shower and tub drain, ubc code

18 years ago

I am instaling the underground drain system for a bath room. The tub and shower are both next to each other with a wall between them. I would like to run both of them on the same drain. They each have a fixture unit of 2 each and I think it is within the code to drain them both in a two inch drain. Can I use one of the 4 way double tee's right under the wall to vent and then take each horizontal to the tub and shower.

If that does not work, can I use a 3 inch double sanitary tee with the side fitting 2 inch and with a reducer in the top fitting to take it into 2 inch for the vent. I could then take the 3 inch into the 4 inch main.

Does anyone know the best way to plum two thower/tub when they are next to each other. Thanks

Comment (1)

  • 18 years ago
    last modified: 11 years ago

    While on first inspection this might seem simple enough in reality there are a number of very complex code issues that must be considered.

    If the double Tee is configured in a vertical position with the tub and shower connected to the side openings and a vent, continuing vertical from the center opening that would be correct, however we must then consider how the discharge end of the Tee would be connected to a horizontal drain line under the floor. If you are then planning to install a 1/4bend to transition from vertical to horizontal and connect to the end of a horizontal line you would be required to install a cleanout on the vertical riser above the double tee. (All horizontal drain lines MUST have a cleanout on the upstream end.) If the double tee is then teeing into an existing horizontal drain line below it you would be required to install a Wye & 1/8 bend or a Combo on the horizontal line to receive the discharge from the double Tee. (Tees are prohibited on horizontal lines)

    If you were planning to put the double Tee on the upstream end of the horizontal drain line you have a number of problems.

    Code prohibits a tee on a horizontal drain line therefore you would be required to install a double Wye with a 1/8bend on each side opening to complete the 90degree turn.

    Code prohibits any horizontal venting until the vent reaches an elevation of 6" above the horizontal rim of the highest fixture served by that vent, therefore you could not connect a vent to the center opening on the input side of the double Wye. You could install a second Wye & 1/8 bend on the downstream end of the double Wye the run a vent line vertical from the second Wye & 1/8th bend however in this configuration the double Wye would be on the upstream end of the horizontal drain and would this would then require that you install a cleanout on the center opening of the double Wye. If the junction is fairly close to an outside wall the center opening could be extended to the footer wall of the structure and the cleanout cap put on the end of the line after it passes through the footer wall so the cleanout is accessible from outdoors or you would be required to stub a cleanout up through the floor.

    There is another option. You could connect the shower and tub by means of the double Wye and 1/8th bend then run a line from the center opening of the double Wye to a riser for the lavatory. You would then Tee off the vertical riser for the lavatory fixture arm and continue the riser vertical to make the vent. In this configuration the portion of the riser below the lavatory fixture arm and the horizontal run from the base of the lavatory riser to the double Wye center opening would be classified as a "Combined Waste & Vent" and you would not be required to connect a vent on the downstream end of the double Wye because all three fixtures would be vented by the lavatory vent riser. In addition, since the lavatory would have a trap adapter on the end of the fixture arm the trap could be removed granting access to snake the line therefore it would meet code for the required cleanout.

    If you will use your graphics program and make a diagram of your layout then email it to me I will work out solution for you.