Fried GFI?

19 years ago

I had some electrical problems yesterday and would like some insight and advice.

My set-up is two 15 amp breakers in my inside box for the pond power. Outside I have a switched, 2 receptacle GFI box and a second box with two double receptacle GFI. I have assumed that each box ties to one of the 15 amp breakers.

I plugged a new external pump into the switched GFI, along with my other pump, hit the switch and it was grand for a few minutes until everything stopped. I figured too many amps for the breaker, read the little plates on the motors and sure enough.

The GFI receptacle in the switched box will not re-set--tried all the tricks I could think of. Oddly, the new pump is two speed and I can't seem to switch from one to the other now.

Is this GFI receptacle fried and need to be replaced or am I missing something? Can a 15 amp breaker be replaced with a 20 amp or does that negate the protection of the GFI? Does it sound like something is fried in my new pump motor or speed switch?

Is receptacle replacement DIY or should I wait however long for an electrician. Either pump runs alone on the other curcuit, but I sure want to play with my new toy.

Thanks in advance - Mike

Comments (13)

  • 19 years ago

    Sorry, can't help. Might have better luck posting at the 'Garden Web Electrical Wiring forum.

    Here is a link that might be useful: Electrical Wiring forum

  • 19 years ago

    There are two things that will prevent a GFI from being reset. One is just the kind of thing a GFI is supposed to do, which is detect current leakage. If there is an ongoing current leakage the GFI will not reset. The second possibility is a fried GFI.

    To test which it is, remove the load wires from the GFI, leave the power source wires on, and try to reset the GFI. If it resets, the problem is in the load circuit, which might, or might not, be your pump. If it doesn't reset the problem is the GFI.

    If it does reset with the load wires removed, hook them back up, and disconnect whatever is next in the load circuit, and see if you can reset the GFI. Keep going like this until you find the part that pops the GFI.

    Since you asked if this is a DYI, I have to say it is IF you know how to not electrocute yourself while fooling with the wires. Be smart turning the breaker off while you work, and check stuff with a tester before you touch it. If this sounds scary, call an electrician.

  • 19 years ago

    Adding to Larryl's wisdom - You could replace the GFCI yourself, if you find that's the problem. It's pretty easy and they usually come with good instructions. You can't change the breaker without also making sure your receptacle is also 20 amp (they make 15 amp) AND making sure your wires are sized for 20 amp. 14 gauge is usually used for 15 amp circuits but you'll need 12 gauge for 20 amp. It doesn't sound like too big of a job but wiring is new to you and you want to play now (don't blame you a bit!). I'd (over)pay an electrician now - and have him show you and explain what he did and why - then get a couple books on basic wiring for the next time you have a problem.
    Vanessa

  • 19 years ago

    Thanks - I think I understand the problem now, I was a little confused about the amps (total of two pumps was 1 amp less than breaker) until someone told me about the relationship between decreased voltage and increasing amperage. If I have it right.

    Anyway, these two circuits were installed specifically for the pond, there are no other loads to check. From what you all have said, most likely I fried the GFI.

    I will install a new 15 amp GFI receptacle to match the 15 amp breaker. I don't understand all the physics but have made repairs and know this is within my abilities. Anything more, or any problems, and I will get my electrician on the scene pronto.

    The pump that doesn't switch speeds apparently is OK, may have been wired incorrectly--single speed instead of two speed, according to the seller and Mike IL.

    Thanks - if I run into snags I will be back.

    Mike

  • 19 years ago

    Mike,
    I think you have a switch that was wired improperly. For the novice, there is a wiring procedure which is overlooked. If that could be the possibility let me know and I can tell you the proper connection of the wires. If it was done by an electrician, it was probably wired correctly. If done by a novice, there is a very good chance the switch and plugin is incorrect.

  • 19 years ago

    Iam a licensed electrician so perhaps I can help. Alot of times it is simple things that are overlooked, & easily fixed.
    1. Reset the breaker. Flip the breaker to the off position until it clicks & then on. Sometimes when a breaker trips & you just flip in on it wont fully reset.
    2. Sometimes a GFI outlet will not reset without power so if the breaker is off then pushing the GFI reset button wont work.
    Try that & let me know if it works. You would be amazed at how many times I have been called out to fix a problem & this is all that is wrong.

  • 19 years ago

    Well, older but possibly wiser, definitely not fried myself.

    This dedicated system for my pond was installed by a professional electrician. I did know lots of the tricks of flipping breakers etc, but no matter what the GFI wouldn't reset.

    I replaced the GFI receptacle easily, done that before. Hit the breaker and had power. Plugged in the pumps, each in a separate circuit and it was great.

    When I bought the GFI I didn't pay attention that there were three receptacles in the box. Working around the pond area, my friend suddenly started using a circular saw on a pump circuit. Lights out--the saw draws 13 amps, something I never thought about. Another GFI was fried but at least I had another. All seems well right now.

    One receptacle we removed was rated at 20 amps, but the breaker is 15 amps. What does this mean.

    What causes these GFI to get "fried?" What is "fried?" I thought the purpose was to shut down and protect.

    Wonderful, helpful responses. Nothing more gets plugged into those GFI.

    Mike

  • 19 years ago

    "One receptacle we removed was rated at 20 amps, but the breaker is 15 amps. What does this mean."
    This means that someone put the wrong size receptacle in. Only 15A outlets can go on 15A circuits, but on 20A circuits you can use 15A or 20A outlets.

    "What causes these GFI to get "fried?" What is "fried?" I thought the purpose was to shut down and protect."
    Fried in your case is where the outlet was overloaded to the point it overheated & melted something in the GFI. Normally the breaker should trip before this happens. This tells me your breaker may be faulty & should be replaced. A GFI outlet trips only when it senses a "shock" hazard, basically a leak in current, not an overload.

  • 19 years ago

    Am I all screwed up or what? A 20A receptacle on a 15A circuit should be safe as the entire circuit is protected against anything higher than a 15A draw, while a 15A receptacle on a 20a circuit could cause a problem as the entire circuit is able to draw 20A, or am I mistaken??????
    Don

  • 19 years ago

    It does seem kinda screwy, but the reason is because a 20A circuit can handle a 15A load where as a 15A circuit cant handle a 20A.
    If you compare a 20A plug & a 15A plug you will notice the "blades" are different. The 20A has one that goes sideways. Technicaly if a tool or what ever is rated above 15A it will have a 20A rated plug on it. This is so you can not plug it into a 15A receptacle because it would just trip because it would be overloaded. But on the other hand a 15A plug can fit into a 15A or 20A receptacle because it can handle the load.

    Now you are right as far as if you plug in 2 seperate 15A plugs on a 15A receptacle on a 20A circuit you could possibly exceed 15A & overheat the receptacle. Which is what might have happened here.
    Even though the national electrical code allows this, I would recommend you use 20A receptacles on 20A circuits for this reason.

    Hopefully this helps & doesnt confuse you more.

  • 19 years ago

    That was what I meant, If you put a 15A receptacle on a 20A circuit, you could overload the receptacle, and not blow the breaker. On the other hand, a 20A receptacle on a 15A circuit should not cause a problem as you should never reach the 20A load of the receptacle due to the 15A breaker......

    Don

  • 19 years ago

    After researching a bit I found out that a 15A receptacle is actually rated for a 20A load. Thats why it is allowed on a 20A circuit. The 15A rating is basically for preventing pluging in a 20A plug when used on a 15A circuit.
    Also, this is not what might have happened here because the circuits in question are 15A anyway. (Sorry my bad)

  • 19 years ago

    Wow, a great education, all easy to follow. Thank you.

    After being away for a long weekend (pumps unplugged-no fish, plants), I plugged in one pump in each circuit. Everything seems just fine and if I use these dedicated circuits for their intended purpose and not for high amp tools, I think I'll be OK.

    Next step is to get my electrician on the scene and have him walk me through from breaker to wires to receptacle and see what works best, is possible, for the set-up.

    Lessons learned here are important. Especially the safety and risks I obviously need to know more about.

    Mike