Do you need a special glass in the windows?

13 years ago
We are having a clawfoot tub installed by the bathroom window in our new home. Builder said that code requires a tempered glass in the window for safety precautions.
Rustic Bathroom · More Info

Comments (2)

  • PRO
    13 years ago
    The code says that any window that is within 18" from the floor or 24" from the jamb of a door MUST be tempered. Additionally, if you were creating a bathtub "enclosure" then you would be required to provide tempered glazing. The Residential building code section R308.4 covers this issue. If your window meets one of these conditions then the contractor is right. If not, then you may want to follow his recommendation as a precaution. It is possible that an inspector may view the window as an "enclosure" for your tub however, I believe the intent of this code section is to regulate all glass enclosures.

    the following is the code section:

    R308.4 Hazardous locations. The following shall be considered
    specific hazardous locations for the purposes of glazing:
    1. Glazing in swinging doors except jalousies.
    2. Glazing in fixed and sliding panels of sliding door
    assemblies and panels in sliding and bifold closet door
    assemblies.
    3. Glazing in storm doors.
    4. Glazing in all unframed swinging doors.
    5. Glazing in doors and enclosures for hot tubs, whirlpools,
    saunas, steam rooms, bathtubs and showers.
    Glazing in any part of a building wall enclosing these
    compartments where the bottom exposed edge of the
    glazing is less than 60 inches (1524 mm) measured vertically
    above any standing or walking surface.
    6. Glazing, in an individual fixed or operable panel adjacent
    to a door where the nearest vertical edge is within a
    24-inch (610 mm) arc of the door in a closed position
    and whose bottom edge is less than 60 inches (1524
    mm) above the floor or walking surface.
    7. Glazing in an individual fixed or operable panel, other
    than those locations described in Items 5 and 6 above,
    that meets all of the following conditions:
    7.1. Exposed area of an individual pane larger than
    9 square feet (0.836 m2).
    7.2. Bottom edge less than 18 inches (457 mm)
    above the floor.
    7.3. Top edge more than 36 inches (914 mm)
    above the floor.
    7.4. One or more walking surfaces within 36
    inches (914 mm) horizontally of the glazing.
    8. All glazing in railings regardless of an area or height
    above a walking surface. Included are structural baluster
    panels and nonstructural infill panels.
    9. Glazing in walls and fences enclosing indoor and outdoor
    swimming pools, hot tubs and spas where the bottom
    edge of the glazing is less than 60 inches (1524mm) above a walking surface and within 60 inches
    (1524 mm) horizontally of the water’s edge. This shall
    apply to single glazing and all panes in multiple glazing.
    10. Glazing adjacent to stairways, landings and ramps
    within 36 inches (914 mm) horizontally of a walking
    surface when the exposed surface of the glass is less
    than 60 inches (1524 mm) above the plane of the adjacent
    walking surface.
    11. Glazing adjacent to stairways within 60 inches (1524
    mm) horizontally of the bottom tread of a stairway in
    any direction when the exposed surface of the glass is
    less than 60 inches (1524 mm) above the nose of the
    tread.

    HOPE THIS HELPS!!!
  • 13 years ago
    It sure does, thank you very much!