Newbie questions on OSB usage

7 years ago

I'm doing a screened porch conversion to a heat living area. I got the framing approved by the inspector and have now put up the OSB sheathing. After I put up a lot of the OSB I noticed that there were notices stamped onto the boards about how it should be oriented. For example "This side down" and "strength axis this direction". So now I am wondering if it is important to have all the pieces cut so they obey these notices? There are not even close to any whole sheets involved because there are so many windows. Also, does it matter which side of the sheets are facing out?


Currently they are just temporarily screwed into place but I don't want to nail these all into place and have the inspector tell me to tear them all down.


Thanks for any help



Comments (37)

  • PRO
    7 years ago
    last modified: 7 years ago

    Why haven't you followed panel instructions?

    Are you simply a rebel?

  • 7 years ago
    last modified: 7 years ago

    OSB is stronger in one direction than the other. That's why you are supposed to orient it properly; to lend strength to the wall. If it's just small pieces that you misoriented then it probably doesn't matter (whether the inspector will care is another question though).

    I think the inside/outside is just so that the inspector is able to see the stamps (from the inside) after you've covered over the outside with something else. So again, an inspector might squawk if he can't see the stamps, but in reality it doesn't matter.

    At least that's my non-pro understanding. It's better to just follow the instructions.

  • 7 years ago
    last modified: 7 years ago

    > There are not even close to any whole sheets involved because there are so many windows.


    Ouch, so have you install a bracing, V bracing, diagonal bracing, leave in bracing, or even thermoply?

    If you did ... may not make a difference. If you did NOT and expect improperly oriented half sheet of OSB to provide you with bracing...

  • 7 years ago
    last modified: 7 years ago

    Relax Peter, it doesn't appear you've done anything wrong. "This side down" and "strength axis this direction" are for OSB used as roof sheathing. One side is less slippery and it helps to span the long dimension across multiple rafters. You can hang it on a wall any way you like but vertical installation of full panels avoids adding horizontal blocking at unsupported sheathing edges. Follow the nailing requirements in the building code table.

    If the walls and roof are attached to the house, additional lateral bracing should not be an issue and the inspector has already inspected and approved the wall configuration and the ratio of wall to openings. Make sure there is a metal tie where each rafter sits on the wall top plate.

    As mentioned earlier, make sure the APA rating stamp is visible somewhere from the inside. I'm sure its OK but show us what it says and include a photo of the wall.

  • 7 years ago

    Just curious Res what is the difference between osb and green board?

  • 7 years ago

    First, green board is construction slang for moisture resistant gypsum board used in non wet areas of bathrooms.
    Structural OSB wall sheathing made by Huber is called Zip System and has a green acrylic waterproof coating that is vapor permeable and acts like house wrap. It might be called green board by someone new to the construction trade or hard of hearing.

  • 7 years ago
    last modified: 7 years ago

    Thanks Res! Which is better?

  • 7 years ago
    last modified: 7 years ago

    I assume you are referring to Zip vs plain OSB wall sheathing.

    I have never been a fan of housewrap. Until something better comes along, I believe Zip sheathing is far superior and well worth the additional cost as long as the contractor rolls the joint tape properly..

  • 7 years ago

    Too late for us, they just put our osb up and didn’t even offer the zip sheathing as an option! Now I’m disappointed we are missing out on the benefit. What house wrap do you suggest, that may upgrade performance?

  • 7 years ago
    last modified: 7 years ago

    What is the exterior cladding? Tyvek is the only wrap I would consider using. I've used Typar but they seem to keep changing how its made. Avoid at all cost wrap with a lumberyard logo on it.

    You can still add a liquid coating or a self-adhering membrane but you would need a cooperative builder familiar with such building systems and be willing to pay for it.

  • 7 years ago

    I just bought a roll of Everbilt house wrap mainly because it was sold at Home Depot in a roll that was the right size for my job, Are you saying that was a bad idea?


  • 7 years ago
    last modified: 7 years ago

    Yes, it’s a bad idea. Tyvek is the only real choice.

  • 7 years ago
    last modified: 7 years ago

    Everbilt wrap offers little resistance to water infiltration which could cause you very expensive repairs later. check out this video.

    Count yourself lucky you asked. This is one of the construction choices where you can't afford to be frugal. Another is the window flashing.

    Home Depot sells Tyvek in a 3ft x 165ft roll for $47+

    What is the cladding?

  • 7 years ago
    last modified: 7 years ago

    I have never been a fan of housewrap. Until something better comes along, I believe Zip sheathing is far superior

    DuPont begs to differ.



    XPS sheathing added to DensGlass gypsum sheathing.

    I prefer taped tongue and groove XPS followed by brick paper (felt) under stone and brick. Still, where the plan specifies it, I've used OSB or gypsum board followed by Typar or Tyvek.

    Fibreglass-covered gypsum sheathing is tempting and widely used in commercial structures.


    The problem with housewrap is getting all the details correct. Especially on a multi-storey home in the wind! At the basic level, not all contractors understand the importance of using capped nails or staples.

  • 7 years ago
    last modified: 7 years ago

    Peter sorry to have asked questions on your thread. I am a newbie too with osb. Hope you can exchange the everbuilt house wrap still. My house will have lp smartsiding. I will be sure we get the tyvek house wrap and related tape accessories.

  • 7 years ago

    Not sure why but my photos don't show up on this forum. Maybe they are too big. At any rate: It's a pretty small area. I'm enclosing a 13x16 screened porch that was already a part of the footprint of the house and shares a roof with the house. I've done the framing and sheathing. There are 5 3x5' windows and a door so it's not a lot of exterior wall space. The plan is to put house wrap on the OSB and then 1x12 pine siding on that. The siding was on the inside of the porch so I already have it. I assume that is what is meant by cladding.

  • 7 years ago

    The photos should be jpg files and if they are large there will be a delay while they are reduced. It might be necessary to reduce their size first.

  • 7 years ago

    Peter, talk to the inspector and find out what they say. They are supposed to be the professionals.

  • 7 years ago

    Peter doesn’t want to nail the sheathing before the inspection and apparently it must be nailed in order to get the inspection so he is asking our advice. The alternative would be to take a photograph to the building dept. but this seems like a simple issue that any experienced designer or builder could put to rest from a photo if he can get it posted. As long as the joints are blocked and the nailing is correct I doubt there would be an issue and there might be other issues that arise from the photo that could be fixed before inspection.
    DensGlass is often used for commercial projects because it’s non-combustible and it isn’t usually needed for lateral bracing.
    I’ve used it behind brick but taped the joints with Grace Vycor and water based primer. Some like to add a coating like Sto offers.

  • PRO
    7 years ago

    From the OP's description, it doesn't sound as if there's enough wall area to provide much in the way of bracing, so perhaps the only thing that matters is the city inspection and approval.


    Check with their office for their requirements.

  • 7 years ago

    ANother attempt to upload photos


  • 7 years ago



  • 7 years ago



  • 7 years ago

    I inserted blocking behind all the seams that were not already supported by the framing.



  • 7 years ago
    last modified: 7 years ago

    This would not get an inspection pass. That outside corner needs to not be pieced. Both of those corner sections need to be from a full single sheet, cut around the window penetration, not in small patchwork pieces. The point of the sheathing is to add rigidity. Small pieces with a seam line at a stress point contribute nothing to that rigidity.

  • 7 years ago

    make sense but the entire height is more than 9 feet so there would have to be a seam somewhere.

  • 7 years ago
    last modified: 7 years ago

    As long as the corner windows cutout area was from a single sheet, with meat top and bottom, the second seam would be allowable. But no seaming at penetrations on corners. It’s a gray area here for the other seams at windows.

    If there were the required Simpson ties holding down to the foundation, and holding down the roof rafters as well, attached properly to seismic and high winds requirements, the other window corner seams would likely get a pass, because that wall is tucked in and attached to the other wall, which stabilizes it. That Simpson is less than $50 worth of hardware on a project like that. It’s well worth it.

  • 7 years ago

    In a related matter, should I remove the OSB that is on what used to be the interior walls of the screened in porch? These walls are now to be the interior walls of the new space and I wonder about the formaldahyde.. If I remove this OSB I could use it to replace some of the OSB in the pics above. I could use it to solve the problem that GreenDesigns identifies.

  • 7 years ago

    GreenDesigns: FYI I just drove by some new (professional) construction in my area that had this very same sheathing construction on an outer corner. It could be that the inspectors in Charlotte, NC are less particular than in other areas.


  • 7 years ago

    I have a somewhat random question. In your last picture you can see a picket fence fairly close to the new wall. Is this a property line fence or is it a fence within your yard? The reason I ask is that when we applied for a permit we were allowed an exception to build about 4 1/2 feet from our property line. However, since it was less than five feet from the line, we had to use a fire rated wall assembly. This required special fire rated exterior sheathing and thicker 5/8" interior wall board to achieve the fire rating.

    Bruce

  • PRO
    7 years ago

    I agree. If this was originally a screened porch, it likely contributed nothing to the strength and rigidity of the house.


    The best thing to do is simply go to the building officials office and ask for their requirements to transform the porch to a habitable room.


    Simple!

  • 7 years ago
    last modified: 7 years ago

    Presumably, Peter has already submitted drawings that should have addressed the important code issues and received a building permit and I believe he said the inspector had already approved the framing. I doubt there is any way he could hang the OSB that the inspector would not approve if it was fully nailed and blocked per code but if he's nervous, he should take the photos to the building department when the inspector is normally there. The inspector will probably accept 6d nails which will be easier to install so its worth a trip. His additional panel cuts only cost him additional nailing.

  • 7 years ago

    Thank you RES 3d. Yes, the inspector has approved the framing. This was only a question about the sheathing. I am second guessing myself before the final nailing after belatedly reading what was written on the panels. A structural engineer told me that because it is not exposed on three sides there were not wind issues.

  • 7 years ago
    last modified: 7 years ago

    Like 3D said bracing and shear wall design are based on "exposure". I was concerned from your original statement that there was not even 2' on the outside corner. There is. I would never allow this style of continuous bracing line for a house, but for porch.. Ideally one would sheath entire wall [not required only certain percent] . If you ever attend the LWC class on resisting lateral forces - you can blow your brains out, so mind numbing. In the end your inspector will not understand anyway ... so if he is ok good for you. Follow the nailing scheduler.

    Peter de Klerk thanked BT
  • 7 years ago

    This addition uses what the code calls "continuous sheathing". The lateral resistance of continuous sheathing is determined by the width and location of any and all "braced wall panels" which must be at least 24" wide and full height. The lateral resistance of portions of the sheathing above or below window openings (including where it is part of an L-shaped panel) are not recognized by the code.

    However, its a moot point since it was the opinion of the owner's engineer that additional lateral resistance was not needed.



  • 7 years ago

    Update. I decided to roll the dice and I nailed the sheathing into place today (every 6 inches on perimeter and 12 inches on the in between studs, etc.). Hopefully the inspector will be OK with it. Since so many people have kindly advised me on this I will post the results.