Should I close this return?

11 years ago
last modified: 11 years ago

We tore down a wall to combine two rooms into one. In doing so, we sealed the returns for one of the rooms. To make up for this, I had another return installed. I've had contractors tell me to close the new return I had installed. The reasons to close it: One return will give better airflow pressure, and high and low returns will further reduce airflow. Does that make sense to the experts here?

The closed old returns that you see in the pictures, these were going through the wall that was previously there, and the return vent was high like the other old return. The new return, however, will stay on the floor.

Also, the existing old return you see in the pictures, should that be opened on both sides, or is it better to just keep it open on one side?

Comments (28)

  • 11 years ago

    I don't see your contractor's logic of getting better air flow with fewer returns. In most cases, additional cold air returns helps overall circulation; however, I've never seen them in the middle of the floor. That new return also very small, so it is probably not even big enough for one room.

    Will there be a grill in the floor? That is very unusual for a cold air return.

    Bruce

  • 11 years ago

    Let's be sure you're not confusing 'return' with 'supply'.

  • 11 years ago

    Yes, there will be a grill over that return. I know that's unusual. I had a contractor put it in many months ago. I understood way less at the time and thought it was a good idea. "Even though it's small, it's still better than nothing," I thought.

    All of those are definitely returns. I (painfully) applied foam and mastic to all the ductwork -- the ducts run through the basement ceiling -- so you could say I'm intimate with the duct system at this point.

  • 11 years ago
    last modified: 11 years ago

    Since we don't have an overall plan of your system we cant really say what to do with it. You should have a minimum of 200 sq in per ton of return and it is better to have 400 sq in per ton. Those returns are very small, and they do look like supply registers because they are so small. Returns that used to be in the wall you have to measure the opening in the floor, not the return grill on the wall.

  • 11 years ago

    The old returns, the two sealed and single existing, are between studs. I'd approzimate the size at 14" x 4". All the returns in the house are this way.

    The new return uses an angle register (see picture). The basement ceiling was very cramped and we had no choice. Looks to me like that further reduces it's effectiveness.

  • 11 years ago

    " The reasons to close it: One return will give better airflow pressure, and high and low returns will further reduce airflow."

    Both those statments are incorrect. I must say I'm suprised two or more contractors said the same thing since I have never heard either before. Wherther there are other issues can only be determined after assessment of intire system,preferably not by any of those who told you that..

  • 11 years ago

    Do not be surprised. Everyone on these types of forums: Your knowledge and enthusiasm is extremely rare. Evidence: You enjoy your work so much, you answer questions in your spare time.

    It takes forever to find that one contractor in an area who is like that. Everyone is in the industry 20+ years, has great reviews, was recommended by someone, etc. Forums like these are helping me figure out what to look for, and thankfully I have found a few true specialists. Hope to find one in HVAC soon.

  • 11 years ago
    last modified: 11 years ago

    With all the returns like that, you will need at least one return for each supply. Each one gets you about 56 sq in of return.

    Normally there is a return plenum (using the floor joists or not) that runs in the middle of the house and the return uses larger floor grilles. So the returns are found near the middle of the house and the supplies branch out to the exterior of the house. What you have is not wrong, just requires more ductwork and is more complicated than it has to be.

  • 11 years ago

    The returns are all in the middle of the house, with the supplies branching out to the exterior, just like you said it should be. The return ductwork "ends" at the floor, and the studs and drywall act like the rest of the duct, leading to the grille high on the wall.

    How about that one old return with grill high on the wall? If we open that up on the other side by placing a grill on that side, too, will that negatively affect airflow?

  • 11 years ago

    "the studs and drywall act like the rest of the duct, leading to the grille high on the wall."

    Now I understand how that grille at the top of the wall was a return. I couldn't figure it out until your last post.

    Using the wall captivity as a return is a bad idea. All the dirt and debris inside the wall gets pulled into the duct work. Don't repeat this mistake.

    Rooms that are open to each other don't need their own returns. One or two big returns on the first floor will work. The duct elbow you show above are designed for supplies. You are going to create more air noise is you install several of these small returns.

    Your general contractor does not understand HVAC ducting and air flow. Hire a HVAC contractor who knows what he is doing. It would be a shame to spend all this money on the renovation and then have a HVAC system that is not working properly.

  • 11 years ago

    I hear you on finding such an HVAC contractor. Let's just say it's a process. If an HVAC contractor subs out their duct work, is that a bad sign?That duct elbow is the only extra return we've installed in the house. The old returns in the pictures that were sealed are the only ones we sealed in the house.

    Unfortunately, all the returns on the upper level, save for that new duct elbow one we made, use the wall captivity.

    I will say my brother has had his upper level level redone to have one big return instead of many smaller ones, and he now wishes he could have the old system of a return in every room. That's why I was cautious of "consolidating" returns, and went the opposite approach of the more returns the better.

  • 11 years ago

    I see no problem with an installer hiring someone who is good at making duct work. It requires the right skill and tools to do the job correctly. But the HVAC contractor should have the knowledge of how big the ducts should be and how they are connected.

    One return per room works well with bedrooms when the doors are closed. My house only has central returns on both floors and it doesn't seem to be a problem even for the bedrooms. There is enough of a gap below doors for air to flow. During the day the doors are open.

    You have to wonder what the what builder of your house was thinking. He went through all the trouble of creating separate returns but then did not spend the extra few dollars to put a duct inside the wall. If he wanted to save money he could have put the return grille near the floor. In a house with 8 foot ceilings the height is not going to make much difference.

  • 10 years ago

    So will a "skinny" rectangular duct that fits in the 14" x 4" wall cavity be okay, or should I create a larger framing and increase the duct size?

  • 10 years ago

    My only concern would how much air is going to be pulled in this return and will it be noisy. If there is another return nearby in an open area then you may not need it.

    You could shorten the length of the duct and install the grill close to the floor. The height is not that critical with 8 foot ceilings.

  • 10 years ago

    By noisy, you mean the noise the air will make traveling through the duct? I've never noticed noise from a return. I hope I don't start noticing it now that you've mentioned it.

  • 10 years ago

    My understanding is you had no return ducts. All the returns relied on wall cavities. Installing a narrow return may cause some increase in air noise. It is hard to tell since you have several small returns.

  • 10 years ago

    Yes, your understanding is correct. Thanks for the explanation.

  • 10 years ago

    I finally found a guy who believes returns should be proper ducts, everyone else thought I as crazy, cause using the wall cavity is how everyone does it. Is it code to make proper returns where you live, mike_home?

    Now an issue with putting a duct in that wall cavity, e.g., is on the underside, the builder used the plywood floor, the basement ceiling joists, and pieces of sheet metal to form the rest of the "duct" that leads to the main return line. Will it be worth it to have a sealed return duct above the floor, while below the floor, the rest of the "duct" is this way?

    Also, the way the basement ceiling joists were put in, they don't always align with the studs on the top level. So if I want to take a proper duct all the way through to the main return line, sometimes we can't fit more than a 7" oval through (and it requires two bends.) Is a proper 7" oval return duct still better than a 14x2" wall cavity/joist thing?

  • 10 years ago
    last modified: 10 years ago

    Normally for returns to an air handler in the basement, you will have bulkhead(s) running perpendicular under the floor joists (in the basement) and parallel between the floor joists, all you have to do is close off the bottom of the floor joists to make a return parallel with them.

  • 10 years ago

    Yes, that's how it is right now, but I was under the impression that is the "wrong" way. I.e., returns should be first class duct runs like supplies usually are.

  • 10 years ago
    last modified: 10 years ago

    They dont have to be, mine arent and it works fine. The area is greater in the returns and not normally under high pressure like a supply line, so your surface area drag is not as big of a deal as supply lines. How many tons is your air handler? Some say 100 sq inches of return per ton some say 200 sq in. I tend to think 200 sq in per ton is correct for quietness.

    Example: If you have a 2 ton air handler you would need 400 sq in of return grille (or hole area to the return). Sometimes they will use a wall and cut a hole in the floor at the wall. That only nets you a 3.5x14 area for air to travel = 49 sq in. Then they stick a 10 x 20 grille on the wall, consider it 200 sq in and call it good for that half of the house. You need a true 200 sq inch per ton of return grill not bottlenecked by using wall returns or other bottlenecks. So for the example of the 2 ton, you would need two plenums with a sq in area of 200 each headed to opposite sides of the house, and where they meet it should have an opening for 400 sq in and plenum to the air handler to support that. It is common to use two floor joist cavities for one return, that gets you about 28 x 10 or 28 x 8. The wider you can make it, the narrower it can be for headroom.

    Over time dust will settle in the returns, it should be vaccumed out, other than that it is generally not a problem. Takes a good 20 years before enough dust settles to be worth doing, otherwise a standard pleated filter will suffice. Using too high MERV of a filter is hard on the blower motor, and using the plain fiberglass filters is not good for allergies or having pets.

    If you want to have a sheet metal plenum inside the floor joist cavities, that wont hurt either, it will just be more labor and material in my opinion. You shouldnt be using round ductwork for return, it puts the system under too much stress to have both the supply and the return under pressure. Higher pressures make it louder also.

  • 10 years ago
    last modified: 10 years ago

    Before closing off the bottom of the floor joist, do you caulk the area where the plywood floor meets the joist? Or would sealing that too tightly put the return under pressure?

    The air handler is listed as "up to 3 tons". Outside AC unit is 2.5 tons. Coil is 2.5/3 tons.

    To make sure I understand correctly, if I go with a sheet metal plenum inside the floor joist cavity, I should use rectangular ductwork instead of round ductwork, correct?

  • 10 years ago
    last modified: 10 years ago

    You get more area, less flow restriction, less pressure on the system and less noise, yes rectangular for returns. For supplies, there is usually a rectangular main plenum either one way or two way, then they use round or oval take offs off of that to go to the supply registers.

    Sealing the bottom of the floor joists is a good idea. You want your return air to come from the grilles that have been placed in specific areas (returns usually are placed in the center of the house and supply registers on the exterior near windows). It is good to have supply and return available in each closed off room, otherwise, space underneath the door to allow air to flow. You need returns to assist supply air by pulling on the air in the space.

    http://www.perfect-home-hvac-design.com/hvac-for-beginners.html

  • 10 years ago

    Vith, what's your view on using the wall cavity in between two studs, enclosed within drywall, as part of the return?

  • 10 years ago
    last modified: 10 years ago

    As long as they use the square inch of the hole in the floor that goes into the return (at the bottom of the wall) for their calculations, and they give you enough return to operate correctly. Usually this doesn't happen with wall returns because they are so narrow. You will get a larger return sq inch with a floor grille and it is normally a better option. My house had returns on the wall, it was not enough. I had to add more grille sized accordingly (floor grill upstairs, grille in ceiling downstairs, extra grille for new room downstairs).

  • 10 years ago

    Here's what I ended up with. It's not really rectangular, not really oval. It's a first class duct run all the way to the return. (I forgot to take a picture while the floor boards were off.) The ductwork doesn't fit the whole cavity because of basement ceiling joist alignement, as shown in one of the pictures. Once I found a guy who was pro-ductwork, he wouldn't let me back out and do it the other way.

    I estimated our air handler at 2.5 tons although it's listed as "up to 3 tons". Using the min/max of 200/400 sq in per ton, we come in at the minimum with almost exactly 500 sq in. Using the other method -- namely, one matching return for each supply -- we are under: We have 2 1/2 unmatched supplies. (Bathroom supplies are half the size in this house.)

    Thanks everyone for your help. I'll try my best to update later and let you know how it works in real life. (P.S. Should I foam the gaps between the ductwork and the floor?)



  • 10 years ago

    This is a big improvement over what you had. If walls and floors are open, then adding a duct is easy and not expensive as long as you have someone who knows how to make ducts.

    You can stuff fiberglass insulation in the floor gaps. The foam would make a better seal but I am not sure it is worth the expense.

    Are those studs placed 16 inches on center? They seem to be further apart then they should be.

  • 10 years ago

    It cost $240 including parts to make this return duct, but I guess if I do a lot at one time, I can bring the cost down.

    Yes, 16 inches on center. The studs on the right that look all strange, that was my general contractor's work. They accidentally sawed through the stud while removing drywall, so they used another 2x4 to "repair" it. Then, they used another 2x4 to install a light switch there.

    My duct guy didn't like the electrical work to be in that return cavity (see original picture), so he moved it up to the attic, then made a groove in the 2x4 to bring the light switch wire down.