Easy Touch problem

18 years ago

Either I have a problem with my Easy Touch 8 installation or I don't understand how to program it. I've studied all the helpful posts I can find and am still lost. This is a wonderful forum and I'm hoping one of the many experts out there can shed some light.

What I want to do is run filtering at speed 2 at night and have the pump (an intelliflo 4x160) increase from speed 2 to 3 when solar kicks in and back to 2 when solar shuts down.

The three way solar valve opens when temp differential is reached but the pump does not come on. The only way I can run the solar is if the pump is already on. I can't figure out how to program that.

On checking over the wiring I noticed that the pump was wired from the circuit breaker to the filter pump relay and then to the pump. I read on an older post that this is incorrect as the intelliflo is meant to always be on. I changed the wiring to go directly from the circut breaker to the pump but now it won't come on except manually.

With the power off I carefully checked the wiring in the motherboard. All the sensors are wired in correctly, the valve actuators cables are in place which is not a surprise as the valves work as they should. However, the electrician ran the RS-485 cable from the pump to the IS-4 remote, J-22. The RS-485 cable has two wires, a yellow and a green. I believe they should be connected to the com-port, J-20. The Com-Port has four wires, red, yellow, green and black running back to the motherboard itself. Is it safe to assume that I should add the yellow to the yellow and the green to the green, RS-485 to J-20. I want to be sure and not damage the electronics. If this is the correct wiring will this solve my problem or is there something else I would need?

Thank you.

Waterouzel

Comments (11)

  • 18 years ago

    I don't think you have a bad system. I think that it is not wired correctly. Repair_guy would be better able to help you than I will but I believe that the 4X160 with the Easy Touch needs to be wired through a relay and that the yellow and green wires need to be hooked to the yellow and green on the com port.

    I would wait for a replay from someone more knowledgeable on this than myself.

  • 18 years ago

    The pump was not installed properly. Looking from left to right on J20, you put the RS-485 green to #2 and yellow to #3.

    Make sure solar is enabled. Select no to heat pump in place of solar. Make sure the solar actuator is in valve port A.

    You'll need to set the solar differential. Of course, use the Easy Touch to set the speed for solar.

  • 18 years ago

    Thanks for the help. I'll make the change tomorrow. I'm still not sure if the intelliflo should be wired directly to the breaker or from the relay.

  • 18 years ago

    To the breaker

  • 18 years ago

    Thank you repair guy! Bad weather has kept me from outside work but the sun came out today so I rewired the easy touch as to your instructions and it works! But I'm curious, the relay labeled filter pump is not being used and yet it activates whenever the pump comes on. With this setup is it possible to use that relay for something else? I don't really need it at this point but I might later.

    Thanks again.

    Waterouzel

  • 18 years ago

    In most cases, the relay will retain the salt and heater loads, assuming your ET is not an IC-20,40. The relay is programmed to come on with your system, and those two items will have power at that point. You could assign that relay another function but any other loads will need a spot.

  • 18 years ago

    Repair guy--thanks for the explanation. Mine is an IC-40.

    I saw your post on 'solar' suggesting that it is best to plumb the solar return in after the heater as it reduces back pressure. I couldn't think of any situation where I would want to run the hot water from solar through the heater so I switched mine over yesterday and the difference is dramatic. The way it was originally set up the solar return went through a Pentair Master Temp and at 2200 rpms on my intelliflo 160X4 I was only getting 20 gpm through the solar panels. After the re-plumbing I get 40 gpm. Pressure at the panels stayed at about 2-3 psi and around 10psi at the sand filter. This means I can reach my target of 30 gpm with 1800-2000 rpm or even less, and save considerably on energy consumption. Thanks for that suggestion.

    On a different note: can I use my easy touch 8 to control 24v irrigation valves? If so how would I go about hooking that up? I'm reluctant to call back my electrician as he didn't wiring things correctly to begin with. At the moment I have several available aux relays or are these only for high voltage?

    Thanks again.

    Waterouzel

  • 18 years ago

    Yea, the EasyTouch plumbing diagram calls for routing the solar heated water through the gas heater but I just see that as more resistance. As far as the sprinklers go, I've never done it but one way that seems like it would work is this. You need the 24 volts that the sprinkler timer normally would use. You could plug the transformer into the outlet on the EasyTouch gfi and then connect that to the line side of a relay. run low voltage to the sprinkler solenois as you normally would and then program the EasyTouch to trigger that relay. Keep in mind, you need to route all low voltage lines through the low voltage raceway. This is just an idea.

  • 18 years ago

    I like that idea except it ties up the EasyTouch gfi and mine is in an awkward spot. Any reason I couldn't run a 120v line from one of the aux relays to an outside gfi outlet in a better location and go from there by programing that aux circuit as my watering schedule.

  • 18 years ago

    Not if the timer is a 120v timer. The sprinkler valve is low voltage and that timer supplies the low voltage through the plug in transformer which is 24v. If you put a gfi for transformer on an aux relay, it will not keep time. What you are trying to do is basically glorify your sprinkler timer with the easy touch. To do that, you are bypassing the supplied timer and now controlling the 24v to the valves with your easy touch. But, the only way you can get that 24v is through the sprinkler transformer plug. With any gfi on the easy touch, they are rarely used for anything other than protecting the lights. You can still plug the transformer in, pop on one of those bubble type covers so it is rain tight and have access to the other socket in the gfi. Should not be a problem unless they installed something too close to the easy touch box for access.

  • 18 years ago

    Sorry, I didn't explain this very well. The 'timer' would be the schedule I program into the EasyTouch for that particular aux relay. When it turns on the transformer plugged into the gfi outlet opens the 24v valve and my grapes get irrigated.

    What I'm trying to do is find ways to use 4 aux relays plus valve B that are now idle in my setup. I have a number of irrigation valves close by that I would love to be able to program off the EasyTouch rather than relying on battery operated timers. You know how reliable they are. It would be difficult to run 120v to each location but easy for low voltage wiring. One thought I had would be to find inexpensive 120v/24v transformers that I could mount inside my equipment shed each wired to a differed relay and then low voltage to the appropriate valve. I haven't checked on the relays so this may be impractical. Any thoughts?