Did they install my ridge vent wrong? Please help :(

9 years ago

A few months ago, we had a new roof put on our home. The old roof already had a ridge vent so the slots were already cut for the most part, they did add one new row. Yesterday I noticed that the house seemed quite warm inside but had expected that the new roof and some additional ridge vents would have helped keep the house cooler. It wasn't all that hot outside. I decided to go up into the attic since it's really easy to get up there, we have a stair case up to the attic. I was looking around and saw something I believe to be incorrect installation of the ridge vent. When I was looking up at the crevice that is cut out of the roof for the vent...what I can see there is the plastic sheeting that goes over the entire roof. My question is; shouldn't that plastic have been cut out of the ridge before they put down the ridge vent? How will air get out with the plastic down? I am going to contact my contractor but I want to have some educated advice if he claims this is the correct way to install. I'm just a housewife so I certainly I am no authority on the subject but in my mind I feel this is not correct. I did do some google searching and that also confirmed my fears. Just as a mention, the ridge vent is Owens Corning and so is the moisture barrier plastic sheeting or whatever you call it...the roll of plastic they put over the entire roof(what I can see under the ridge vent, it is light gray or white in color). I remember the ridge vent being a hard ridged black plastic and it came in a roll.

Any advice would be appreciated...thank you!

Comments (24)

  • 9 years ago

    You are 100% right. They goofed.

  • 9 years ago

    I'm assuming they will have to remove and throw out the old and replace this entirely...right? I was afraid of that but really...I knew. All I had to do was look at Lowe's for how to install it. UGH! The guy that put the roof on is supposed to be the best. Sheesh.

  • 9 years ago

    Sounds like your opinion is the correct one. There is no reason for the plastic to be covering the slots cut in the roof.

    The pest/moisture barrier should be a material much like a kitchen plastic scrubber between the cap and roof, not sheet plastic.

  • 9 years ago

    Let me make sure I understand you correctly HandyMac, there is supposed to a pest barrier that resembles a kitchen scrubber installed underneath the hard ridged plastic ridge vent and over the cut out crevice? I just want to know for sure I'm understanding you correctly. I need to get my ducks in a row for calling the contractor. Do you know what it's called so I can find a photo of it?

  • 9 years ago
    last modified: 9 years ago

    You might also want to add a sturdier pest barrier over the entire ridge vent to keep from meeting this guy.

  • 9 years ago

    There are some times when I person isn't happy to be RIGHT! UGH!

  • 9 years ago

    The stuff worthy posted is what is generally used. It keeps critters out, keeps all but straight horizontal rain out, and also snow.


    Here is an example

    arkansas girl thanked User
  • 9 years ago

    The product that was used is this: VentSure Rigid Roll Ridge Vents made by Owens Corning. I was able to find an instructional sheet at the Owens Corning website. I says that all underlayment should be trimmed away from opening. It shows how to install it. There is nothing for this particular product that goes under it. It is installed and caulked directly to the shingles surrounding the hole and then is nailed and then covered with cut three tab shingles.

    Thanks all for the help. Our contractor is coming out on Monday to see it for himself. Fingers crossed that he understands the installation process and gets us fixed up!

  • 9 years ago
    last modified: 9 years ago

    I would go one step beyond the roofer. Contact OC and ask for a field rep to meet roofer at job. Since OC is covering the warranty, they will be very interested in verifying correct application.

    A moisture barrier is required and included with the VentSure product. It's an integral piece, not an add on. It breathes. It can look like plastic from a distant view.

    Also, if the vent stops short of the ridge length, it's improperly installed. The ridge vent must cover all of the uncut ridge, end to end.

    Picture of Moisture Barrier

    Installation Sheet

    Afterthought. Are the soffit vents open or do you have enough free vent area to equal the ridge vent? Is it balanced? More soffit intake is far better than exhaust.

    arkansas girl thanked Michael
  • 9 years ago

    Thanks brushworks, I don't know anything about the soffit vents. I know they are there but I haven't a clue if it's balanced or not.


    I will say that after closer inspection and crawling around in the attic more, I am seeing that some of the vents are installed properly ( they have a porous fiber material showing from underneath ) but the one that is over my garage and carport have a different material showing that appears to be the solid white plastic underlayment. That is what I had seen first of all but then over the house, it is a darker gray fiber paper looking stuff. Looks like they will have to redo the one vent. At least that is what I assume. He is coming out on Monday to inspect it.

    On the garage carport vent, the old ridge vent from the old roof was longer than it is now. You had mentioned that the vent must cover the entire cut section, it does not over the garage area.

  • 9 years ago

    The installation sheet says to extend the vent beyond the cut-out to the end of the roof edge, gable, etc. That's the proper way to install ridge vent. The closer the vent is to the cut out, the more likely a leak may happen, especially caused by wind driven rain.

    If you're seeing the underlayment over the cut out, the roofer may be able to slice that out from the attic space. Just make sure it's cut out and removed, not left as a flap which will eventually block the opening.

    While he's there, ask him to proof the soffit vents to make sure they are open and adequate. Proper ventilation is a major part of a roofer's responsibility and improper venting always voids the warranty on materials.

    arkansas girl thanked Michael
  • 9 years ago

    I was just up in the attic and I find that the new ridge vent is about two feet shorter on each end than the old one. Of course it's shingled over on the top over the unused cut out. Do you think I can call OC and get someone to inspect the work?

  • 9 years ago
    last modified: 9 years ago

    As an addition to the story; I went to Lowe's to see a roll of ridge vent in person, the exact same one that was used on our house. I could see the underside has a gray webby thin product attached to it. This is what I see over my house area but is not what I see over my garage and carport area. I looked at underlayment like what was used and that is what I can see over the garage/carport. After they had finished the roof a few months ago, I had questioned him about why the ridge vent was so short compared to what it was before and he claimed that an unairconditioned and unheated structure is not required to have any venting. Is that true? I don't believe that. Another thing, my home attic and garage attic are connected and opened to each other, not a separated structure. Any feedback on the comment that a vent is not required? This is frustrating me because I'm just a homeowner, I'm no professional, that's why we pay through the nose to have a "professional" do it. Roofing is certainly not a DIY sort of a job either!

  • 9 years ago

    Well the contractor came out and the ridge vent over the garage is going
    to have to be taken off. He was really angry almost as if he was mad
    at me about it. Heck, it's not my fault and excuse me for being
    observant. He kept arguing that the garage didn't need to be vented. I
    said "so I have a ridge vent that doesn't do anything?" I am not a
    happy camper at this point.

  • 9 years ago

    I was just up in the attic and I find that the new ridge vent is about
    two feet shorter on each end than the old one. Of course it's shingled
    over on the top over the unused cut out. Do you think I can call OC and
    get someone to inspect the work?

    Are you saying there's a cut-out along the ridge that is shingled over without filling the void with lumber?

  • 9 years ago

    Well, it's a sure indication of poor workmanship and very poor judgement on his part. That void below the shingle will cause the shingle ridge cap to fail because it's going to sag due to no support below it.

    It needs to be fixed! I would contact your local building department.

    arkansas girl thanked Michael
  • 9 years ago
    last modified: 9 years ago

    Of course, this is just speculation on my part but it appears as if the roofer that did the job installed the ridge vent as a dummy ridge vent and didn't intend to have it functioning. I say this because when the owner of the company came here, he expected to just go in the attic and cut away the underlayment. He came back down from the attic after a while and said that he couldn't cut it from inside the attic, it was just too hot up there and he couldn't get to it well enough. Well....I went up there and there are no obstructions keeping him from getting in there and cutting out that plastic...BUT what I did find is that he had cut into the plastic so I looked inside the hole....what I saw was not what I had expected. What I saw was the backside of shingles with only a small opening of about an inch. So not only was the plastic there, the shingles were not installed in a way that you would install them to put on that ridge vent. So he is going to have to take it all off and actually saw out the shingles to make a hole for the air to escape. All the while he kept saying that it isn't even required for there to be a ridge vent over this garage. So I don't know if they were being deceptive or if it really was an oversight. I guess only god knows the answer to that one...HA! But I do know what it looks like. Also, I doubt the company owner knew this because he wouldn't have cut the plastic opened had he known because he had fully intended to just cut it opened.

  • 9 years ago

    The garage vent will certainly help cool the attic space above it, if there are soffit vents below. If it's an open attic (no ceiling) it's just a beneficial as soffits.

    It makes perfect sense to vent a garage, especially one with a ceiling. Venting accomplishes many things, but one special reason is to prolong the life of the shingles and roof framing, sheathing, and to lower energy bills in summer.

  • 9 years ago

    The garage has a ceiling and soffit vents and a gable vent on the end of the house at the very middle peak. The attic of the garage and the house are a common area/connected and opened to each other.

    Thanks for all your help!

  • 9 years ago
    last modified: 9 years ago

    The gable vent needs to be blocked (typically from the inside)so it doesn't short circuit the soffit and ridge vents.

    arkansas girl thanked Michael
  • 4 years ago
    last modified: 4 years ago

    Arkansas Girl, whatever happened in your situation? The same thing just happened to me and I phoned the roofer back and told him I wanted the same length of ridge vent I had before. Now the new ridge vent is just this short little thing, and it looks awful. So I'm curious how you resolved it.

  • 4 years ago

    This issue was not resolved by the contractor, I think he went out of business shortly after the job on my house.

    I would assume that in your case, the contractor was trying to save money by using less material and so made it shorter than the original one. Like I had said before, I'm not any sort of an expert, but the ridge vent should have been the same as before, not shorter! The heat needs to escape from the attic!

  • 4 years ago
    last modified: 4 years ago

    Thanks very much for responding Arkansas Girl. Yes, the contractor told me he was trying to save *me* money by buying only one ridge vent. I don't know about that. But I told him I'm adamant that the vent is changed it back to the way it was. It's going to cost *me* more money now. So we'll see if he changes it back. Boy, it's tough getting these jobs done. I'm really upset about it. Did you get yours changed back to the proper length? Thanks again. Editing: I saw your other response and see that you did get it fixed. :)