Please tell me this blower will work

10 years ago

Hi. We have purchased a BlueStar 36 RNB with griddle and we were expecting to use a 1200CFM BlueStar hood and blower with it, but because of quirks that were discovered later, that won't be possible. We cannot use an in line blower, in must be an internal blower. My rep has suggested the Wolf 900CFM blower. Do you think that will suffice? I cook a lot, but not a lot (read: any) wok cooking.

Comments (6)

  • 10 years ago

    Sorry, I know there are more details--I simply flaked.

    OK, so range is 36" with griddle and it will be going into a cabinet face that will be 42" wide and at least 22 1/2" deep, but since it will be custom, I can assume I can make it 24" if I want. It will be 30" above range. Duct is 10" round with one slight bend to roof. We live in Austin, so a make-up air system is not required, but the kitchen has three exterior doors that are always open, year round .

    The appliance rep quoted me the 91422 900 CFM Wolf Internal Blower and the PL342212 Wolf 34" custom air insert.

    I hope that helps and thank you for your time. Venting is ALWAYS Greek to me, no matter how many posts and articles I read.

  • 10 years ago

    OK, we can look at the Wolf Design Guide and find that on the Pro Hood page there is a liner that is 40-3/8 inches wide by 22-1/2 inches deep. The next smaller 34-inch liner is too small; you need width overlap. Ignoring wall thickness and any control space (for which I have no data, not owning this particular hood), this is a possible capture aperture area of 6.3 square feet. At 90 CFM per square foot for adequate containment, you should have an actual flow rate of at least 570 CFM. With a low resistance exit path and minimal pressure loss MUA path, the main restriction will be the baffles.

    I don't have the fan curve for that particular 900 CFM blower, but looking at the likely comparable curve for the Broan-NuTone 801645 900 CFM internal blower, and making some WAGs about the pressure loss in the baffles, duct, and external duct cap, I would guess that you can easily surpass an actual 570 CFM at full power with that blower.

    Plan on blocking any gaps between the cabinet and the liner so grease doesn't get into them. A sheet metal shop can provide appropriately sized stainless steel pieces. Make the cabinet deep enough to fit the actual liner dimensions.

    kas

    sf_treat thanked kaseki
  • 10 years ago

    What sort of quirks would prevent you from using the Bluestar 1200CFM internal blower?


  • 10 years ago

    So, it is all gettIng a little above my pay grade, but my husband and I don't want a chimney style hood. The type we wanted requires a transition from the hood to the venting that would have to go in the roof, and there isn't enough room to house all of that due to the pitch of the roof.

  • 10 years ago

    What about a Bluestar roof mount external blower?