txmat

Circuit Breaker for HVAC Question

12 years ago

This AM the circuit breaker on the house panel for the HVAC air handler and thermostats tripped. I reset and it tripped again in about an hour. A technician came out and advised me that the CB on the house panel was 50 amps and on the air handler there was a 60 amp circuit breaker which was also wired to a 30 amp circuit breaker. The 60 amp protects the blower and other components and the 30 amp the heat strips (This is a heat pump). The technician suggested I needed to change the circuit breaker on the house panel because I was actually pulling 90 amps. Now to summarize as I understand it electricity enters the house through the 50 amp circuit breaker and then travels through the 60 amp CB and then for the heat strips travels through the 30 amp CB. This setup has been working this way since 2009, so I am wondering first, is he correct; second, do I need to change the house panel circuit breaker; third, if yes than what amperage should it be? I will appreciate any help you can give me in understanding this.

Comments (10)

  • 12 years ago

    The technician may be correct-- or not. I think you need a good electrician. Your post does not indicate that you are ready to personally adequately address this situation.

  • 12 years ago

    If you paid him,insist he give your money back then get somone who knows what they are doing.

  • 12 years ago

    Thanks. Jreagan, the panel has several breakers. There is a 50 amp for the outside part of the heat pump plus the one I am asking about which is 50 amps for the inside portion of the system. These are just the two breakers in the panel for the HVAC. They are not for the whole house. There are several other breakers in the main panel and three sub panels. I am asking about just the one breaker that tripped a couple of times today. I think I understand that even though there is a 60 plus a 30 amp breaker on the air handler there can be no more than 50 amps running through them because that is the size of the breaker at the panel or "upstream." Can I assume that since the system has run without problems for 4 years it probably does not need more than 50 amps.

  • 12 years ago

    Your assumption is correct.
    You need somone compitent to, (A.) Test amp draw of unit to see if it is drawing more than 50 amps or if draw is only 40 amps tripping a worn out 50 amp breaker. (B.) If unit is drawing more than 50 amps,find what is wrong and fix it.(C) If draw is less than 50 tripping worn out breaker,replace breaker.
    Everone has told you to have it looked at by a pro. It is not wise geathering information to pass on when he arrives.

  • 12 years ago

    Thanks. Klem1, I do not understand why it is not wise to gather information to pass on when a pro arrives? If you mean it is not wise to tell him how to do his job, I agree. But, how does it hurt to have an understanding so that I can understand what the pro is telling me and evaluate it? I mean the AC guy is a "pro", but when he suggested I needed to replace the 50 amp house panel breaker with a 60 amp I was skeptical and so I came here to one of my favorite sites. If I had blindly followed his advice, maybe nothing bad would have happened, but it may have been an unnecessary expense. Do you think I am wrong to question what I am told? Everyone's suggestion to get an electrician to determine the load and size the breaker and wiring accordingly makes sense to me. I just don't understand what your meant by that sentence.

  • 10 years ago
    last modified: 10 years ago

    The solution is quite simple, first of all both the compressor & air handler have their own breakers, so long proper permits were obtained and installed by licensed professional than hvac for your home should meet or exceed code therefor, problem existing with hvac directly in this particular case is not the issue unless breakers on either unit are being tripped, if not than issue lies with breaker at panel, most likely worn out, in such case breaker gets hot under load and trips, the time period of such being determined by amount of breakers deterioration, in any case changing it would be the solution.

    FYI, hvac breakers wear out just like any other. In the past I've used domestic (OEM) breakers from Home Depot which had to be replaced after 2-3 years of use.

    [ S. Florida AC set to 73 ] Quality vs. Lifespan.

  • 10 years ago

    b.nyc please say you are not a technician and taking people's money based on conclusions like that.

  • 5 years ago

    I'm not seeing what the flaw in his conclusion is klem1 could you elaborate because I pretty was thinking along the same lines maybe minus the whole code spill but from what the guy said the panel breaker is flipping but the other two are not then one you look at the name plate.and if it calls for a 50 amp breaker then you need to change the 60 amp to a 50 if it calls for a 60 amp breaker then you need to change the panel breaker to a 60 breaker and then for good measure test the amp draw after you change the breaker to make sure that it is not drawing to many amps and if problem persists them I would start with the contacts in the motor and work my way back

  • 5 years ago

    Hi Clayton,welcome to houzz HVAC forum. The flaw in b.nyc's conclusion is that breakers sold by Home Depot can be expected to wear out within a few years. "NO BREAKER" should wear out in 2-3 years and breakers sold by Home Depot come from the same manufactures as those sold elsewhere.

    ^^^That^^^ answer's your question. Since I have time on my hands,I'll elaborate farthar on my reply to b.nyc and this thread in general. Notice that I said conclusions,not conclusion. When I posted my reply to b.nyc,there were a bunch of other bad information in his origional post. If you look just below his name you will see where he sneeked back and attempted to eliminate his misinformation after I posted.

    The op and this thread could be a poster child (npi ) for folks seeking silver bullets for problems they encounter. Daily people go on the net and through so many words basicly ask that pros tell/teach them in 25 words or less what required the pros years to learn. To the uninformed it seem's simple but that's far from the truth. A couple examples in this short thread. OP was offended that I advised aginst "geathering information to pass along when a pro arrives). It's simply not possible to cover all the bases in 25 words or less,if it were,trade school could be completed in a day and technician would be experienced 2 days after entering the field. Clayton,go back and read your post. You reccomended replacing the 60 amp near air handler if rating plate caled for 50 amp circuit. The 60 amp IS NOT protecting the equipment,it is simply a disconnect that could be and often is 100 amps by code. The worst part is that you replaced the breaker(s) BEFORE running tests.

    I'm not shaming any one,I'd just like folks to realize a little information can be expensive at best and at worst dangerous. I've laid out this challenge that at worst could make one look weird for a few day and no one want's any part of it but they still want to risk destroying their home or possibly kiling themselves by trying to fix things via the net. Ask that someone tell you in 25 words or less how to cut your own hair.