Questions to Update Pool Equipment

17 years ago

Hello everyone. Great forum. I am relatively new here and was hoping people might be able to give me some guidance.

I purchased a house about 5 years ago that has a 25,000 gallon pool. I am looking to upgrade some of the equipment and have a few questions.

The pool has one skimmer. There is a drain in the deep end of the pool that only works through one of those float valves (not sure if that is the correct name for it) in the skimmer. I.e. this drain does not appear to be hooked up to anything except when the float valve is configured to cause the skimmer to pull water from this drain. There is also a spa attached to the pool that has a drain.

At the equipment pad, there are two 1.5" or 2" inch pipes feeding the pump. Although not certain, as best as I can tell one pipe is from the skimmer and one pipe is from the drain in the spa. The system currently uses a Tagleus Pentair sand filter (probably relatively old, although I have removed the sand and confirmed that everything still appears to be intact internally). There was a very old gas heater hooked up, which I removed from the plumbing loop because the heater does not work at all. On the output side of the filter, there are three 1.5" lines going back to the pool. As best as I can tell, one goes to the pool and one goes to the spa jets. The third was marked with an "X." Not exactly sure what that one does, although it appears that it may somehow balance water between the pool and an additional set of jets in the spa.

The current pump is a single speed Hayward Max-Flo rated 1.5HP, with a service factor of 1. There is also a booster pump on the output side of the filter for a Hayward Viper pool cleaner. That pump is rated .75 HP.

At minimum, judging by the noise it is making, I believe I need a new main pump. I have read a good number of the threads comparing the Intelliflo pumps with two speed pumps, and without intending to offend anyone, I have to say that I am leaning in the direction of a two speed Whisper-flo pump. Having said that, I live in CA, so it is possible that my high utility rates (probably about $.12 per KWH, on average) and long swimming season may mean that a variable speed may be more likely to make sense. So, please do not hesitate to tell me why you think my decision to use a two speed pump may be a mistake. I am sure the Intelliflo's are great pumps, and it sounds like there may be a good consensus that they are more efficient at low speeds. But, in light of the information I have read, I am coming down in the camp of being unsure that the performance/flexibility of the Intelliflo justifies the price premium. In particular, my reaction, at this point at least, is that a properly sized two speed pump may be the way to go. So, I am looking for help in deciding whether to go with a 1HP or 1.5HP two speed pump.

The skimmer is probably about 60 ft from the equipment pad; the spa is probably 10-15 feet closer to the equipment pad; and the jets in the pool are maybe another 10-15 feet even closer to the equipment pad.

My wife and I honestly don't care about the strength of the spa jets. In particular, we are placing a higher priority on energy costs savings than performance of the spa jets. It is possible that the reason the pool owner originally went with a 1.5HP pump was to have strong spa jets. When I look at the performance specs for the 1HP 2 speed Whisper-flo's, however, it looks like a 1HP Whisperflo should be sufficient to clean the pool. So, my first question is whether or not you think I may be wrong in that conclusion. In considering my questions, it makes sense to assume that each of the plumbing lines that I mention above has at least 2-3 90 degree elbows, although I obviously don't know what is underground.

I'd like to use my new main pump to drive my viper pool cleaner and get rid of the booster pump. Any reason that may not make sense?

I am also thinking that I'd like to add a solar heater. I am in a great location for solar, although I'd be interested if people feel that solar is not cost effective e.g. because I'd have to run my pump on high for most of the day to drive water through it. The solar panels would be on the top of a single story house that is probably 35-40 feet from the equipment pad. I am not sure if the low speed on the Whisperflo will be enough to drive the water through the solar heating system. Do you think solar heat makes sense for my circumstance and, if so, what one or more pump(s) would you recommend? Would I be better off with a gas heater or heat pump? Again, not too worried about the spa heat at this point (e.g. don't care if I have a heater to heat up the spa quickly). Rather, we only want to warm the pool water to a more comfortable temp during, at the beginning and end of, the swimming season.

The pool doesn't see a high bathing load, and I don't expect that to change within the next 5 years.

In any event, look forward to any input and guidance. Thanks in advance for any help. Please let me know if there is additional info I can provide to help evaluate my situation.

Regards,

Mike

Comments (6)

  • 17 years ago
    last modified: 11 years ago

    Anyone?

  • 17 years ago
    last modified: 11 years ago

    Your filtration pump needs to be sized to the sand filter.

    Don't know about the viper but most cleaner booster pumps are high head pumps designed for that particular purpose.

  • 17 years ago
    last modified: 11 years ago

    Given the variety of applications that you have for your pump, I would seriously consider a variable speed pump.

    You could possibly get a two speed to work but it would require some careful consideration of each application how much flow rate it requires and how much head loss you have. But in the end, the pump choice will be a compromise and you may not be satisfied with the results.

    It would be much easier to get a VS and then adjust the speed for each application. Here are some of the advantages of VS.

    Adjust spa jet strength to what ever you feel like from very light to very strong depending on your mood.

    Adjust flow rate for solar to achieve optimum heat transfer while minimizing energy consumption.

    Adjust circulation flow rates to minimize energy consumption when solar is not in use.

    A couple of other points regarding a 2 speed pump:

    A 1 HP pump will probably not give you very strong jets at all.

    A 2 speed pump can be made to work with solar but I do not recommend running on low speed with solar. This requires a very low placement of the vacuum release which can in turn cause a vacuum in the solar panels and plumbing installed on a roof. Under certain conditions, a few installations done this way have had pipe collapse. Besides, solar panels become very inefficient at low flow rates so if you want the maximum heat transfer possible, you will want to hit the minimum flow rate specification.

  • 17 years ago
    last modified: 11 years ago

    mike-

    If you want to go the simple 2 speed approach to save money, I would recommend at least the 1.5HP 2 speed which will be 1/4 HP at low speed and will provide adequate turns on your pool daily for filtration and chlorination. The 1.0HP at low speed is 1/5 HP and will require much longer run times to circulate your pool. With the right valving, the 1.5HP at high speed will be enough for your spa and cleaner. Also, I have seen 1 story solar panels work fine with 2 speed pumps at low speed. I think mas985 was referring to 2 story solar panels and with these elevations, the vacuum levels can reach the design limit of the panels, but even then, there have been folks on this forum that have successfully used 2 speed pumps on low speed for 2 story panels. Like mas985 says, the vacuum breaker has to be positioned at lower elevations and you should consult your solar panel maker for exceptions to their normal application guidelines.

    Variable speed will also do the job, but as you said, it is more money to begin with and the payoff will depend largely on your local utility rate. If my utility rate was $.30/KWH, I would have chosen a variable speed pump, but at $.07/KWH, the payoff would be over 10 years.

    All the above assumes no problems with the 2 speed or variable speed over its life. If the variable speed fails, you are likely looking an expensive total pump replacement. From recent posts on this forum, it seems that at least one variable speed manufacturer will not provide separate replacement parts for their variable speed pumps. If the 2 speed fails, you can replace the parts and be back up and running with a nominal expense.

    Hope this helps!

  • 17 years ago
    last modified: 11 years ago

    Mike, The hayward viper requires a booster pump and will not operate from your filter pump alone.

    Your current pump is a 1 1/2 hp uprated pump which means it is equal to a 1 hp full rated pump. You should determine your filter size and get the appropriate pump size. If the pump is too small it will not properly backwash the filter. If it is too big it will channel the sand.

    I will stay out of the trhought/mas985 ongoing debate. Although we have used the whisperflow 2 speed for many years with pretty good success. Have not tried the intelliflo yet but probably will because it satisfies the SVRS code requirements in some of the surrounding counties.

  • 17 years ago
    last modified: 11 years ago

    Hey, thanks everyone! Great input. Appreciate it very much.

    Regards,

    Mike