installing a lintel

20 years ago

I need to install a lintel over a basement door that was done without permits, etc. Can someone advise the best way to do this after the fact.

Joists do run to this wall, and the foundation is poured concrete (10"). (The door has been in for over a year, and there is no apparent sag, etc.) Still, I would install temp wall support inside. (total width that needs support is 54", since it adjoins an old window opening)

I am thinking of cutting a notch for a steel lintel, and hammering the lintel in from the exterior. Since the door framing is up against the rim joist, I am considering notching the bottom of the wood sole plate that sits on the wall. Thoughts? (how would you do that? Sacrifice a circular saw blade?) Otherwise I would have to notch the concrete with a grinder, but I'd have to somehow continue the notch across the door's rough opening frame. Any ideas?


Comments (5)

  • 20 years ago

    A simpler approach might be to create a 'blind header' directly above the door.

    What you would do is cut back the floor joists from the rim joist say 4 1/2" and temporarily support them.

    Then you could install 3 2x10s (or whatever the depth of the floor and rim joist lumber) about 60" long along side and fastened to the rim joist over the door.

    Re-attach the joists to the header using joist hangers.

    Done.

  • 20 years ago

    Interesting idea.

    But there's a small catch. To keep my question simple, I neglected to mention that the rim joist (2x10) is also tied into an addition (so it's bolted to a 2x6 on the exterior). I guess I could still do it if I hollowed out some room for the bolt heads.

    What about this option:

    Inside, since I have 3 1/4" vertically to work with (the door frame is 1.5 inches below the edge of the foundation wall, and there's 1.5 gap further up to the joists (since the plate only sits on the outer 1/2 of the 10" wall). What if I push angle iron up against the joists inside with the ends resting on 1.5" block that sit on the wall? Block could be PT 2x, or even a 1.5 thick piece of steel welded to the angle iron itself? (And is it structurally the same to install as an upside down "L"?

    Also, I don't know if it's "inspectially ok" to rest the load on block like that, but the advantage is that I would have to do minimal cutting and supporting to install it.

    Thanks for the help.

  • 20 years ago

    I like my idea better...:)

  • 20 years ago

    Ok, but yet another thought comes to mind.+

    How about if I use a piece of steel shaped like a 3 inch "C" - I think it's called 3" channel. Actual dimensions are 3 x 1 3/8 so it could sit adjacent to the sill plate. I imagine it might be a bear to get in there, but seems to have promise.

    Whadaya think?

  • 18 years ago

    so how did this project turn out? i want to do the same thing.

    not sure i understand the "blind header" though. why are we concerned about the thickness of the floor above?