. I'm suspecting the settings in the air handler area, but thats a guess.

  • 16 years ago

    srercrer,

    So it is not normal for the variable speed inside fan to run at very low speed for hours? Yesterday was a little warmer here. Near 90 degrees outside. My thermostat is set for 75 degrees at from 4:30 PM until the morning. It is set at 76 degrees during the day.

    Yesterday the Heat Pump ran from about 10:00AM until at least 9:00PM. Most of the time the variable speed fan was running at slow speed and the outside fan was running and the supply duct off the plenum was moist on the outside.

    The in-house humidity was in the 40s, the basement humidity and temp were in the 60s, and the house temp matched the tstat setting.

  • 16 years ago

    I have a brand new Carrier Infinity HP system myself in the MD (DC Metro) area and have not had excessive running of my system. It does run a lot during the days of late (since we have hit the low/mid 90s a lot), but it does cut off. It even goes into high when it gets real hot outside. What you are describing doesn't sound quite right. I would call the installation company to take a look. You spent a lot of good money for that system.

  • 16 years ago

    emarston,

    I'm in Rockville. Yesterday was your system running all afternoon?

  • 16 years ago

    I'm in Laurel. I actually have 2 systems now, but they actually did cut off for periods yesterday. They are both running on low speed at the moment (temp is currently 90) and are set at 74 @50% humidity. I know when they hit high cause they are a little louder (I can actually hear them very faintly when near the window). The upstairs unit runs more due to the higher cooling load, but it does still shut off. I also added a return and supply to the basement and now I have zero humidity issues in the house. The only condensation I see is outside where the line set connects to the outdoor unit and the condensate drain lines.

    My experience has been very different from yours. While my run times are long they do stop for periods of time (eventually).

  • 16 years ago

    emarston,

    Your post is most helpful. I have my tstat set at 76 @ 60% Humidity. The humidity is in the mid 40% range. The house temp is being maintained at the set 76 degrees by the unit running at a very low fan speed continuously. Like you, I had a return added from my basement to help control humidity but unlike you the humidity in my basement remains high. (I have a dehumidifier now on order.)

    I will gather a little more info and call my installer.

    I pass thru Laurel about once a week on the way to the Ft. Meade Commissary - I'm a Retired Navy Submariner.

  • 16 years ago

    Very nice! Thank you for your service!

    My humidity stays in the mid 40s as well. Is your basement completely cut off from the rest of the house? maybe you should open one of the vents to improve circulation. I currently have 2 of 4 open. It is a bit cooler down here, but I prefer it that way. High humidity would be immediately noticeable as I have carpet in my basement. My basement door tends to open and close a lot too(small child running up and down) so that probably also increases the mixing of air.

  • 16 years ago

    My basement door to the upper floors is ALWAYS open. I have a house cat and his litter box is in the basement.

    I took your suggestion and just opened the two vents in the basement.