flood test

11 years ago

So, for our swanstone shower base and Kerdi on the wall, contractor keeps trying to talk me out of having flood test done. Plumber did pull the permit and an inspection will be done, I think flood test should still be done after membrane dries for a day, to check the seams and the drain. Correct?

I





Comments (13)

  • 11 years ago
    last modified: 11 years ago

    With most manufactured pans the perimeter tiling flange is at a higher elevation than the top of the pan curb. I'm not terribly familiar with Swanstone pans, but a flood test of the pan will usually just check the integrity of the drain-to-pan connection. It could, I suppose, show any defects in the pan itself. Micro-cracks that may leak, etc.

    But it's likely that the the kerdi-to-flange connection is above the flood level of the pan itself, so a typical flood test will not wet or test the Kerdi seam.

    With all that said? Yes, do a flood check. You still want to check the drain connection, and with you having an AHJ, it's likely a code requirement in your area.

  • 11 years ago

    Thank you mongoct. Do I still need 24 hour test and 2 inches of water or just small amount of water to test drain? Plumber set the pan yesterday and put just a small amt water in.

  • 11 years ago

    Isn't the flood test required to get the permit signed off, or is that only for a tiled shower floor?

  • 11 years ago

    Our inspector passed it today and I asked him if a flood test was required. He said no. Rats, I wanted him to back me up

  • 11 years ago
    last modified: 11 years ago

    The flood test is part of the plumbing code. But UPC doesn't require a flood test for manufactured pans. Just for site-formed membraned trays (CPE, sheet membrane, liquid membrane, copper, lead, etc).

  • 11 years ago

    I don't have UPC handy, but as a footnote, I think UPC only requires a 15 minute minimum test.


  • 11 years ago

    mmaggied, I am planning on a Swanstone shower, too. I am going for the ADA one with the trench drain at the front edge for a roll-in shower. I have not seen it in person yet, nor have I even found a salesman who knows it exists without me telling them where to find it on the internet. Would you share info about the shower base you are using and photos of the installation, please? I know others who are looking at solid-surface (ie: no grout!) showers would enjoy seeing it, too. TIA and best of luck with the remodel!


  • 11 years ago

    Nancy, yes I will show photo. Right now, the workers have their equipment on the pan. I ordered it through our remodeler. Also, in PA, Ferguson can order it

  • 11 years ago

    Mongo, thanks for all the info. Hubby is satisfied that the drain connection won,t leak as we can see it from below in the basement w our bath on the first floor and we checked when plumber did the little fill

  • 11 years ago

    Congrats. I took a look at a Swanstone pan today as a matter of fact. The pans are pretty stout. No flex equals less chance of a drain leak due to material fatigue. Good luck with the rest of your installation.


  • PRO
    11 years ago

    The ideal water level is 2" and no more than 4". Good for you checking.


    Your project is one of the few that is travelling down the proper path of inspections.


    Always flood test your showers. Ready made. Custom Made. All the same.


    Bravo.

  • 11 years ago

    Mongo, thanks for the report on your assessment of the shower pan. Even such a little thing as your having seen it in the store and giving us your opinion of its being "stout" is great to have. It is not like we homeowners get the chance to get good at this remodeling stuff. If we do, then we are done for the next fifteen years or so and everything we learned is out of date the next time we jump into this world!