load bearing wall removal

12 years ago

Hello,

I recently hired a contrcator to remove part (approx 8')of the wall between kitchen and dining room. The house is 22' wide and 30' long. The wall location is on the top of the metal beam that runs in the basement approx. 12' from the outside wall. The joists (2x8) for thr second floor join on top of the wall that we partially removed. The roof is triangle type and it sits on the outside walls (30' apart). He used 2 LVL beams (1 3/4" x 11 7/8" x 12' LVL 1.9E). I just want to make sure that this will be anough to support the second floor. The house is about 45 years old, no heavy materials like hard wood floors or tiles are installed on the second floor, just plywood and carpet. Please see the attatched pictures for refrence.

thank you!

Comments (8)

  • 12 years ago

    What did your local code inspector say when you filed the plans? When he inspected?

  • 12 years ago

    Also what did the report by the structural engineer hired by either the GC or the Architect recommend?

  • 12 years ago

    the job has not been inspected yet beacuse there is other work being done. I think the plans said 2x12 but I don't know for sure.

  • 12 years ago

    "I just want to make sure that this will be anough to support the second floor."

    Ask the contractor for the load calculations. Or hire a structural engineer yourself.

    Normally the calculating is done BEFORE the permits are granted.

  • PRO
    12 years ago

    " I just want to make sure that this will be anough to support the second floor."

    Yes. Plenty.

  • 12 years ago

    Not all jurisdictions check structural calcs when granting permits. That's the case for where I live now and my last home.

    In such cases, the manufacturer of the LVLs typically can do the calcs and determine what's needed, as this is their bread and butter. It's not something that mandates the use of a separate structural engineer, unless your local permit people require it.

    That's what we did when we replaced a load-bearing wall with an LVL (though we put it flush in the ceiling).

  • 12 years ago

    When I applied for a permit the city office told me I could bring in all the LVL manufacturer docs to prove the beam was the right size to replace the load bearing wall, and also show them there was appropriate support in the basement to hold up the 1st floor support posts (there was a steel beam in the basement under the floor). Or I could hire a structural engineer and have him certify it was correct. I took the easy way out and paid the structural engineer, since the city engineer seemed a little difficult to work with.

    Bruce

  • 12 years ago

    To answer your question it is necessary to know the span of the beam (is it 8 ft or 12 ft long?) and the area of the second floor that it supports.

    It is not enough to describe this condition; you need to make a drawing.

    Off hand it seems like it might be oversized. As noted earlier LVL manufacturers will size a beam like this for you if your lumberyard is willing to contact them.

    A more important issue is probably the location of the support posts on the beam below. If they are not near a basement support post, the steel beam might need to be checked for the new point loads.