kevin1727

testing shower floor before tiling

18 years ago

My contractor finished the mortar bed floor over the membrane yesterday. When I got home I noticed the shower floor seemed very wet and shiny, and it did not look like the photos on the Ontariotile web site. It is gray instead of brown. It has dried today, the surface is soft like stucco siding, and I can rub away sand particles easily with my hand.

I am questioning whether the contractor used the right mortar and/or mix. He claims he did this with the same sand/mortar mix as he does on all other shower floors. He knows I am watching him closely as he even took a photo to show the pebbles he put around the drain before adding the mortar. I found a bag of modified mortar mix on the site, but haven't confronted him yet about it. We have already had other issues, and I don't want to falsely accuse him.

Is there a test I can do to verify the mortar bed will do what it is supposed to do? I seem to remember someone saying you can pour water on the floor and it should soak in and come out the weep holes. Is there a time limit for the water to soak in? Does the floor have to dry more before I do this test?

Comments (7)

  • 18 years ago

    If the floor is done properly the surface will be a little sandy. I wouldn't go screwin' around with the guy and adding any water to his work without him agreeing to it. Besides what's that going to prove?

    You found modified mortar mix onsite? So what? What does that have to do with anything? I guess I'm missing something here. Are there any "real issues"?

  • 18 years ago

    Hello Bud,
    I thought the sandy part was correct. My concern is that the guy has had to redo several things that were not done correctly. He has already fired a carpenter and plumber because of poor workmanship and code violations. He has corrected every problem I found but "he" never seems to spot any problems.
    According to the instructions on the Ontariotile website you are not supposed to use any additives in the mortar mix and the mix is supposed to be dry, not soupy. Several people have referenced this site.
    The real issue is that I don't trust the guy to do it right and I want to make sure what he is doing is correct. I need some way to inspect this mortar bed before he gets the job finished and I find that water doesn't drain from under the tile.

    Here is a link that might be useful: Example of improper mortar bed.

  • 18 years ago

    Sounds like the cement is about right. It should be gray.
    More importantly, did he put a mud pre-slope under the membrane?

  • 18 years ago

    Kevin the commonality between all pros that live on the tile forum websites is that the cement mixed for the installation of a shower floor is to be mixed very dry. It is mixed of Portland cement and sand in a ratio of 4: or 5:1 (sand to Portland). After mixing one should be able to grab a hand full of the mix and squeeze it in his hand thereby packing the mix tightly but no oozing of the mix between the fingers. If the recipe is off a little it's not a big deal. No additives are usually used in this recipe simply because the floor is to be cast and NOT poured. The shape and slope of the floor is then shaved and not shaped with a trowel necessarily as in finishing a concrete slab. The reason for the dry mix is so that the proper slope (1/4" per ft.) can be maintained without slumping of the mix and a distortion of the slope. The raw sand and Portland recipe lends itself to this shaving process. Additives tend to disrupt the shaving and cause a trowel to drag on the surface rather than glide across the surface.

    If an installer wants to use some additive that's his business, some do some don't, but it's nothing for you to be worried about. If you were to contact Harry at Ontario Tile I'm sure he would tell you the same thing.

    I don't know what this guy has had to re-do but for now the facts are he's doing OK so far from what you are saying and the deeper truth is we are only getting one side of the story. If you are micro-managing the guy at every turn then you should expect some issues from him.

  • 18 years ago

    If you are micro-managing the guy at every turn then you should expect some issues from him.

    That's why I've left this thread alone. If you can't trust the guy to do what needs to be done, get someone in there that you DO trust, or do it yourself. I've never had a problem with a customer who looks over my shoulder asking me about what I'm doing. I do, however, have a problem with a customer telling me how to do my job. been there, done that, won't do it again. Period. Quite frankly, right from the opening post, it sounded like you were LOOKING for a reason to can the guy.

    Kevin, I know you've seen some of the horror stories in here, and it's obviously got you paranoid as hell. You said the carpenter and plumber were a problem, not the tile guy.

  • 18 years ago

    Thanks terriks, Bud, and Bill. I feel a lot better right now. I wonÂt worry about testing it.
    I like this guy because he is trying to do things right and he is agreeable whenever there is a problem. I started double checking the work after his plumber installed the drains not to code and used the wrong fittings on the shower fixtures. His carpenter put a wall up 1" out of plumb, forgot to nail several studs, misaligned the light fixtures, and built the tub surround ¾" out of level from one end to the other, not to mention the dozens of nails that missed their mark and split most of the 2x4s. The contractor missed all of that and said everything was perfect. We did a walk through together and he was embarrassed. He told me that carpenter and plumber would not be back. Whether he is using them elsewhere I donÂt know but all those things have been fixed.

    The new guy presloped the pan but only after I asked him to. He hadnÂt planned to do that. If that is micro-managing to tell him code requires the membrane to be sloped then it is probably a good thing I am doing that or else the membrane would be flat on the concrete slab right now. There was also the hole I found poked in the floor of the membrane that I asked him to patch. He didnÂt realize he had done that either.

    IÂm wouldnÂt say IÂm micro-managing him as much as I am just inspecting everything he does. He agrees with everything I point out, apologizes, and has his guys fix it.

    Yes Bill, I am paranoid, but I donÂt really want to can this guy. I would probably end up with the same situation and spend a lot more money plus I doubt I will find anyone who is honest and admits if he made a mistake. I donÂt think I am irritating him since he has mentioned to my wife that he likes the work and is learning things from me. Example  tape a ¼" thick block 12" from the end of level to check the slope quickly. I have also been loaning tools and sweeping up after them, so I wouldnÂt consider myself a slave-driver. I just want it done so it doesnÂt have to be torn out ten years from now.

  • 18 years ago

    The new guy presloped the pan but only after I asked him to. He hadnÂt planned to do that.

    it's not right, but there are alot of tile guys, plumbers, and GC's who have no idea that the membrane is suppoed to be pitched! THat's why we harp on it so much in here. So although it's good that you caught it, and better that he was agreeable to installing the preslope without too much BS, but I wouldn't be too upset about him not knowing about it.