Trane xl 18i changes to quote

11 years ago

help! Our hvac sub quoted an xl 18i 4 ton system, but it looks like we are getting different models and different size! original quote was for Trane 4TWX8048A1 WITH *AM7A0C42H31 air handler. what is installed to date is a TEM6A0C36H31 to go with a 4TWX8036C1 XL18I.

We are building passive solar house with good windows, tight insulation and foam on ceiling in zone 6b..some hot days, some cold nights, but not extreme. Our contractor trusts the HVAC sub, and is only moderately engaged…so I am turning to garden web to see if we are being steered off course.

We did have to ASK for an exact model quote, so it is disconcerting to have surprises. Manual J load is attached, and HVAc sub is saying 3 ton is right size. Any input on that? We don't want to undersize our unit, and the original suggestion was for a 3.5 Lennox 14HPX…but since we wanted 2 stage we went with the XL18i. Thank you.

Comments (3)

  • 11 years ago
    last modified: 11 years ago

    What size home?....why haven't you discussed your issues with your GC and HVAC sub, that seems a reasonable starting place. I will assume you have excellent building/insulation qualities for your home. What size heat strip? What thermostat? It does seem that a 3 ton is the correct size. See below.

    7553562 ActiveSystems TRANE XL18I TRANE 4TWX8036C1 TEM6A0C36H31+TDR 1075 855 36200 12.50 17.00 32000 9.60 20400 1HRCU-A-CB 270678 Yes

    IMO

  • 11 years ago

    It is a good that the HVAC contractor has provided a load calculation and trying to not over size the equipment. However I am concerned with some of the numbers.

    The summer design temperature is 86 degrees. He picked the temperature for the Asheville NC airport. This is a lower temperature that was used for my house in NJ. Most of NC has a design temperature of 92-93 degrees. Do you think 86 degrees is a typical summer high?

    The area is listed as 4420 sq. feet. Is this a one story 2210 sq. foot house with a full walk out basement?

    What will be the location of the air handler? What are the insulation values for the attic and exterior walls?

    I see the heat gain for the duct work is zero. The duct work has some heat gain even if it is conditioned space. Duct work in unconditioned space will have even more gain.

    The calculation of 2.6 tons seems low. Making some changes will increase the heat gain calculation, but a 3 ton condenser may still be the right size. Talk to the HVAC contractor about making the calculation as accurate as possible.

    knitmaster thanked mike_home
  • 11 years ago

    Good pickup by Mike...I agree figures seem low especially on cooling. I would think a 90 degree minimum design outside temp with 74 degree inside setting. That's why you should have a sit down with GC and HvAC sub to review load calc and equipment chosen. Also you want adequate returns for your home, both size and number for good airflow and comfort. R8 ductwork insulation minimum.

    IMO