what size downrod will I need?

8 years ago
I have a great room that has 25 ft ceilings. What would be the best size downrod for the 96" ceiling fan?
Indoor Industrial Ceiling Fan, 96" · More Info

Comments (2)

  • PRO
    8 years ago

    The ideal height for these fans is 10' from the ground so they would need to drop approx 15'. We sell 12, 18 and 24 inch down rods. Item includes a 6 inch down rod.

  • PRO
    8 years ago

    Keeping the blades at 10 feet from the floor would maximize the
    perceived air flow while staying at the safe blade height prescribed by
    UL. That would mean the customer would need a 14.5 foot long down rod.
    There is a complication with the wiring when the down rod is extended
    beyond four feet. The customer would need to add the additional length
    of wire to the wiring of the fan to allow it to be installed.