Software
Houzz Logo Print
mtnrdredux

HVAC recovery

10 years ago

We have a multi-zone central air system, expanded 5 yrs ago, supposedly top of the line. I hate CA but I suppose it does its job well. Except when I go to sleep 71 is too cold, it has to be 73, and when I wake up I am so hot, have to move it to 71.

But anyway...

We spend a lot of time away in the summer, and while a caretaker is usually living here, sometimes they are away and even so they use only a small area of the house. We turn off the AC elsewhere.

When we get back, it is often quite hot, esp in August Like 85. We always seem to come home at night, and it is so hard to fall asleep in that heat. It takes nearly 18 hours to get back to a cool temperature.

Questions

1. Does that seem acceptable... 18 hours?

2. Anyone have a system or add on where we could turn the A/C on the day before we head home?


TIA

Comments (42)

  • 10 years ago

    For a while I used "the nest" which allows you to control your thermostat for both heat and AC by your phone. It worked great, but I got rid of it because my Internet was spotty in the room where the main thermostat was located. Didn't want to chance failure. My sister has one and it has been working like a charm for several years now. While I had it, I would turn the heat back up before beginning my trip back home so that it would be toasty when I arrived to my driveway. 18 hours seems like an awfully long time.

    https://nest.com/thermostat/meet-nest-thermostat/

    jo

  • 10 years ago

    I run my HVAC remotely from an app on my iphone through a Honeywell wi-fi thermostat. It does take a long time for the temp to get down if you've let it get hot while you're gone. I can run my programmable thermostats completely from my phone or any internet enabled device as well as with the thermostat on the wall.

  • 10 years ago

    Before we had the kitties, we went away for almost 2 weeks in July and had no ac on at all. When we came in, the house was about 88 degrees. We got it down to about 76 degrees in about 3 hours so our geothermal system works esp well for ac. The equivalent heating, however, would take quite a bit longer. But it's the nature of the technology.

    We don't use remote control thermostats, but I'm sure they're available. Honeywell makes smart thermostats.

  • 10 years ago
    last modified: 10 years ago

    We hae a Carrier system and the thermostat has a phone app you can control it with. There is bound to be something compatible with your system, but it probaby means a new thermostat.

    I'd start with having the AC checked by a reputable AC firm. It should not take 18 hours to cool 10 or 15 degrees. A week or two ago, we had a power surge that caused the compressor to overheat and shut off. We checked all the things we could (had not noticed the power surge) and then I called our AC company to leave a message and hope to get an appoinment the next day. The owner who sold us the unit and surpervised the installation answered from his home and told us about the power outage. Guess a lot of customers were doing the same thing. We had to shut it off at the breaker for an hour and then restart it (gotta love and AC man who answers the phone and diagnises the problem from home and tells you what to do to fix it, n o charge juat happy to help). We probably dropped ten degrees in an hour, maybe less but certainly not much more.

    Even when we had this system installed, we'd been without AC for two weeks (long story) and we were happy to keep the house under 90 with a portable unit and a couple of fans. It was something like 104 outside. They finished installing a complete system for the entire house, new ductsy and everything, that evening. We were cool by bedtime. Sounds like aren't getting sufficient cooling. Could be the coolant is low. If so, you want to get that fixed before it becomes a bigger problem. While they are there, you could ask them about a smart thermostat or your system. But get it working right first.

  • 10 years ago

    18 hours seems awfully long. The key to being comfortable is moving air, not so much the temperature. I'd rather it be 80 with a fan than 70 without one. Get a pedestal fan and direct the air straight at you where you sleep. You won't have the problem of being cool when you go to sleep and hot when you wake up.

  • 10 years ago
    last modified: 10 years ago

    The Ecobee3. WiFi controlled from anywhere in the world and is equipped with room sensors.

    So, if you want your bedroom 71, the bedroom sensor will ignore the main thermostat setting and keep your room at 71.

    If your HVAC is newer, the fan should run on low to circulate air throughout the house 24/7.

  • 10 years ago

    Definitely use the nest...it has many cool features to control temps remotely, can sense "away" so it will reduce/raise temp accordingly. My geeky husband loves it.


  • 10 years ago

    I'm not so sure 18 hours is excessive - your home is large.

    We used to turn our AC off at our vacation house in the mountains whenever we left. Starting in September we would set the thermostat to Heat and the temperature to 55 just in case there was a cold snap we wouldn't have to worry about freezing pipes.

    In the summer months it would easily take 12 hours for the AC to cool the house - but it would take up to 24 hours to bring the temp all the way down to 71. And it's not just the temperature to consider - it's also the humidity factor. This house is smaller than yours - about 3500 sq. ft.

    This summer we called our HVAC guy and told him that we thought the unit wasn't working correctly because after 24 hours the house hadn't sufficiently cooled. He told us that the AC was working perfectly but that the cooling time was increased due to the humidity.

    He also suggested the Nest so that we could turn it on ahead of time and then when we arrived the house would be comfortable. He'll install one and program it when he comes to service the furnace in September but in the meantime we leave the AC on and set the thermostat to 80 - what a difference that made - now when we go up the house cools within hours.


  • 10 years ago

    A programmable thermostat. Someone previously mentioned humidity and that's what would bother me. If you are letting your house get that warm, doesn't the humidity increase? I've been in houses where people have had a problem with that and have "sweating" behind pictures, etc.

  • 10 years ago

    Someone also recently mentioned the Nest to us to turn on the cooling ahead of time at our lake house. But, we only live 20 minutes away, and our place is less than 1500 sq feet, so seemed unnecessary for us.

  • 10 years ago
    last modified: 10 years ago

    If you live in Houston and have high ceilings, then 18 hours might be about right. If you live in Denver and have 8-ft ceilings, then 18 hours seems like a long time.

    If you have not already, you might get more informed replies in a HVAC forum.

  • 10 years ago

    Eighteen hours seems too long, especially when you are starting your cooling at night. Have you always had this issue?

    The life span of new air conditioners is about 15 years. I don't think it would be unusual to need something repaired or adjusted after 5 years. I would call someone to check your system.

  • 10 years ago

    18 hours isn't too long to have it get down from uncooled and uninsulated in a hot climate to the low 70s. The ongoing fan idea and possibly leaving the thermostat on at 80 would shorten the time to get the temp down. I would also have the machine checked because they can leak...

  • 10 years ago
    last modified: 10 years ago

    Your house is good sized. Do you have a big enough system or multiple systems for your square footage?

    Also, the AC can only efficiently cool about 20 degrees below the outside temperature, so if it is 90 outside, it might be really hard to get it to 71 inside. So, you might not get it as cold as you want it on hot days when you are trying to cool a hot interior.

    You also might have a refrigerant leak, so maybe getting it looked it is not a bad idea.

  • 10 years ago

    If you think about how everything inside the house has been heated up with no ac running - floors, walls, furnishings..... once you turn the ac back on those things will still be radiating their absorbed heat so it's not unreasonable for a large section of a house to take 18 hours to 'feel cool' to you.

  • 10 years ago

    Question about the Nest and such: can more than one phone control it? Because I'd worry that one of us decides it's not hot enough for the air and turn it off remotely, while someone else is at home or comes home wondering why it's so warm? Thermostat wars already go on while everyone's in the house; adding on the remote factor could get escalate things.

  • 10 years ago

    Thanks everyone for your input. It seems that most, not all, feel that 18 hours is a long time get to cool.

    The system, which was put in/expanded about 5 yrs ago, works fine in every other regard. It is simply this narrow question of how long it takes to cool it on a very hot evening after 2 weeks or so of the system being off.

    I hear a lot of your saying that the large size of our home will mean it takes longer to cool off. To me, that doesn't make sense, even though we do have. The large size of our home is why we installed two 5-ton 2-zone systems, one for each floor. Plus we have a Dectron which removes the humidity from the indoor pool and cools/heats. So that is three systems.

    It may simply be, that when they calibrate system needs, they don't calibrate it to perform for this type of situation. IDK

    We get very regular maintenance (I think that is because of the Dectron) so I will talk to the HVAC guys. Maybe the Nest is a solution; or maybe a few box fans like Tibb says, just to get us over the hump. It wouldn't matter as much if we were arriving midday and could swim or sit outside, but we always drag our feet leaving the beachhouse and it is invariably midnight or so and we are all dead!

  • 10 years ago

    The Nest is terrific, but why not have the caretaker just turn on your ac the day before you return?

  • 10 years ago

    It should not take 18 hours to get a space from 85 degrees to 70-ish in my opinion. It shouldn't take half that time.

  • 10 years ago
    last modified: 10 years ago

    If the outside temperature is lower outside than inside, consider a whole house fan.

    My house is older, I had A/C added, then a year later had insulation added to my attic. Going from 6" to 18" of insulation changed my home. Warmer in the winter, cooler in the summer, after adding insulation my energy bill went down and the temperature swings were reduced. I operate my HVA/C manually. Because of work or travel, I do not heat or cool my home when I am not there. Coming home late in the summer, inside temp is ~10 degrees warmer then outside, instead of running the A/C, I use the whole house fan.

    The instructions for my A/C recommend not doing what you are doing...turn off the A/C and expect cooling, I do not know if 18 hours is acceptable, but when everything in your house has heated to 85, I would expect a long cooling time.

  • 10 years ago

    Cyn, We do that when we remember and they are there. But sometimes they aren't there, and also we go up and back on a whim. And it still begs the question if it should take that long.

    Jim,Thanks. A whole house fan would not really be an option. Our house is mostly a rambling one story, added on to over the years, and only a very small portion of the 8400 sq ft has an attic. I don't recall the detail on insulation (our house is old too) but we did pretty much a whole house reno down to the studs and upgraded insulation then. No complaints about it getting warm or staying warm or really anything but this narrow situation.

  • 10 years ago

    I do not think that 18 hours sounds like a long time. Once the thermal mass of the house has warmed up that much over a 2 week period, it will likewise take quite a bit of time for the thermal mass of the house to get to a cooler temperature, especially during the warmest times of the year.

    We do not use A/C but I can definitely feel it in the summer when the temperatures have warmed enough to the thermal mass of the house has warmed up and it takes significantly longer in the evenings to be comfortable. That is when I wish we had added a sleeping porch with a ceiling fan to the house.

  • 10 years ago

    Sounds like you're going to get conflicting opinions here on if it should or shouldn't take that long. Maybe you need to get with an HVAC professional who can accurately assess your situation and give you a solid answer on that. We don't know the capacity of the AC unit(s) that are cooling the 8400 sq ft or the heat/humidity conditions at the time you are going from no AC to AC.


  • 10 years ago
    last modified: 10 years ago

    I agree 3katz. Based on what I hear, it is not a foregone conclusion that we have a system problem, but neither is it a dumb question to ask my HVAC people if they think this performance under these conditions is to be expected.

    And, I think I want to get a nest!

  • 10 years ago

    Mnt,


    From my instruction manual, 12 degrees heating per hour, 6 degrees cooling per hour.

  • 10 years ago

    Some of the issue may be how your AC is sized. Air conditioners should be sized for normal use, meaning that they turn on when the temperature gets out of whack a degree or two from the thermostat setting rather than trying to cool a house that has been 15 degrees warmer than normal for 2 weeks. Your AC system may be doing a great job in normal operation (at least I don't hear you complaining about that). An oversized AC, on the other hand, can cause problems in normal operation because it tends to run in really short cycles that aren't long enough to fully dehumidify the air. But an oversized AC would be faster at bringing down the temperature in the situation you're describing.

    I suspect that the differences in responses are due both to what climate the respondent lives in (how humid) and whether their AC is oversized relative to their day-to-day cooling needs. Oversized AC units are very, very common. Maybe because HVAC installers get to sell you a larger, more expensive unit, maybe because they are too lazy to do the Manual J calculation, or maybe they think overkill reduces customer complaints. I don't know.

    Here's an article about AC oversizing.

  • 10 years ago

    This summer heat & humidity were excessive. We had CA in our last house, if we were away I left it set at 78. It kept the humidity down and didn't need to run forever when we came home & lowered it. The other thing I did - if a heat wave was predicted I turned it on befor the house heated up.

  • 10 years ago

    eandhl2,

    That is similar to the instructions for my A/C

  • 10 years ago

    The Nest is not the best solution for a large house with plenty of rooms. It's central location doesn't read room temps and make adjustments according to the owner's wishes. If the hallway is cool, your other rooms will be warm or hot. If the hallway is warm, your other rooms will be cool or cold.

    Ecobee3 offers a central location, accompanied by room sensors to make a house more evenly comfortable.

    Ecobee3 is also Apple HomeKit compatible.

  • 10 years ago

    Mtn, is this something you have noticed every year or mainly just this past summer? I live in CT also and our CA system broke down a couple of weeks ago ( during that crazy heatwave with
    high humidity) and had to be replaced. The house was sitting at around
    90 degrees before it was replaced ( oh the misery for those two days!)
    and it also took about 18 hours or so to get the whole house back down
    to the 72 which we normally keep it set to. Normally it is much faster to bring the temps down but it was so humid and there had been no air circulating for those two days that it did take extra time and our house is much smaller than yours as well.


  • 10 years ago

    If only a small portion has an attic, does the cool air enter the rooms at or near the floor? If so, that probably works better for heating the house but would be much less efficient since hot air rises. I have no idea how much difference that might make, but 18 hrs just seems way too long -- and would seem to indicate your system is straining.


  • 10 years ago

    The easiest way to prevent long cooling delays is.....

    >>>> Start cooling WELL before high temps/humidity hit!!!

    * The system doesn't have to work HALF as hard then!!! AND....the comfort-level is vastly improved.

    * If I know it's gonna be a warm day, I insist on closing everything up by mid-morning...b4 10am for sure! If it's 76 upstairs on our hallway t-stat, I set it for 70 or 72. It only has to cool just A FEW DEGREES THEN!!

    * It's lunacy to leave a system off, & remotely turn it on shortly b4 coming home, especially in warm temps with humidity!!! It probably won't even reach a persons chosen "target-temp".....

    * Some here alluded to the "Heat island" effect....BINGO!

    >>>> Let the system run itself, within your parameters. It doesn't have to work NEAR as hard then!!!!!

    The easiest way to stop a fire??? DON'T LET IT START.....;-)

    Faron

  • 10 years ago

    From my Florida experience, it should not take that long, although I do not turn off mine when I leave, I have it set at 79 when I am away so that the humidity is controlled at all times, I switch it down to 72 when I arrive. Our previous home had 3 medium sized units instead of 2 large ones, it was more efficient. One unit was dedicated mainly to the master area, which was quite large.

  • 10 years ago

    Faron is right, of course. It's more energy efficient to keep the temp consistent.

    Once the furniture, flooring, walls and fixtures, even the water in the toilet tank becomes hot, it will take a lot of energy to reduce the temps to comfortable.

  • 10 years ago

    I get your point entirely about shutting it off creating more work to cool things off, but obviously there is a time limit to that arbitrage. I mean, to be extreme, if I were going away for 3 months it would clearly use less energy to turn it off even if it has to work hard to cool off again. I think that advice is aimed very much at people who used to shut the system off when they went to work, for example.

    Anyway, we are away again so I haven't met w my HVAC guy yet, but we will.


  • 10 years ago

    This is what I think and I'm no pro or anything but to me this is how to look at it. OK so does your A/C work to keep the house cool and comfortable with its normal usage and costs a reasonable price for utilities? If the answer is yes then it's going to take however long it's going to take to cool off a really hot house. Remember that everything inside that house is HOT and it emits heat until it gets cooled off. My line of thinking: your system either works or it doesn't work? Right? So if it's working just fine all the other times, then it's working correctly. I have found that I like to just set the A/C temp up some (maybe 80) while I'm gone because I discovered that if I just turn it off and it's really hot outside, it seems to run and run and run without shutting off before it finally cools the hot house once we come back home from vacation.

  • 10 years ago

    If there has been a coolant leak, after being turned off, it may not cool at all next time. I think that is quite possible. Again, I have lived with 100 degree plus outside, lost AC comepletely and not had it take that long to cool down once repaired -- even with high heat and humidity outside.

    The last time we were without AC, we got to 95 inside before we got a portable unit to help until we got things worked out (we had two warranty repairs and the second time the part failed -- then the manufacturer came back and said they weren't paying for the coil because the wrong part had been used and we got caught in a three way fingerpointing. We didn't know who to believe and finally found a new company to come in and redo the whole mess -- but it took 2 weeks to resolve and the cloudy, rainy days had given way to a heat wave). I get a hot house. I get it can take a few hours -- but 18 hours is way more than a few hours. The system may be freezing up and not working properly if it is running that long. The coolant may not be sufficient. The system may not be right for the home and it's construction (I was going to suggest that 8400 sq ft might need more that 2 zones to control properly, but it looks like a significant portion is your indoor pool and that has it's own system . Two might be enough, but something's not right. Glad you are questioning it and I hope you get it figured out.

    There is a school of thought that turning your climatr control off completely is not good for the system or the house itself. Your climate may be less extreme, but at least here, I've read things recetnly that suggest keeping your temp within 10 degrees at all times -- not just for comfort but also to maintain a controlled range of temperature, humidity and expansion/contration of all the structural elements. That's new to me, but it makes a certain amount of sense. Again, age and construction may have something to do with how much that maters -- just throwing it out there for you to consider.


  • 10 years ago
    last modified: 10 years ago

    I just got an email from our power company about a significant Nest rebate. To qualify you need to be a Georgia Power customer but I'll post this because other power companies may be offering the deal as well.

    Nest Rebate

  • 10 years ago
    last modified: 10 years ago

    Lascatx --- just to qualify, I didn't write that it was two zones,I wrote that we had "two 5-ton 2-zone systems, one for each floor", plus the Dectron. So that would be 4 zones.

    But DH corrected me and said it was three units, each with two zones, so we have SIX zones plus the Dectron! Sheesh.

    The receptionist who answered the phone at our HVAC people didn't seem to think it seemed crazy that on the hottest, humid days it could take that long for go from 89 to 70 after 2+ weeks of the system being off. But that was just her impression ... the guy who does our maintenance is going to call me back. And I have scheduled an apptmt with them to discuss installing a wireless thermostat for the future.

    PS I agree that it is probably better for the materials and the contents to experience a narrower range of temps and humidity. In our temperate climate, perhaps less so than in a tropical climate or desert climate, but still the case. My DD plays the harp, and if we do not keep it in an A/C room the strings pop. A PITA and not cheap.

  • 10 years ago

    d_gw

    Georgia Power and many other power companies offer $100 rebates on several programmable thermostats, not just Nest. The Ecobee includes a room sensor which Nest can't compete with.

    Rebate


  • 10 years ago

    Even as a Florida/Tennessee snowbird, we never shut off our heat or air conditioning. When we left for the winter the TN house had its water lines drained and sprinkler blown out by our plumber, and simply kept the thermostat at 55 in the main area of the house and basement---not the master bedroom or upstairs (4 zones). When leaving the Florida house for the summer the humidistat was used and temp raised up to 80. The humidistat would turn the system on for temp and/or humidity. In Florida you would never want to run your AC fan constantly because the duct work is in the attic (the house would be 100+ degrees in no time). Even traveling out of the country for a month our Florida AC was not turned off. Our weather is more extreme in the summer than yours, for sure, but just don't see the advantage of shutting the AC down when you leave and running it straight for 18 hours when you return. Consider it as bringing a dish from the oven closer to room temp before putting it in the refrigerator, or thawing your frozen meat before putting it in the oven to bake. Otherwise you would be taxing the appliances and causing them to run too long. When we had a Florida condo that was empty for the summer with the temp raised to 80 degrees our electric bill was $10.00 a month. Good luck, talk to the AC service tech and hopefully you will find a nice compromise so that you can stop suffering every time you come home. ;-)

Sponsored
Urban Upkeep LLC
Average rating: 5 out of 5 stars6 Reviews