Geothermal Quote

15 years ago

First, thanks to everyone who responded to my earlier post about heat pump quotes. Very helpful advice. We decided, in the end, to pursue geothermal since the prices were close enough to an air source heat pump to make it viable.

We had a reputable local contractor come out and do the heat load calc on the house and bring in a well driller to look at our site. We now have a quote for $13,757.57 for the system plus $6,800 for the wells, so $20,557.57 total. That is after $1,200 of rebates, but before the 30% govt incentive, so it will cost us around $14,390 in the end which is about 50% over the air-source heat pump quotes we've had. Seems very reasonable from everything I've read.

The quote, which is for a ClimateMaster Tranquility 27, 4 ton, lists the following items:

DESUPERHEATER CONTAINS 1 52 GALLON WATER HEATER

1 1/4in FUSION x O-RING

SINGLE GRUNDFOS 26-99 PUMP WITH COMPOSITE VALVES 708634

INTERNAL AUXILARY / EMERGENCY HEATER

7 DAY PROGRAMMABLE ACO 3H 2C WITH FAULT DIAGNOSTICS

TRANQUILITY 27 - 2 STAGE SCROLL COMPRESSOR - ECM2 - W/ HWG

10 YEAR LABOR WARRANTY

OUTDOOR UNIT W/O COIL LEVEL 2 W/AH OR FURNACE

How does this look? Anything else I should ask the contractor?

Thanks.

Comments (5)

  • 15 years ago

    I would do it. Sounds like a wise investment (expecially with the 30% off).

  • 15 years ago

    Sounds good to me too and I would also take this system. I would like to see the specifics of the ground loop installation though, as well as a couple of other things.

    I�ll take some �educated� guesses on the data already provided, you can fill us in. I would say this is going to be a no larger than 3-ton system with a single deep borehole of no deeper than 450-feet.

    I would like to know how many feet per ton they intend to drill, how the borehole(s) will be grouted and with what. How far from the envelope the closest (only), borehole will be, is the 52-gal tank a buffer (passive) tank, is the Aux backup (probably 15kW) staged (5,10,15kW), what percentage of the heating capacity has the system be designed for, what�s the outdoor design temperature, is the �Single Grundfos� circulating pump part of an integrated, insulated �Flow Center� with associated 3-way valves?

    I would also INSIST on a flow meter (see link below) & EWT & LWT temperature meters (digital/solar powered). No mention of parts warranty�

    I�m not sure what "OUTDOOR UNIT W/O COIL LEVEL 2 W/AH OR FURNACE" is.

    I would also ask what this price does NOT include, what part of the warranty is from ClimateMaster and what part is from the installer, is the warranty transferable, what detailed info will be provided in writing regarding the design and installation of this system & its startup? This last item is important to have so that any competent technician can come onsite and understand what�s going on and have a �baseline� to compare to just like when you visit a doctor and have an electro-cardiogram done while you�re still well and healthy.

    I�ll stop now�

    SR

    Here is a link that might be useful: Flow Meter (see-thru)

  • 15 years ago

    Thanks for the questions, fsq4cw. Here are the answers I received from the contractor:

    This is a 4 ton unit, by the way.

    -The well drillers and I estimate there will be 2-3 wells at a total of roughly 600 ft (150 ft /ton). We will use bentonite to grout the wells and to ensure soil conductivity.

    -Yes the 52 gal tank is a buffer and will be used to store the hot water produced by the heat exchange in the Geo system. Your current hot water tank will draw from the buffer tank to save on energy consumption.

    -The auxiliary heater is 15KW. That size is recommended from 3.5 to 5 ton. The Geo system is staged.

    -The system has been designed for 100% of the heating capacity

    - The outdoor design temp is 11 deg in the winter and 95 deg in the summer.

    -Yes, the Single Grundfos are integrated, insulated and have 3-way valves

    -There is a flow valve that is wired into the electrical component of the Geo. The thermostat will notify you if there is a problem with the flow.

    -We do not typically install EWT and LWT meters. What was your thought with these?

    -The OUTDOOR UNIT W/O COIL LEVEL 2 W/AH FURNACE HMP200 is simply labor. It should take 2 days to finish the project.
    -The warranty is 10 yrs parts, 10 yrs labor. (Climatemaster takes care of the parts and we provide the labor) The warranty is fully transferable.

  • 15 years ago

    It is Best Practice to have a 2-pump flow centre with capacities larger than 3-ton.

    Will the wells be connected in series or parallel with reverse return headers?

    Will the (Thermally Enhanced) Bentonite grout be installed with a tremie line?

    Buffer tank is OK.

    Good that the geo is staged since it is designed for 100% heating capacity but is the 15kW backup also staged (5,10,15kW)?

    Good that it is an integrated insulated flow centre w/3-way valves.

    I personally prefer a see thru flow meter in that it is fool proof and you can also see air bubbles should they develop.

    "We do not typically install EWT and LWT meters. What was your thought with these?"
    That is typical but OK. I prefer meters to measure the Delta-T between EWT & LWT. Should there ever be a drop in Delta-T between supply & return plenums, EWT & LWT along with flow rate are the first places you want to look.

    Good luck. Keep us posted.

    SR

  • 15 years ago

    Geothermal in this instance means ground source heat pump not geothermal heat which is even more efficient but only possible in certain areas. It is almost never done in residential construction and makes more sense to generate electricity.