Major joist reinforcement

20 years ago

Most of the questions here do not deal with major structural issues. The old house in question was built in 1921 from used lumber. The floor joists were too small for the span AND spaced too far apart. Due to the foundation, sistering with deeper joists is not an option. And the depth of the present joist, about 7", is too small for the span, even at 12" spacing. I have found Deitrich steel joists in 7 1/4" depth , their TDJ code, that will work with the span if spaced properly. Anyone ever used or seen this type joist placed in an existing structure? How else to solve the problem? Without a long explanation as to how and why, I will just say that the existing joists are not sagged, but are very springy/bouncy.

Here is a link that might be useful: Steel joists

Comments (5)

  • 20 years ago

    Joists do not need to have a uniform depth across a span to carry a load.
    If you need depth at the foundation you can cut back the bottom edge to the depth needed to rest on the seat while leaving the rest of the span full depth.
    Steel joists have signficant buckling issues unless carefully installed and braced.
    Another alternative is to strap the bottom edge of the joists with steel (flat, 1/8 or 1/4 by 1.5 wide for about 90% of the length) or if you want additional stiffness angle iron. It does tale a lot of fasteners (6-8 inch spacing) but things can really be stiffened up.
    If you want to apply a new ceiling to the strapped joists 2x4 ripped and attached to the side of the joist sticking down just past the steel provide a surface for fastening drywall.

  • 20 years ago

    What is under the joists? Crawl space, living space?
    It might be easier to put a support beam across the joists held up with lolly columns.

    If you have moisture issues, the steel could cause condensation. Just a thought.

    You could also build flitch plates, which would be steel vertical to the joists, usually with a matching joist the other side. That may be overkill for you though.

  • 20 years ago

    Flitching in an exsiting structure is a real PITA.
    To get anything apporaching full strength a flitch beam (steel between 2 pieces of wood) requires through fastening to prevent the steel from buckling under load. It will just force the wood memebers apart as it buckles.
    Drilling through 3 inches of wood plus 1/8 or 1/4 inch of steel plate that is already on 16 inch centers is the problem.
    The steel plate typically used is also very hard and typically requires something more than a run of the mill HSS twist bit.

  • 20 years ago

    I do appreciate the suggestions. The house was built over a crawl space. Balloon framed with 6"wide and 8" high solid oak perimeter sills. The original joists were butted into the sill and notched over a ledger strip. The sills were originally on fieldstone piers. Some balloon framing has the joists set on top of the sill, but not in this case. Looks like the flooring was done before the studs were placed and extends to the outer edge of the sill. I see that as an advantage in that the flooring holds against lateral separation of the joist from the sills. Flooring was T&G pine with face width of 6" and true 1" thickness. The existing joists are placed 2' O.C. and the joists vary in width with some as much as 2 1/2" wide. Originally, the center of the joists span was supported with more stone piers, so the actual span was only 8' between supports. In the late 1950's, an ill advised attempt was made to excavate a partial basement under the house and posts were placed under the center of the joist span. Now for sentimental reasons as much as anything else, this mess needs correction. I am not an engineer, but the idea I had was to sister each side of the existing joist with the Deitrich C-shape joist. This would place the new joists about 2' O.C., but there would be as many of them as if they were only 1' O.C., in fact there would be one joist more if my count is correct. The ends would have a shop-made (me) joist hanger at each end around the whole "sandwich" and lag bolted to the perimeter sill. I had thought about the condensation issue and would use several 1/4" plywood spacers on each side of the wood joist to hold the steel 1/4" away. The steel joist would be fastened to the wood joist with perhaps two #12 screws every 2' of length to provide side stability. The steel joists would be selected from span tables as if they were the sole support for the floor system. These would be installed from underneath and existing flooring would not be disturbed. Each hanger would be custom sized due to the varying width of the existing joists. This is new territory for me. I have tried to be creative and of all the schemes I have devised this seems to be the best of the bunch. I have visited two sites where these steel joists were being used to build residences. I have worked out the details of holding the steel joists up in place while the hanger is being fabricated. Some of the hanger fabrication could be done in advance. I believe 1/8" thick steel should be enough for the hangers based on the joist hangers that are normally sold. My (uneducated) calculations lead me to believe that four 3/8" diameter (with proper pilot holes) lag bolts 5" long into the sill should be more adequate for each hanger. A hanger at each end of the "sandwich". Nails are not practical for the hard oak. Comments and suggestions from those more educated?

  • 20 years ago

    Bus,
    Try and find an engineer experienced in wood structure design. It is a limited area but if you can find someone they will understand how wood behaves under load. It is very different than steel, and the combination is not at all obvious.
    If you look at the steel deign guidelines I think you will find a bunch of the details you cannot accomplish in a wood-steel retrofit. This makes the standard steel tables not applicable to the problem.
    Half flitching with a correct fastener schedule can work, but the compressive strength of the wood determines things like the exact size of washers to spread load. There are quick answers (often based on modern wood) and field methods to approximate the actual wood characteristics that give a better answer (and the cost difference can be substantial).

    Old wood can be amazing stuff. The tight grain structure can increase load factors by 2 to 10 times what modern softwood can do.

    Replacing any missing supports is often a very effective way (both money and time) to restore old structures. Jacking before replacing is often beneficial.