possible problem with in-floor heat; circulating pump hot

19 years ago

We have in-floor heat in our basement using an AO Smith Powershot water heater and Grundfos cirulating pumps for two zones of heat (used for the first time last winter). It has just recently gotten cold enough for the heat to kick in here in SE Minnesota. The system was not off over the summer, but most likely never needed to run. In checking on it yesterday, the water lines from the water heater feel cool, but the pumps themselves are very hot and the copper pipes just downstream of the pumps are quite warm, also. The red water tubes going into the floor don't feel particularly warm. I don't remember the pipes downstream from the pumps feeling warm without the supply lines from the water heater being warm last year. Does this sound like the pumps are trying to run since there is now a call for heat, but the water isn't actually circulating? We have turned it off for now in case the pumps were overheating. We will call the company that installed the system, but have lost some confidence in them for a number of reasons. We would appreciate any input some of you may have.

Comments (6)

  • 19 years ago

    Are you saying the boiler isn't hot, but the pumps are? Can you hear them running?

  • 19 years ago

    The outflow pipe from the water heater is warm just above the heater, so it is heating, but the rest of the pipe (6-10 ft) to the cirulating pump is cool to the touch. The pumps themselves were almost too hot to touch, and the pipe just beyond them was also very warm. I could feel some vibration so it appeared the pumps were running. We have now turned the system off and everything is cool (except right at the water heater). Could there be a vapor lock or something like that where the pumps are working hard and heating up but the water isn't circulating?

  • 19 years ago

    You are right. The pumps are air locked. they are also water cooled and the seals are lubed. with water. So don't run them until the system is bleed. may be too late already
    but you could be lucky. Those pumps will take some abuse but not a lot.
    Good Luck.

  • 19 years ago

    Thanks for your reply - that helps. We have a call in to the installer.

  • 19 years ago

    I called the installer and he was surprised that anything should be wrong - said it should run without any major maintenance. They will come out next week. I was going to attach a picture of the setup up to see if there is anything that seems unusual that would allow an air lock to develop but am not sure how to do this. Any advice? There is an Amtrol Extrol tank and a Spirovent attached to the water line near the heater.

  • 19 years ago

    The air pocket is likely at the highest point in the house. Sometimes there are screwdriver vents at the end of the baseboard to release trapped air. You may have one. Loosen the screw until the water drips out.