Bouncy floor question

18 years ago

I am in process of finishing basement, and while joists are "open", considering a fix to my bouncy floor..I have 2 x10's spanning 15+- ft, 16" on center..House is 5+- years old...My contractor suggests adding 2 x8's sistered to joists,full length, supported at existing steel beams... I have read with great interest adding 2 x 4 adhered to the bottom of 2 x 10's,...questions are which method "might" be better? and if we go 2 x 4 adhered to bottom of joists, do the 2x4's need to run full length? thanks in advance for any and all thoughts and opinions

Comments (12)

  • 18 years ago

    Either method would probably stiffen the floor system. I know nothing about the 2 x 4 method, but I would assume that to be effective the 2 x 4 would have to run the entire length in one piece. I also assume that the 2 x 4 piece makes the joist into a faux "I beam". If that is true, then you would have to use only the glue and nail schedule recommended by whomever designed the 'idea'.

  • 18 years ago

    You might try solid blocking connecting the joists. Install the blocking every 5 feet or so. Stagger the blocks so you can nail straight through the joists. You thereby unify the floor into a solid unit. That span for 2x10's is well within the limits of the joist.
    Ron

  • 18 years ago

    the bounce that is experienced is when someone walks heavily across center of room, and the Entertainment Center on wall, shakes,rattles and rolls,lol...I guess i'll try a combo of things, as there is exisiting blocking in center of span, though it looks like it wasn't nailed tightly...

  • 18 years ago

    the blocking idea won't make any difference at all. the supporting joists run in one direction and span between supports. Adding blocks parallel to this won't change that at all. The most direct way is to make the span shorter but that would involve having additional supports in the basement which maybe you don't want. The next is to stiffen the existing joists. Ideally the deeper it is the stiffer so going to 2x12's would make a big difference sistering will also help but not as dramatically. The relationship is b * h^3 where b is width and h is height. Notice the height is cubed. so doubling the width will double the stiffness but adding 2in. to the height will increase the stiffness 8 times.
    hope this helps

  • 18 years ago

    Ditto sdello. You get much more bang for your buck by increasing the height of the joist than by increasing its thickness; if you can afford the loss of headroom, that would be the way to go. Even adding half of a 2x4, so that the joists were 11" tall, would probably be a huge improvement IF you can get the old and new parts well-fastened so that they act like a single beam. I'm thinking that screws and a lot of construction adhesive would be involved. The added 1 3/4" of height would make the joists more than half-again as strong as they are now.

  • 18 years ago

    would i get any reduction in "bounce" if i only attached 2 x4's to bottom of joist for 12 ft,instead of the entire run of 15+-...I have ac ductwork and piping that would need a little "adjustment" to make 2x4's go over...Nials or screws? how frequent? and what type of adhesive?/ You guys are the best!!!! I'm buying the 1st round for you!!!

  • 18 years ago

    see here:
    http://ths.gardenweb.com/forums/load/repair/msg0915531723856.html?21

    look for the posts by a guy named Brickeyee, he's an engineer and explains a great method for reinforcing your floor

  • 18 years ago

    This post is getting downright interesting.

    Qdog I hope you'll post back with whatever you decide to do and how it works out.

  • 18 years ago

    Adding 1,.5 inches to the bottom of a 2x10 will stiffen by ~57%.
    Adding a 2x4 will more then double the stiffness.
    It does not need to be between the joist and the bearing surface, but the longer you can make it the better.
    The extra fasteners help spread the load better.
    Adding a 1/8 inch thick by 1.5 inch steel strap is equivalent to adding about a railroad tie (~10 x 10, the exact numbers are buried in my notebooks at the moment).

    The number of fasteners really depends on the wood species being used, but a 16d nail (or equivalent diameter screw shank) is at least 300 pounds in shear in any softwood likely used for joists.

    Field applied glue products are so risky (as Boston about epoxy) that they rarely are assigned ANY structural rating in wood construction for fabrication outside a factory environment.

    Notice there is no fastener relief for drywall with glue.
    All the screws or nails do in a floor is hold things in position, they are not actually structural.

    This is what limits using the sub floor as a structural element for joist bending. If there was a strictly enforced nailing schedule, some allowance could be made.

  • 18 years ago

    thanks for the terrific insight,Brickeyee, i was hoping you stop here...I am going to do this this week, so i'll add my results soon after...Am i correct if you implied NOT to use adhesive along with nails when adhereing the 2x4 to the bottom of joists?

  • 18 years ago

    ok, going to try the 2x4 added to the bottom of joists tommorrow...Can only get 12' lengths in, instead of the 15'+- exisitng length, so we'll see how it works...

  • 18 years ago

    Since most of the flex actually occurs near the middle it can still be very effective.