Hot Water Radiators

19 years ago

I have had a house with radiators for 3 years now. They have worked properly for 3 years with just a little air released throught he valves at the beginning of winter each year.

This year, one of the radiators makes trickling noises. Maybe the radiators always did have to fill up each time they kicked in, but I never heard water trickling in before. Also, the air release used to continue to hiss until a little jet of water came out. Now, it hisses for a few moments and then nothing. If I turn the valve off for a minute or two, again it will hiss for a few moments and then nothing.

I did have something replaced about 2 weeks ago, a thing that helps the pilot light turn on the burner - a CDM or DMC - I don't remember right now. The technician told me he had checked to see if there was enough water in the boiler, and there was.

Does anyone know what could be causing this, and better yet, what I should do about it? The radiator does heat up just fine, but I worry that I may cause some damage running it the way it is.

On the first floor, the radiators are the baseboard variety and I don't see anyplace on them to check if air needs releasing. On the second floor, there are 3 old hot water radiators with the release valve. The other 2 radiators have no air to be released. A water jet comes out immediately. Thanks for any suggestions. Carmellia

Comments (2)

  • 19 years ago
    last modified: 11 years ago

    I'm probably not going to tell you what you want to hear, but I am going to let you know what you should know:

    "The technician told me he had checked to see if there was enough water in the boiler, and there was."

    Now, do you know where the water guage is, the pressure guage and the temperature guage? That is how you tell what is happening in the boiler. You can have burners on and very little water in the system which can lead to problems, serious ones. Every homeowner should know something about their units. To be ignorant is not bliss.

    Anytime you let air or water or both out of a bleed valve, the pressure in the system drops and you will eventually need to add some water from the inlet valve. This should be marked and off during normal operation. Also, you have an expansion tank? Probably. It needs to be checked also. They get full and then the heated water has no place to expand.

    You should only need to bleed from a radiator upstairs, not the baseboards although they pronbably have a bleed valve screw also. At the end of the run. Do you know how to know if a radiator top is full of air? By feeling with your hand. Cool top sections may mean air is trapped there and heat doesn't transfer as well thru the air pocket. Do you know if the valves on each radiator are open? Not the bleed valve but the inlet near the bottom of each radiator. They may be 1/4 turn valves, not like on a garden hose valve on the house.

    You might call the tech back and this time have him show you where things are and what you should be aware of. Did you have a thermocouple changed? (CDM/DMC), is what?

    What is the psi and temp reading on the guage when the boiler is operating? Should be a guage on the top or side of the boiler.

    " "Maybe the radiators always did have to fill up each time they kicked in, but I never heard water trickling in before."

    Think of the radiator system in your car. There is x amount of water and antifreeze in the system. It is always there waiting to extract the heat from the engine block and dissipate it thru the radiator coils. Once the car starts, a pump circulates the water. It is always there, but sitting still when the system is off. A fan is added next to the radiator to speed up the process of dissiapating heat. Also, a heater coil (mini radiator) is installed in the passenger compartment with a fan to use some of that heat in the wintertime to warm the occupants.

    If too little water is in the system, it overheats, boils, and the excess pressure opens a safety valve on the radiator cap allowing the overheated water/antifreeze to escape. Remember the old pics of the stranded motorists?

    Your boiler also has a safety valve, and opens at about 30psi. You probably should have about 12-14 psi in the system whether or not the boiler is on or not. You may have a circulating pump on that system also and should know something about it also.

    As for the trickling noise, I would call the company back and report that there is something different with the system after the tech visited and that he did not fully explain things to you. Try to get a free visit buy you may have to pay something for their time. Remember to ask about the expansion tank. Do you have yearly service?

  • 19 years ago
    last modified: 11 years ago

    Thank you for your wonderful detailed answer. I have printed it out. Now I will take a look at my equipment and see what I can recognize. Wish me luck. Carmellia