trane systems

18 years ago

Hi, you sounded so helpful to "nate" so Here is my question

I have 4TWX6048B1000BA with air handler 4TEE3F48A1000AA (both trane and both installed recently) Arizona needs an EER not lower than 11.5. Is this system OK?

jeannie

Comments (10)

  • 18 years ago

    also we put in a 2twr30421000AA and the air handler is 2tGb3f42a1000ab do you know the seer, eer and hspf of these. We put in 8.4 Kw of solar, so the trane guys no we are green, I hope these are credit worthy. Is it normal for the techs to empty the old coolent from the old system into the atmosphere? That is what they did, I questioned him and he looked a little scared.

  • 18 years ago

    4TWX6048B1 and 4TEE3F48A1 (ARI-rated match):

    11.30 EER, 14.75 EER, and 8.70 HSPF.

    The heating capacity for this match is not even 3.5 tons of heating for a 4 ton system. That's one problem about Trane heat pumps; they have low heat outputs.

    -----------------------------------------------------------------

    2TWR3042A1 and 2TGB3F42A1 (ARI-rated match):

    11.10 EER, 13.00 SEER, and 8.00 HSPF.

    The heating capacity for this match-up is just over 3 tons at 37,000 BTU/H (3.5 tons should be 42,000 BTU/H).

    I got my information from the American Refrigeration Institute (www.aridirectory.org).

  • 18 years ago

    Good reply, Ryan.

    For the 16i heat pump, the 3F49 air handler puts out 47,500 btu cooling, 11.2 EER, 15.5 SEER, 43,000 btu heating at 47F, 9.1 HSPF.

    These numbers are still week for such a hi-tech dual stage compressor unit.

  • 18 years ago

    So why did they put in the air handler unit for the 4T. The 2T was an emergency (we had dad in hospice) then the air handler was retrofitted to a small attic space); but the 4T was done with pleanty of time and good attic space.Was there a better air handler for our 16i. Should I be distressed? I guess we didnt make the cut for arizona standards, but can we get the federal tax break? Also, do heat pump installers often let the coolent go into the atmosphere?

  • 18 years ago

    There wasn't really a better air handler for your XL16i. That's Trane's top-of-the-line variable-speed air handler (4TEE). Trane just has problems pushing those numbers to the place where other manufacturers like Amana and Carrier are. Trane is solid equipment; they are just lacking in terms of efficiency and capacity for heat pumps. It's not a good idea to let R-22 refrigerant out into the atmosphere. R-22 is bad for the atmosphere, which is why R410a equipment is being used more commonly. I doubt the technician who let that refrigerant out into the atmosphere was EPA-certified (EPA = Environmental Protection Agency). All refrigerant should be recovered. Good luck to you.

  • 18 years ago

    The 4-ton 16i does not qualify for the $300 Federal Tax Credit. The system must be 9 HSPF, 13 EER, and 15 SEER (all 3 must be met).

    I would ask Mr Trane about the air handler choice when a better match exists. Hope he told you the truth about the Tax Credit. You do get a $50 Tax Credit for the variable speed blower in the air handler.

  • 18 years ago

    Thanks garyg and ryan. These guys have been our Trane guys through 2 houses. They are there when we need them. I will ask, they may have told us, and we didnt understand. We didnt think about going with another brand because we have lived with the reliability of trane forever. I did lecture the tech about the atmosphere. He knew better. You helped alot. The tax credit isnt that important. we put in 8.4 KW solar this year, it was commisioned 9 days ago and we have saved the world from inhaling about 600 pounds of co2. It is fun to watch our electric meter run backwards. The trane guys did tell us how to use our systems, no sudden ups. We keep the house at about 65 and I am sure it is more efficient then the old system.Merry Christmas!

  • 18 years ago

    Jeannie:

    In the long run, it doesn't really matter much that the performance numbers aren't the best in the world at this time. What really matters is that you have 2 brand new, high-quality systems, installed by pros, that will hopefully last you 15 years minimum.

    Best to you and Merry Xmas!!

  • 18 years ago

    Venting refrigerant to the atmosphere is illegal and subject to a hefty fine, so I'm not surprised that your guy looked "a little scared."

  • 18 years ago

    I thought i had it fixed last year?... theremostat was replaced adn something in the attic.. a fuse or relay switch, something was replaced, for the heat box in the attic. The heating shuts down and than a few days later it works again for a couple of days. One morning I woke up to cold blowing air! I'm guessing it's the fan blower, I figure I can replace that. Any advice????