4 ton vs 5 ton

12 years ago

I have a new 3580sf home with 2480sf of downstairs space located in North FL. House has a mill finish metal roof. House is heated/cooled with a heat pump system. Originally the house was fitting with a York Affinity 5ton 2 stage compressor unit for the down stairs and a 3 ton unit for the upstairs. 5ton unit was removed due to issues and was replaced with a 4ton 2 stage compressor unit. The downstairs is also a 3 zone system. Per the sf is a 4ton unit going to be efficient per energy usage and cooling? I can provide more detailed info if needed. Thank you.

Comments (7)

  • 12 years ago

    Properly sized equipment will operate more efficiently than than the same equipment in a larger sized. That is because the smaller equipment will tend to run for longer cycle times. Houses rarely have the duct work large enough to handle the air flow of a 5 ton condenser. This is another reason why moving to a 4 ton condenser is a good move.

    Was the cooling load calculated for each floor? It seems both condensers were over sized. It load calculation would confirm this.

  • 12 years ago

    I agree the upstairs is over sized and never understood why we had a 3 ton unit for 1100sf. The 4ton unit for the 2480sf down stairs is just past the max of 2400sf for zone 1 where I live. Although half of the down stairs has a cool ceiling per the upstairs above. My concern is that the unit is running noticeably longer and will that result in higher electric bill? I would think the 4ton draws less load so does it even out?

  • 12 years ago

    AC condensers are not sized by floor area. Using a general rule of thumb of 600 sq. foot per ton will result in over sized equipment.

    The AC condenser runs inefficiently if it operates in short bursts. A lot of electricity is used during the initial start up and the first several minutes as the equipment is running. The longer run times are more efficient and it will help lower the humidity. It may allow you to raise the temperature setting by a degree or two.

    The 4 ton unit will use less energy than the 5 ton. The run times will be longer but there should be a net savings in energy costs.

  • 12 years ago

    Thank you for the info. Sounds like its better to be at the max side of the window than the minimum.

  • 12 years ago

    nice post mike. I totally agree.

  • 12 years ago

    You initially had 8-Tons of cooling which is outrageous.

    Especially with a zoned system you don't want things oversized. You probably could have gotten by with a 3 or 3.5-Ton on the 2480-sf 1st floor; with a 3-Ton that's about 800-sf per/ton of cooling.

    Do your load-calcs.

    Here is a link that might be useful: Free Load-calc

  • 12 years ago

    thank you