Manual J Air Conditioning Sizing

17 years ago

My existing 20 year old 2 zone A/C system for a two story colonial house in NJ has 2 24000 BTU compressor units. I believe the downstairs evaporator coil may be larger than the upstairs one. On a really hot 95+ day, those units didn't seem to keep up with the load. I received proposals for new A/C units, upstairs 30,000 BTU and downstairs 36,000 BTUs with matching evaporator coils and want to know if the larger capacity units are reasonably sized for my house. I want good dehumidification and don't want to pay extra for cooling that's unnecessary.

New Jersey 2 story built about 1981

2508 sq ft (1400 dn/1100 up)

All new double glazed wood windows

Attic insulation ~6", Walls ~3.5"

Fairly good sealing, new vinyl shake siding with tyvek and insulation panels

No attic ducts, most duct runs in basement with vertical leaders in exterior walls, no serious leaks.

North facing - no shade, glass ~121 sq ft

South facing - " , glass ~105 sq ft

East facing - " , glass ~22 sq ft

West facing - " , glass ~22 sq ft

Comments (4)

  • 17 years ago

    Your cooling issues may not be size related, but rather involved with inadequate/leaking ductwork and/or insufficient return air. Make sure they check this first before upsizing. If they upsize and your ductwork can't handle it, just asking for more noise and more comfort and efficiency issues. Based on square footage alone it sounds like their proposal is oversized. Did they do a formal load calculation?

  • 17 years ago

    Don't know if a 'formal' load calc was performed, but I questioned the sizing and was told those were the correct numbers for my house. As for the ductwork, every room has its own return and although upstairs and downstairs returns share a common return trunk in the basement on the way to individual plenums, the contractor said it was adequate. As I mentioned, the old 24,000 ACs couldn't quite keep up on those 95+ days, so perhaps additional BTU's are necessary.

  • 17 years ago

    Going from 4 ton to 5.5 ton on 2500 sq ft in Jersey seems excessive. Around here, and we have similar heat in the summer, we'd probably have 1 system and 3 tons, 3.5 tons max. I find it hard to believe the house has a duct system sufficient to upsize the equipment like that! Most systems are starved for airflow as it is.

    I don't see going 2 to 3 downstairs. Cool air from above falls and warm air down goes up. Maybe the 2.5 ton upstairs makes sense.

    Oversized can mean humidity control issues. I wouldn't do anything without an accurate load calc being done. Then someone should check the static pressures of the duct systems and be sure there is the capability of moving enough air. You could spend all this money and find you aren't any more comfy than before.

  • 17 years ago

    You were provided excellent advice.

    I would want more insulation in the attic, especially for the cold winters.

    Your winter design is around +10-F, while here in WI mine is -11-F both at 99%.

    The worse thing you can do is oversize the air conditioning. It will greatly lower the SEER Rating & be very inefficient. - udarrell

    Here is a link that might be useful: Sizing