jason_young8719

Supply/Branch diameter question

19 years ago

Hi. I currently have plenty of hot water (heat and pressure are fine) at each location and a pretty short wait for it to arrive. However, it's challenging to find "warm". (No thermostatic valves.) On the shower, I can open hot 100% and then open cold about 3-5% before it reaches warm. If I open them equally, it's essentially cold.

Details:

I have a 3/4" copper main that's instantly stepped down to 1/2" after the shutoff valve behind the meter. After a 30' run, it steps back up to 3/4" (flex) into the water heater. (Along that 30' run, there are a few 1/2" cold branches to the only bath, the kitchen, washer and outdoor spigot.) The 3/4" (flex) out of the water heater steps immediately back down to 1/2" and then supplies all the fixtures with hot water.

My first thought is to replace that 30' run of 1/2" copper to the water heater with 3/4" copper. I plan to keep the cold branches at 1/2". I have heard that the 1/2" copper from the water heater is probably ok because if you go bigger it will take much longer to get hot water to the outlet. Fine.

I would like to know (a) if there are problems with this approach and (b) if it will solve the "finding warm" problem.

Thanks...

Comments (6)

  • 19 years ago

    Changing that 30' section of line from 1/2" to 3/4" would reduce the velocity of flow through that section, which in turn would reduce friction head loss and result in a slight increase in the working pressure throughout the house, but you stated you have adequate pressure so there would be no advantage to changing it.

    Changing that line would have absolutely no influence on the temperature of your shower. The problem your confronted with is a code issue. The plumbing code limits the temperature of the hot water to a maximum of 125degF unless all showers and tubs are fitted with anti-scald valves, in which case the hot water may be a maximum of 140degF.

    For most people a hot shower is typically in a range of 95 to 105degf. With the supply water coming in at 125degF it only takes a slight amount of cold water to temper it down to the "Hot shower" range, therefore there is no problem with your system.

  • 19 years ago

    Clearly I have not explained myself adequately. Every faucet in my experience operates with the same basic principle. Turn on hot plus cold to get "warm". In a perfect world, half a turn of the hot and half a turn of the cold should result in warm. If the faucets were "calibrated" in this fashion, the user would have the maximum ability to adjust the temperature and pressure accordingly. Full_hot+full_cold equals blasting_warm; 5%_hot+5%_cold equals a trickle of warm; etc. Everyone following me here?

    In my case, on any faucet in the house, it takes about 100% hot and about 5% cold to hit warm. Under these conditions, you lose all ability to fine tune the adjustments. A hair over or under 5% cold results in cold... (It's like driving a car that can only make hard 90-degree turns.) This is unacceptable.

    I tried cranking up the temp on my hot water heater, which resulting in much hotter water coming from the hot tap. But the same minuscule addition of cold to the mix results in cold from the tap. I can't pinpoint the reason, but it seems as though the cold is "overwhelming" the hot water further up the pipe. In other words, the second I open the cold tap, it seems that the hot water perhaps loses pressure and disappears from the pipe.

    I have not validated this claim, but that's how it appears to me. Why else would the introduction of so little cold water to the mix result in a temperature drop that's so abrupt? I have not lived in the house long enough to notice what happens if the washer is running or a toilet is flushed, but am open to suggestions on how to further diagnose the issue...

  • 19 years ago

    your cold branches off before the hot. so when you open the cold tap that much water is diverted from flowing thru the hot tap. this lowers the flow of the hot water.

    as far as equal flow from each, what temp do you consider to be warm? if the cold water is 70, and the hot water is 125, then equal parts should make the water 97.5. that is a full degree cooler than normal body temps, and will feel only lukewarm to you, if not outright cold.

    in my house i get the same thing as you. i have not measured my temps, but i can tell you that if i turn cold on more than 1/4 turn i get what feels almost pure cold. but if i turn the hot off, i can feel it get colder. in my case the cold line enters my house at the northwest corner, right in my master bath. the water heater is in the southwest corner of my house, over 150 feet away by pipe. since my shower is the first thing to come off the water line, turning on cold there causes flow elsewhere inteh hosue to drop and therefore the hot flowing back has less flow. add in heat loss in the pipes, and i get a cold shower real quick.

    Lazypup can explain all the above in much better terms than i.

    why no install an anti-scald shower faucet and set it to the desired temp. then all you have to do is turn it on.

  • 19 years ago

    You said: "your cold branches off before the hot. so when you open the cold tap that much water is diverted from flowing thru the hot tap. this lowers the flow of the hot water."

    This is precisely what I envision to be my problem. I have the same condition as you, but mine is far more extreme. You can turn the tap 1/4 turn. Well, I can turn my cold tap about 1/30th of a turn before it's too cold for a shower, even with hot turn on 100%. Do you see what I mean? I don't know how to better describe it.

    It's not so much about my perception of what's hot and what's cold, nor is it about the precise temperature of the output. It's the fact that I have zero ability to fine tune the output... I am admittedly a plumbing-neophyte, but I've been using faucets for 35 years and this seems abnormal. :)

    That said, I don't see how this could be a faucet issue. Maybe I'm wrong. If thermostatic faucets do such a superior job of mixing and give me the granular control that I desire, then I'll give it a shot. But my gut says that extending the 3/4" copper run directly to my hot water heater will address this issue. All the pipes are exposed in the basement and very easily replaced. Any other input is much appreciated...

  • 19 years ago

    Anyone?

  • 19 years ago

    From personal obversation and living in old houses with mixed plumbing, (3/4" copper to 1/2" CPVC tp 1/2" galvanized ro 3/4" copper, no 3/8" lines in this house) change it out to 3/4" to the water heater. You will notice that the water heater is manufactured for 3/4" lines.

    This may not solve your problem but I think it will help.