TECHs' Determining Metering Device Easy Way

18 years ago

All Techs, to avoid using Superheat charging instead of Subcooling for TXVs -Determining which metering device TXV or Fixed Orifice the system has - without physically looking.

You have to know which metering device it is, in order to use the correct charging method.

Hook up your manifold gauges, block off considerable condenser air intake for a short time.

If the suction pressure & head starts rising, you have a piston, or a cap tube.

If only the high side head goes up, you have a TXV.

Have what you need in your van or truck to block-off the condenser air-intake (NOT discharge air) for a short time.

Check every time you are not certain what metering device it has.

With many TXVs being used now, there will be far too much guessing now & in the future.

Do this procedure on known metering devices to observe the difference. Report back to me how well it works for you.

In some situations, this method could save you from cutting a hole in the plenum.

-----

Squirrel cage wheels with forward curved blades on residential systems

unload when discharge air is blocked off too much & will overload

when there is no static pressure.

There is a preferable ESP range for each Air Handler blower design, that ought to be listed on the blower; they vary at the point of serious unloading.

If you amp-probe check enough of those blower motors, if the amp draw is too low according to its rating, you can begin to tell that the External Static Pressures (ESP) is too high.

-------

I lot of us used to set a nearly empty R-22 cylinder on top of a condenser to warm it a little. Back then fan motors had more HP & higher amp draws, therefore it didn't seem to cause any harm, just more noise.

Where there were cottonwood trees, nearby clothes dryer lint vents, or a lot of leaves or other debris under the unit, the fan motors would be blocked overload & burnout.

I don't understand the engineering genius of that moronic design.

However, on hot days & a heat-loaded E-Coil, you could move your wrist over the condenser from outlet up to inlet, & tell if the liquid was taking up too much area of the coils; an overcharged system. - udarrell

Here is a link that might be useful: Superheat & Subcooling Charging Procedures

Comments (6)

  • 18 years ago

    I have seen the discharge air blocked off before to "bring the pressures up." Is there any truth to this? That's good information for techs; I saw you post this over at HVAC-Talk.

  • 18 years ago

    Oh, and when the tech blocked off the discharge air, it was to charge the system in A/C mode in the winter. I do believe this tech to be competent, but I wanted to know if what he did was the same idea as what you are proposing.

  • 18 years ago

    Tech's block off the ["intake-air"] [not discharge air] to get the pressure up to both check &/or charge a heat pump, but [in the cooling mode.]

    You can charge a Heat Pump in the cooling mode. You need an adequate heatload in the conditioned space, if it's less than 65 degrees outside use a trash bag or something to block off the coil to the temperature& pressure up.

    Never block the discharge air of a propeller fan as it could overload the motor. - udarrell

  • 18 years ago

    That's a nice tip Udarrel...I'll put it to the test, but...................I think after looking at gauges, that the indoor coil should always be inspected before any refrigeration adjustments are made to an unknown system. Even if you have to cut a hole.

  • 18 years ago

    And your point, Udarrel ? We were taught that in school.

  • 18 years ago

    Kalining from Canada, my point is that I have discovered that a lot of so-called Pro-Tech's are not aware of this helpful technique.

    They are used to fixed piston orifice metering devices, & many appear to be using the superheat method or NO proper charging method, some don't even follow the mfg'ers procedures which in many cases provide NO positive indication as to which metering device the system has.

    The tech needs to know that the airflow through the coil is within specs & then techs need to know which metering device the system has in order to use the correct charging procedure.

    As for service techs checking or cutting a hole in a plenum to check, forget it, ask the users how many checked to see what metering device was on the coil, or verified that in any way. When servicing, many are in a hurry to get to the next service call.

    I would love to see a survey taken on the issue of how many verified which metering device the system had.

    Because we would "do it right" has zip to do with whatr others are doing. I have witnessed them only checking the suction pressure & nothing else, & saying the system's charge is okay, when I knew it was way off as was the CFM airflow through the E-Coil.

    We had a mix of TXVs & cap tube systems in the mid 1970's, & needed to know what we were dealing with. - udarrell

    Here is a link that might be useful: Superheat & Subcooling Procedures for Optimal Charging