Warm climate - return high or low?

12 years ago

Hi folks,

We have ended up with a somewhat nutty HVAC layout in our house. We have a 130+ year old house in SE Louisiana, with a flat roof, so that has made things challenging. We are going to have four different systems split between two flours, two per floor (basically front and rear of house).

Now for the one in the rear of the first floor, the return is going where there is going to be a pantry. The HVAC contractor and my GC both feel very strongly that it should go on the floor, as hot air rises and they are concerned that we will be unhappy and uncomfortable in the winter if the return is at the top of the pantry. My hesitation with this is that putting the return at the bottom will take up 25 inches of our pantry (i.e. it will only begin at 25 inches off the ground).

They both seem to feel quite strongly about this, but are willing to do whatever we wish. So I just wanted to see if any folks on here had opinions.

Thanks in advance for any thoughts!

Comments (6)

  • 12 years ago

    I'm not sure exactly what your question is so i will only comment in general. Heat does rise and you likly have higher than normal ceilings where heat will try to stratify. Returns near ceiling and discharges near floor will best circulate air to keep tempature closer to even throughout living space. Returns near floor with discharge near ceiling is a better arrangment for heat than both near ceiling. I would base 99% of hvac dicissions on cooling in coastal La. and let heating fall where it may.
    For better responses it might be better to post the intire return/discharge arrangement proposed.

  • 12 years ago

    I rented a house in urban Jefferson Parish for two years. It was a small house, raised with uninsulated floors. Supplys were high and it had one, central return in the hallway. Ceilings were 9' with arches between hall and LR and LR, DR and kitchen. Stratification was the word. I was much more comfortable in the winter when I supported a box fan on a laundry basket on the floor under the return, blowing up.

    Owned a 1950 house on a slab had high supply and low central return. No comfort problems. House was Katrina'd

    Rented a small raised 1940ish house with two low returns (on the opposite sides of the same interior wall). High supplies heated the house fine. Window units for cooling. That house almost certainly had gas wall furnace or floor furnace and ducts were added on. Puttting the multiple vents up high and two low with a furnace in the attic was the easy way, but it worked.

    Now in a 1940ish raised house with central low return. and ducted heating and cooling. No real problems but exterior ducts were inefficient so I bagged all that and put in 7 mini-splits (3 outdoor/7 indoor) when it needed an overhaul. There is some stratification with those. Manually switching to high speed or using a ceiling paddle fan makes it OK.

  • 12 years ago

    Ideally, the return should be opposite your supplies to aid in air mixing and help prevent "short circuiting" of supply air (though that can be avoided with proper register placement even if returns are at the same height as the supplies)

  • 12 years ago

    Thanks so much to all for the responses - much appreciated. Thanks especially, Ionized, for your detailed response - we are in NOLA too, perhaps our paths will cross some day (or perhaps they already have).

    I happened to speak to another HVAC fellow today (jury duty), and after explaining to him, he said, "definitely, definitely low." So I guess that is what we are gonna do, we'll just give up some space from the pantry. C'est la vie.

  • 12 years ago

    "The HVAC contractor and my GC both feel very strongly that it should go on the floor, as hot air rises and they are concerned that we will be unhappy and uncomfortable in the winter if the return is at the top of the pantry."

    The ceilings in my first and second floors are 8 feet high. The returns on both floors are near the ceiling. Last winter the temperatures went below zero. The house was comfortable on both floors, so I can't agree with the idea the position of the return is going to affect your comfort in the winter.

    If you were the measure the centers of the low and high positions it probably comes out to about 6 feet. I don't think you are going to see much difference at that distance.

    If it were my house I would install it above the pantry and make it big enough the meet the air flow needs. A bigger high return will out perform a smaller low return.

  • 12 years ago

    " The house was comfortable on both floors, so I can't agree with the idea the position of the return is going to affect your comfort in the winter."

    My experience in this climate indicates that this is very dependent on other characteristics of the house. The OP might find this is true if well sealed and insulated. if the house is raised and somewhat leaky and poorly-insulated, I predict similar results to what I found in such a house here.