To cycle or not to cycle

16 years ago

I finally replaced an 8.5 yr old leaky summit coil, 3.5 ton, 10 SEER unit for a new Lennox coil and an Aire-Flo 14 SEER, 3.5 ton condensor. I was literally losing 5 lbs of Freon every few days.

My question is should this new system (minus the blower/furnace portion) cycle at all on 100+ degree days? My stat is set to 78. The system stays on continuously from say 1PM to 9 or 10PM. At 10PM it starts to cycle every 13 minutes. I realize the fine line of being oversized and the ramifications, but I consulted with HVAC tech, considered the upstairs-1755 SQ FT area to be cooled and concluded to go with the same size condensor. He is scheduled to come back tomorrow and double check charge, meter readings and blower operation. If all checks out, I suppose I'm somewhat undersized, which doesn't make me happy even after spending what I thought was a reasonable $3500 on the above equipment.

Any thoughts on how else to maximize heat loss?

I do plan to add more insulation, possibly radiant barrier (foil on ceiling rafters)and solar screens on west side of home.

Thanks

Comments (2)

  • 16 years ago

    "should this new system (minus the blower/furnace portion) cycle at all on 100+ degree days?"

    Depends on how closely the estimate of required size is to the actual heat gain of the house and the design point.

    If the unit is slightly oversize compared to the actual heat gain of the house it should cycle at the design limit.

    If it is not at the design limit (say thermostat not as low as the design used) or the heat gain is less than estimated it may cycle.

    If you design for 72 inside/100 outside and the unit is otherwise sized perfectly it may not cycle if you leave the temp set above 72.

    It takes a pretty decent amount of work to size for old houses.

    Blower door tests, IR camera tests, etc. all start to get real m=numbers of heat gain (or loss).

    If a typical Manual J was done even a minor difference in the estimated R-value of the exterior walls and ceilings from what they actually are can make a large difference.

    There are a lot of square feet of exterior surface.

    Add to that the estimate of infiltration losses from windows and doors.

    Many systems end up at least slightly oversize, but as long as the humidity control is adequate that is often about as accurate as you really need to be.

  • 16 years ago

    hire an energy rater to perform the testing that
    brickeyee mentioned.
    a blower door test, duct test will show you
    house & ductwork leakage sites,

    a rater will give you more specific to your home
    info as he/she will actually see and test it.

    how much of the 1755 sq ft is upstairs?
    hotter up there in the summer and colder
    in the winter would be my guess.

    its not a bad thing in our hot humid climate
    for the unit to run continously for those hours.
    the cooling load starts early afternoon and continues
    until after the sun causing the need for cooling has set.

    as far as adding insulation..do all the sealing work prior
    to the install of addtional insulation.
    ..and install your radiant barrier first,
    so that you can work longer/cooler in the attic.
    otherwise it will be difficult to work due to added insulation.

    best of luck.