17 years ago

I want to replace my electric cooktop with a 30" Bosch induction cooktop NIT5065uc that according the specs uses 7200 watts. Using my 240 volt service and dividing that into the wattage of the cooktop give me a 30 amp service requirement. However the technical spec sheet and instruction a manual calls for a 40 amp service. Can I use my existing 30 amp service for this cooktop without encountering problems?

The cooktop is on the kitchen island on a concrete slab with no walls for easy access, so running a new service would be difficult and expensive. It seems to me that their spec for a 40 amp service is conservative and could in fact be more dangerous in certain circumstances.

Comments (12)

  • 17 years ago

    NIT8053uc is a 30 inch full induction Bosch cooktop that requires only 30 amps. It has a very large 12" burner.
    chances are that you would only need the 40 amps if you were to "Power boost" all of the burners at the same time.
    As a matter of fact, we never use the power boost on our Electrolux Icon Induction unit---the thing is terifically fast even without doing that, and I dont have to remember to turn down the boost to keep the pot or whatever from boiling over.
    If you have your heart set on that 40 amp model, You could have an Electrician check the guage of wire that is going to your old stove---it may be off sufficient gage to carry the 40 amps---not that you would ever use it, just to keep things legal--permits and all that---ya know what I mean?
    If wire is correct gage (or is it guage, Thickness), then assuming your main electrical service can handle it, all you would have to do is install 40 amp breakers.

    Good luck, whatever you decide.

    See the link below for more info on the 30 amp Bosch. You can also checks sources such as AJMadsion for more details, including an operator's manual on either of these Models.

    Gary

    Here is a link that might be useful: 30 Amp Bosch Induction Cooktop

  • 17 years ago

    Their spec for 40 amps has to do with running at 208 volts. And also the powerboost functions.

  • 17 years ago

    Just keep in mind that if you don't follow the manufacturer specs, and you have a fire in your house that is traced to electrical circuits, your insurance company may use that opportunity to deny your claim...

  • 17 years ago

    Not to get too technical, but...

    The wattage used by any electrical system is not simply the voltage times the current. The "power factor" (pF) is also part of the equation. The actual formula is: W=V x A x pF. The pf can range from 0 to 1.

    In an induction system the pF is a number much below 1. Thus, to get a wattage up to 7200 watts, the current must go higher than 30 Amps when using a 240 Volt supply.

  • 17 years ago

    If your house is fairly new, then you should only need to change the breaker. I'm looking at going from a 30 inch electric to 36 inch induction and will be going to 50amps. I was told that I only need to change the breaker.

  • 17 years ago

    I hope you were told by an electrician that checked the guage (thickness) of the wiring to your new induction unit.
    More than likely the plug or the junction box where the new appliance will be hooked up will need to be changed too.
    The other poster make a good comment about possible insurance problems.

    Gary

  • 17 years ago

    I think all our comments are just to be sure you do the right thing when the new cooktop is installed.

    I recently changed from one wall oven to another which used more current. This required pulling new, heavier gauge wires in the EMT conduit within our walls and changing the circuit breaker from a 40 Amp to a 50 Amp.

    All I needed to do was buy new wire and a new breaker. Pulling the wire and changing the breaker took 30 minutes, tops.

    You can do it if you're fully aware of the safety procedures. Or hire someone.

  • 17 years ago

    Ya know folks, we may be talking to ourselves, here!!
    Other than the original post by the OP, we haven't heard a peap!!--- has this OP posted before¿ Some good ideas here, like pulling heavier wire through,

    Gary

  • 17 years ago

    IÂm not the OP, but I am interested in this info too. IMO  on forums such as these, you are never talking to yourself  there are probably lurkers who gain from every post. :-)

    Maybe you can answer this for me  I donÂt fully understanding this myself, so I hope that you do. I keep telling my husband how "green" induction cooking is. But he says that canÂt be true if we need 50 Amps. WhatÂs the story???

  • 17 years ago

    Are you just looking at an induction cooktop (If so, which one), or are you looking at an Induction Range?
    all of the manufacturers "figure worst case" when computing the electrical service.
    They figure you are boosting all the burners at the same time(Those that don't share power boosts) along with the oven/ovens turned to the highest settings or self clean.
    We have had our Electrolux Icon Induction cooktop for 6 months now, I beleive it required 40 amps.
    I never use the boost as the thing is amazingly fast without it---I used it at first ---just to show off with the neighbors---put a paper towel under the pot, added a cup of water, and kicked her to full boost---they were amazed at how fast the bubbles first formed and then boiled.
    As the induction cooktop only heats the pot, not itself, or the surrounding area, it is very efficient.
    You will see posts on this site where people mentioning a lot of the gas flames going around the pot and with it the heat.
    According to different sites, I have checked, Induction is the most energy efficient way to cook---It has been used in Europe for many years, as they have the jump on us when it comes to energy efficiency---they had to be efficient in many parts of Europe---they aren't blessed with the energy resources we have or the "Comparatively Low" prices of energy that the US has.
    We have a 2700 sq ft house, S Calif---have not had to run AC--so far this year, and our last electric bill was $55 and that is running the induction cooktop, most every day.
    Hope this helps!!

    Gary

  • 17 years ago

    Thanks Gary! We're in S Calif too - Ventura County. :-)

  • 17 years ago

    Great jeri, We will be up your way in about 2 weeks for a car show in Solvang.Maybe you can come by and see us there.
    Look for the biggest red convertible in the show!!
    That will be Me.

    Gary