AC condensation drain routing

19 years ago

My daughters condo in Eastern NC..The condensation drain for the AC is routed through the wall and into the bathroom sink drain pipe between the stopper and the P trap. I am not concerned about sewer gas as this connection is above the trap, but I wonder about the codes concerning where you are allowed to drain AC condensate. Is this allowed to be dumped into public waste systems? Private septic? Does it vary locally? What about it Pros?

Comments (6)

  • 19 years ago

    Condensate for central A/C is normally routed to a floor drain which is connected to whatever waste system that house has, so, I'd say 'Why not for a window shaker, too'.
    This sounds like a clever method.

  • 19 years ago

    The volume of condensate is so small as to be of no consequence if added to sanitary sewer lines. I know of no prohibition to doing so. Keeps from having a wet spot on the property. The described installation might be more difficult to unclog if algae growth clogged it. But I would not change it unless it causes real problems.

  • 19 years ago

    Close but no cigar....

    The olumbing code does permit discharging an AC condensate line into the sanitary sewer but it MAY NOT be connected directly to the DWV piping. It MUST BE connected by means of an indirect waste receptor.

    The line may drip into a sink or it may terminate into a floor drain but the lowest point of the condensate drain line must remain 2" above the highest flood level rim of the waste receptor.

    The concern is that if the condensate line is connected directly to the DWV system bacteria in the DWV system will get into the condensate line and could ultimately get back to the condensate tray and the evaporator coil. Once its there the normal airflow through the evaporator would cause the bacteria to become airborne through the structure.

  • 19 years ago

    I am assuming the term DWV means er...DA WASTE VENT?

  • 19 years ago

    DWV is a term used in the plumbing industry to indicate all Drain, Waste & Vent piping.

  • 16 years ago

    My situation is similar, in that it comes out of the A/C unit, then down about 6-8" into the "return air" space, across into a side wall, THEN UP about 6" and across to (I think) a bathroom sink plumbing. It's the UP about 6" that I'm concerned about. I didn't know water could travel directly up!?!