Intelliflo VF features 3-9

16 years ago

Right now I'm using Feature 1, 2 and 3 1 being spa spillover which moves a lot of water. I use feature 3 for solar which who knows when the controller says ok to use. Could I also use feature 4 for spa spillover, so this is included in the total flow during the day? I states features 3-9 can't overlap, so I'm confused.

Merry Christmas everyone.

Comments (18)

  • 16 years ago

    I think you might be confusing the VF's timers with the Intellitouch's which overrides it. Set the speeds/flow-rates in the Intellitouch only.

    Scott

  • 16 years ago

    Scott, I use the intellitouch for all setup yes. The features display page in intellitouch isn't this the same as features setup in the intelliflo? I see 10 features so I assumed 1,2 then 3 to 9 plus MO?

    If I set the deck jets to feature 3, spa spillover to feature 4, and solar to feature 5 could this work? I know features 3 and 4 will not overlap, but "Solar" is the wild card! Does this priority the features? I can't figure out the design of the intelliflo pump and these features when they state "Can't Overlap" what can someone do with these features?

    Side note setup like above, some strange things happened spa spillover went off, solar kicked in and the spa spillover led is lite but not working. Does the latest feature trip win this who working game?

  • 16 years ago

    AFAIK, and I may be wrong, the Intellitouch looks at the VF as a 9 speed pump where speed may be set by speed or flow and desired number of turnovers in a given time period.

    The VF's features are separate from the Intellitouch. Intellitouch controls everything.

    If the VF was running in a stand alone mode, if speed one was set to 30 GPM and volume was set to 20,000 gallons and left alone, the pump would run for just over 11 hours.

    If a second timer is set, the 1st timer would have to expire before the second timer starts.

    If the second timer is set to 65 GPM (speed #2) for two hours for improved skimming, the added volume of water moved would be added to what was moved already.

    Timer two expires and timer 3 is set to the same flow speed as speed one but requires it be set in speed 3's slot. The remaining time needed to fulfill the turnovers per day setting will shut the pump off if the set amount of time is longer than required.

    I don't think that the Intellitouch has this limitation. but I am not 100% certain. It can be set to behave this way, but I don't think it's required. I think it can reuse speed one after speed two.

    If I had a test station, I could work out a good program for you. I don't but Pentair does. You might want to spend some time on the phone with them.

    Scott

    Soapbox Moment: To those considering going the Owner Builder route vs. the PB route, this is exactly the type of situation why the PB route would work best for you. The builder's techs would be on site and work out ahead of time the needs, desires, and configuration with the customer. When I was in the data communications field, I went with the salesmen to make sure that what the customer wanted to do a possible, made sense, and to propose potential alternatives. Expectations Set, Expectations Met. No Surprises!
    End Soapbox Moment.

  • 16 years ago

    Ok my other setup didn't work, it was like this.

    Read like this

    Main pump / Value control
    Aux 1 / Aux 2
    Aux 3 / Aux 4

    Features screen (my thinking anyway)

    1 / 6
    2 / 7
    3 / 8
    4 / 9
    5 / M.O.


    Display Main

    Pool / Spa
    blower / pool lights
    landscape / not used

    Display Feature

    not used / not used
    not used / not used
    deck jets / not used
    spa spillover / not used
    solar / not used

    The above had some strange issues the spa spillover was active, but solar kick in and turn it off. The total filter time didn't reduce time, but it should have since solar was on for 4 hours / spa spillover is active for 1 hour.

    Changed to this, still testing / learning also.

    Display Main

    Pool / Spa
    blower / pool lights
    landscape / desk jets

    Display Feature

    spa spillover / not used
    not used / not used
    solar / not used
    not used / not used
    not used / not used

    Since spa spillover working on feature #1 and it will not reduce the filter time, but feature 3 does. My flow is 18gpm for filter, everything else is 40gpm, solar, desk jets, spa spillover. Since spa spillover is 40gpm for 2 times 30mins then it's 2400gph I minus the 2400 from 13000=10600. I readjust the filter data so I told it was a 11000 pool. My filter time is 10am to 8pm, so if no solar it should work till 8pm. With solar it should be off earlier, it has work this before when I set the feature 3 for the solar.

    Steve

    I either know some stuff just to get me in trouble, or...

  • 16 years ago

    For everyone's benefit, let take some time to make some inventories. The 1st is the existing equipment list. 2nd is the plumbing connections and 3rd is a list of desired functions.

    Lets label the valves as V1, V2, etc...
    Suction lines as DS and SS for deep and shallow skimmer, MD or MD1 for bottom drain set(s). If a second set exists, MD2.
    Pool Returns and their locations.

    Once we have all of this in one spot, we can logically figure out what needs to happen and or what questions need to be answered so we can move forward easily. You have a number of postings and bouncing around trying to figure out what is where is not reasonably simple.

    Scott

  • 16 years ago

    Ok I try this...

    Orginal pool pump was Wisperflo 1.5hp uprated.

    i5 Intellitouch system

    Pump intake closer to the pump is 1.

    All values are Jandy Neverlube 3 way.

    i1 Spa drain

    i2 Pool cleaner

    i3 skimmer / pool main drains

    outputs

    o1 solar 7 panels 4x10'

    o2 spa main returns

    o3 deskjets

    o4 spa second floor return / spillover

    Value activators are on i1, o1, o2, o3.

    Filter is a 100 gpm cartridge filter.

    Aquarite 40k salt system.

    Air blower for the spa.

    Pentair Minimax NT propane heater 300k

    125g propane tank in the ground.

    Solar on the roof 1 story house with a high pitch roof.

    Spa return is done with the return value to the main returns. The spa second floor return is shut off. Pool cleaner is set for the correct flow when the pump is 40gpm. Pool main drain is off. Deskjets work for 3mins twice a day, with 40gpm. Solar works with 40gpm, spa spillover works with 40gpm. Since everything is either 18gpm or 40gpm the pool cleaner and skimmer should on everyday for a least 1 hour, but I would think at least the solar would on a hour also so 2 hours.

    13000 gallon pool, with 300? gallon spa. Need to filter the spa a little everyday, this is handled by spa spillover. Wish to pool to do a 1 flip for each day.

    Timers pool filter 10am to 8pm
    Deskjets 12pm and 3pm 3mins on
    Spa spillover 11:30am to 12:00pm and 5:30pm to 6:00pm

    Relays

    1. Pump not used or wired now.
    2. Blower
    3. Pool lights
    4. Landscape
    5. Not use / can't use. Used for activator #4 Deskjets.

    Activators

    Intake
    Return
    Solar A
    Deskjets B

    I hope that clears it up a little anyway.

  • 16 years ago

    So current equipment is :

    I5+3 Intellitouch
    Intelliflow VF
    Blower
    Lighting (assuming plain white and single button turn all pool lights on and common relay in use)
    Solar
    Propane heater
    Suction side pool sweep
    4 valve actuators
    Salt Cell

    Plumbing

    Intake: Spa Drain, pool drain, pool skimmers, pool sweep
    Returns: Deck Jets, Spa Jets Main level, spa jets 2nd level but shut off, pool returns.

    Several questions:

    1) Is the blower tied to the second set of jets in the spa?
    2) Is the I5 controlling the salt cell in any way?
    3) Do you still have the Whisperflow? Does it work?
    4) Is the spa raised?
    5) Is there a spa side controller? Which?

    Scott

  • 16 years ago

    Scott,

    Your Questions.


    Several questions:

    "1) Is the blower tied to the second set of jets in the spa?"

    No Spa mode is not joined with the blower, blower can be controlled by a spa controller switch.

    "2) Is the I5 controlling the salt cell in any way?"

    Yes tied to the serial port.

    "3) Do you still have the Whisperflow? Does it work?"

    Trashed the whole pump, it started to smoke one day.

    "4) Is the spa raised?"

    Yes 12"+ or so.


    "5) Is there a spa side controller? Which?"

    Yes, Intellitouch S4 (not working removed wires on the controller, I need to replace it.)

    Steve

  • 16 years ago

    You misunderstood the question:
    "1) Is the blower tied to the second set of jets in the spa?"

    No Spa mode is not joined with the blower, blower can be controlled by a spa controller switch.

    I meant is it plumbed to both the upper and/or lower jets so that when it's on, air comes out. If so, which set of jets?

    Additional questions:

    Spas that have multiple levels of jets usually have one pump and one blower per level. You have only one of each. As I read you statements, it seems that you have been plumbed so the return water path to the spa can go to the upper or lower jets and that the lower jets have been plumbed to the pool returns. Is this correct? Is it also correct that the blower only sends air to upper jets?

    Scott

  • 16 years ago

    Spas that have multiple levels of jets usually have one pump and one blower per level. You have only one of each.
    Quote

    "As I read you statements, it seems that you have been plumbed so the return water path to the spa can go to the upper or lower jets and that the lower jets have been plumbed to the pool returns. Is this correct? Is it also correct that the blower only sends air to upper jets?"

    True, the pb built pool for spa spillover with the lower jet is plumbed with the pool returns. This way the spa spillover works when the pool pump was on. But with a VF pump which is lowered to flow easy, I couldn't balance this value on 15gpm vs. 60gpm / 1 to 4 ratio. That was my other issue to keep the glass blocks clean, with my hard water problem. The blower is on the upper jets returns to the spa. I'm using the upper returns for the spa spillover with the intellitouch, the lower jet is off for the dipping trouble.

  • 16 years ago

    So the lower jets are actually only one pool return in the spa.

    Got a picture of the pool and spa? Especially the spa, facing the spill.

    Scott

  • 16 years ago

    The only pictures I have right now are these. Scott, Not sure why all the questions about this, doesn't the intellitouch controller have the same features of an intelliflo vf pump. Not sure why the pump by itself would reduce the filter time with feature 3 but not on the intellitouch?

  • 16 years ago

    Thanks for the reminder pics.

    Now lets see if I remember all desired behaviors:

    1) Single turnover of pool volume
    2) Use solar to heat pool if heat is desired turned on from inside controller
    3) Use Gas Heater for spa if heat is desired turned on from inside controller
    4) Blower on from inside controller
    5) 2X Deck jet test/day (Why?)
    6) Spa Spill 2X 30 min ea.
    7) Pool Lights on from inside controller

    Relevant Issues:

    1) Pool return in spa valved off because low flow during standard filter cycle causes spilling water to run under the spillway and onto the spa wall. In the future, this can be corrected by putting short walls on the spillway's sides and putting a couple shallow grooves under the lip. This will cause any water trying to flow under the spill to fall in the pool. Alternative is to glue a couple thin strips to underside instead of grooves to achieve the same functionality.

    2) Pool sweep shares suction with skimmer and drain. Line always open except in Spa Mode and Spa Drain Mode. When pump speed is increased, sweep works.

    3) Intellitouch thinks there are two different pool volumes. There should only be one AFAIK.

    4) Why program the deck jets for anything other than manual control at the indoor panel?

    5) Is Solar Heat is in Manual control mode at the front panel?

    6) What speed is spa mode? This should be dictated by the recommendation of the jet manufacturer times the number of jets.

    Useful but not seen in the manual:

    Lockouts:

    If the pool is in spa mode, lock out solar, deck jets...
    If the pool is in Spillover or Spa Fill (same valve settings but not always the same pump speed), lock out deck jets but not solar.

    I can think of other uses for a programmable lockout feature that go beyond what you want/need. I am going to try to get a Pentair Guru to look at this thread. I would like to be able to give them your email adrdress to, if it's ok with you.

    Scott

  • 16 years ago

    From Scott,

    Answers are under the questions.

    Relevant Issues:

    1) Pool return in spa valved off because low flow during standard filter cycle causes spilling water to run under the spillway and onto the spa wall. In the future, this can be corrected by putting short walls on the spillway's sides and putting a couple shallow grooves under the lip. This will cause any water trying to flow under the spill to fall in the pool. Alternative is to glue a couple thin strips to underside instead of grooves to achieve the same functionality.

    I corrected this trouble by shutting off the floor jet return. I using the main spa jets on the walls, for the spillover time.

    2) Pool sweep shares suction with skimmer and drain. Line always open except in Spa Mode and Spa Drain Mode. When pump speed is increased, sweep works.

    Yes, this is working ok.

    3) Intellitouch thinks there are two different pool volumes. There should only be one AFAIK.

    Ok.

    4) Why program the deck jets for anything other than manual control at the indoor panel?

    To Show off, why not! I also know the time is around 3pm since they go off at that time.

    5) Is Solar Heat is in Manual control mode at the front panel?

    Front panel? Do you mean main panel? If so yes.

    6) What speed is spa mode? This should be dictated by the recommendation of the jet manufacturer times the number of jets.

    Hayward jets, without any jets inserts. Very wide, I moved this spa flow to 110gpm, I happier with it. But I thinking to put 1" jets in those 5 jets, to see if I like it better. If so I may need to reduce the flow level.
    I am going to try to get a Pentair Guru to look at this thread. I would like to be able to give them your email address to, if it's ok with you.

    That's fine.

    Steve

  • 16 years ago

    #4 unless there is a cover on the pool, its not a bad idea to have water features run on a schedule to keep mold and bacteria from growing in them.

    #6 You can use MFR's suggested flow rates, but remember these are only guidelines. Some people want stronger jets, and sometimes we have to overpump them to get them to work better.

    I am not sure what you mean by 1" jets. If by 1" jets you mean 1" eyeballs, this probably wont increase the strength of the jets that much. There is a fine balance between orifice size, the distance from the end of the nozzle to the back of the eyeball, and size of the eyeball. If you increase the orifice and eyeball you will get stronger jets.

    What are the issues you are still having. I don't have time to mine the thread, but I have a lot of experience with intellitouch product.

  • 16 years ago

    Yes eyeballs, the jets or the return in the spa doesn't have any eyeballs. The return jets just have the top cap of them no eyeballs so they are like 1 3/4"+ holes.

  • 16 years ago

    Racket,

    Both you and Scott are trying to help me Thanks.

    Your Question

    "What are the issues you are still having. I don't have time to mine the thread, but I have a lot of experience with intellitouch product."

    The issues I have is the spa spillover isn't reducing the filter time. The Solar isn't lowering the reduce time. I still learning stuff all the time.

    We lost some post today.

    So here's what I know today (if wrong please correct me)

    VF features aren't in the intellitouch. You need to do a flow rater for your items. The feature display on intellitouch aren't not the same on the VF pump.

    I redid the intellitouch this morning, so I see if this works any better.

    Display 1

    Pool / Spa
    blower / pool lights
    Landscape lights / deskjet

    Display feature

    Solar
    Spa spillover
    none
    ~ ect.

    (Taking spaces out and place solar first)

    Intellitouch / Intelliflo data

    Flow rate

    Pool 18
    Solar 40
    spa spillover 40
    deskjet 40

    More but working from memory and work burnt me out some.

  • 16 years ago

    Ok would pictures of screens help?

    Does the it really matter how the screens are setup in intellitouch concerning intelliflo VF pump?

    Steve