I use my solar panels to keep my lap pool in the mid 70's during the summer months. Solar gain in Northern California is such that the water temperature easily climbs into the 80's. I run the filter pump at night and manually open the valve to the solar panels when air temp falls into the 60's and switch it back in the morning. I can lower pool temp by 2 to 3 degrees a night this way. We often have nighttime temps in the low 50's.

I have an EasyTouch panel that controls the pool and spa schedules. Is there any way I could set the solar panel cooling time automatically? I don't have the wireless remote or the indoor control panel but would get one if this would help solve my problem.

Thanks in advance.

Waterouzel

Comments (7)

  • 18 years ago

    I just setup the lower end system, solar touch. You should be able to set up the system to run w/o solar for a set number of hours and then setup the solar to heat the pool when the temp hits your low threshhold and turn off when it hits your high threshold. Simple stuff. -cjd

  • 18 years ago

    As I read the question, it does not look like you need o run at night for the heck of it, you are looking to get some radiational cooling?

    Normally I'd say you can set a program to run at night and have it activate the solar valve. I've never tried it so I can't say it will work with an active solar program already. I'm guessing you can't assign the solar valve to more than one program. I'd have to actually go out and try it.

    But, you can do that too. Make a program for a few nighttime hours and try to assign SOLAR to it. I'm guessing it won't activate as you won't satisfy the differential. But, they may have an ability to put a negative differential in which might work for cooling.

    Good question.

  • 18 years ago

    repair_guy,

    You were right. I set up a program and assigned the 'aux extra' which is my solar relay but it wouldn't activate the valve or the filter pump. I'm guessing it's because solar is enabled (I need it for the spa) and the temp differential doesn't permit it to work. I don't see any obvious way to put in a negative differential.

    My next thought is to plumb in another 3 way valve to bypass the present solar valve and control it using an actuator wired to 'valve B relay ' in the EasyTouch. 'Valve B relay' is not being used but would it work in that situation?

    Thanks for your help.

  • 17 years ago

    We just had our pool retiled/plastered and new coping put it. When the pool was filled, I went to run the pump and our (ancient) Compool LX-10 panel flipped it's breaker. this is not the main breaker on the electrical box, but a little breaker switch at the top of the LX-10 panel. Long story short, we hired a guy to check it out, and he took every low voltage wire off and it still tripped the breaker. The verdict is that the board is shot. They don't make this board anymore.

    As an immediate workaround, we had the pool and cleaner hardwired to the electrical breakers.

    So it looks like we need a new control system. We have a "Spa" that is unheated, but does have working jets, bubbler and light. Our pool is about 26,000 gallons. We have a Polaris cleaner.

    It looks like our choices here are to put in a mechanical time clock (to run the pool filter and cleaner and maybe the lights) or to put in a replacement automated control system.

    The timer is a lot less money, but that won't deal with the automated valve switching that diverts water to and from the spa. One person said we really don't have to run the spa filter everyday, we could just manually turn the valves once a week or so.

    It looks like the replacement automated control systems run around 2-4K! Not good news after just spending all the money on the remodel. There is an upgrade kit for the LX-10, which is around $900+ installation - so that's the 2K option. On the high end is the intellitouch at about $3500+ some electrical and plumbing changes at another $2-300.

    We'd love to hear any suggestions or opinions you have. When I hear a timer price of up to $1100, I think maybe a bare bones programmable system would be better. Or not? Will we end up with algae in the spa in the summer if we only filter it 1x a week?

    Thanks for any input. We're in Northern California - Walnut Creek, so hot summers.
    Meg

  • 17 years ago

    The upgrade should take 3 maybe 4 hours max (thats being generous), so if you can get one for $900 the installation shouldn't be too much more than $3-400

    If you have an LX-10 with a plastic box, this would be the way to go..

  • 17 years ago

    mverga....

    e-mail me. I have a guy who will sell you a ComPool CP100 for $500.00. He'll even pay the shipping for you to unload it. It is the basic system with an indoor wired control panel and mechanical clock in the sub panel. Check it out to see if it will work for you and let me know. The package has both actuators and water sensor as well. New in the box.

  • 17 years ago

    Not a bad deal w/ both the actuators, but the cp100 doenst control solar IIRC, and it actually doesnt even control temperature just displays it.