Zone valve replacement?

16 years ago

Seems as though, when my hot water heater fires up by the furnace (Energy Kenetics system 2000) my one zone valve is staying open allowing hot water to enter the baseboard heating run. This is with the heating controls (on the thermostat off or on and the setting well below automatic)

Two questions-

There is a manual gate type valve directly above the zone valve. If I shut this manual valve, is there any compromise I should be concerned with?

ItÂs a Invensys pop top control valve # vt2317g13a030 I was quoted $200 just for the valve. Does anyone know of a replacement that is less costly? I will install it myself

Comments (11)

  • 16 years ago

    As long as you have some zones left to dissipate your heat, you can shut off any zone you like.

  • 16 years ago

    Tell me what lights are lit on the system manager, left side (input) and right side (output). How many heating zones are there? If you turn off the power to the system does the valve close?

  • 16 years ago

    Dapoppa,
    No lights until hot water is being made, then upper most lights, one on left one on right.
    One heating zone.
    I turned off the system manager, don't know if it closed. How would I tell?
    PS I heat with a wood stove, so only use the boiler for hot water. Thats how I noticed. The baseboards were warm even though the heat wasn't on!
    Thanks
    Glenn

  • 16 years ago

    if the light comes on it sounds like its opened. do you have a heating coil ?

  • 16 years ago

    Wise, The lights for the hot water function come on.
    Zone one lights do not come on. Which heating coil are you referring to?

  • 16 years ago

    let me ask another question, your boiler makes the hot water for your domestic, that much I understand. do you have a seperate zone for that with a holding tank or is it what we call a tankless coil, which is a coil in side the boiler with a copper line going into the coil and it heats up and then comes right back out of the coil.
    you said you have two lights one for hot water and other for space heat. if the hot water comes on and the space heat doesn't it is possible that the zone valve is stuck open and just heating the line when there is a call for hot water. I need more info
    1. 1 zone with a tankless coil
    2. 2 zones with a indirect water heater
    3. How many wires coming off the zone valves and are they hooked up to a zone control board.

  • 16 years ago

    Wise,
    There is a separate hot water tank that primarily gets heated by the boiler.
    There are two wires that go to the system 2000 energy manager.
    My system is similar to the one I attached. I have a conventional electric hot water heater being used.
    http://www.energykinetics.com/index.shtml

  • 16 years ago

    I don't understand you just said you have a seperate water heater and then in next sentance you said you have an electreic water heater. on the websight it looks like you have a seperate indirect water heater. Howe many circulating pumps do you have? Then you said you have 2 wires going to the boiler, where do they come from. I am guessing the zone valve. what make is the zone valve? just an fyi its a water heater, not a hot water heater, becuase your dont have to heat up hot water.

    I watched the video, is that what you have. you need a pump or a seperate zone for the water tank.

  • 16 years ago

    Wise, I understand its confusing. It's a conventional hot water heater (not what you see on the website) Its set up as a storage tank (primarily recieving from the boiler)and to heat up water itself if it needs to. FYI from the original post ItÂs a Invensys pop top control valve # vt2317g13a030
    There are two wires that go to the system 2000 energy manager from the invensys control valve.

  • 16 years ago

    most zone valves are spring loaded close.when you water heater calls for heat and your pump comes on, the pump creates a little more pressure against the closed heating zone valve so it let a little water go through the heating zone valve even if it is spring closed This is a common problem when only one zone is open. Later Paulbm

  • 16 years ago

    glen, I looked up the valve itself, I think you have 2 choices replace the head itself if that doesnt work your going to have to replace the whole valve. or just simply replace the whole valve, it may be stuck open. or like you said shut off the gate valve on top of that.