Conflict between Spec and Plan

10 years ago

Would like builders and legal input on conflict between spec and plan.

What if there is and item or feature called and detailed out on plan and no mention in spec? Is this a conflict or really an omission in the spec.?

Example: plan calls for "concrete slab (verify final layout)" on plan view. This slab is also shown on elevations and has dimensions on it for its size and elevations but there was no mention in the specs for this slab anywhere.

I can understand that when there is a conflict between plans and specs the specs over ride the plan. What about the case of when the plans show something that the specs don not mention. There are usually other details that are not mentioned in the specs but are shown in the plan.

What is the "usual" or lets say typical legal solution to this example or issue?

Thanks all.


Comments (12)

  • 10 years ago
    last modified: 10 years ago

    Specs are meant more to define what product is used in elements of building, not if it's used. A concrete spec would say what the mix needs to be, how long it needs to cure etc. Theoretically, simply not having the spec in there would give a contractor free range to bid whatever mix of concrete he wanted to use. Default is, if its detailed in the plans, it is to be included. Often times if great detail (i.e. concrete mix) is given on the plans, it is not included in the spec since information overlap is where mistakes are made by the architect/spec writer.

  • PRO
    10 years ago

    In residential work, depending on who provides the construction documents (and the fee for doing so), there can be a wide range of practices. Generally speaking, there are drawings, notes and schedules included on the drawings, and in proper, full service projects, a complete specification for the project. Specifications define the quality for workmanship, materials and products used in the project. It has generally been held that, in the advent of conflict within the construction documents, the specifications will prevail. Every design firm has their own approach to preparing specifications, but many follow one national standard or another. Experienced and knowledgeable design firms have their own processes to ensure that information in the drawings, notes an schedules and specifications are organized so that the information is presented only once in the construction documents, and not repeated in in two or more places. Commonly accepted construction techniques and/or code requirements for construction may be called out by reference and not noted in detail in the documents.

    In the case of work shown on the drawings, and not mentioned in the specifications, for example such as concrete strength and reinforcing for a slab, it would be commonplace to either have a foundation detail drawing with the information or to have a note or other comment on the foundation drawings at an appropriate location.

  • 10 years ago
    last modified: 10 years ago

    It's not a conflict if there is no conflicting information. The GC should know what is appropriate for the reinforcing, etc but he should have asked before starting.

    What is your concern?

  • 10 years ago

    Great input Virgil

  • 10 years ago

    I guess maybe I didn't make myself clear enough.

    This is a new home build that was drawn up by General Contractors Agent, an Architect that works work for him.

    My concern is the drawings show a concrete slab. Called out on drawings "concrete slab (verify final layout)".

    The drawing also gives dimensions as to the size of this slab both on the plan view and one elevation view. It is also called out in the elevation view as "conc. patio".

    In the specs generated by the General Contractor there is no mention of this slab. His specs are layed out in a fashion that callout a feature and then they detail out info of that feature. There is info. given on other concrete work such as garage slab, rear stoop and footings and foundations. These features are all mentioned and there is info on thickness, sealing and ingredients (fiber mesh) along with other detail that may pertain to each feature.

    So nowhere is this slab mentioned in the specs. So my Contractors stance is that the specs and the drawings are in conflict because the slab is not called out in the specs. In a conflict we agree that the specs dominate. My stance however is the lack of any mention of this feature in the specs does not constitute a conflict.

    My contractor feels that he is not on the hook to supply this slab.

    I disagree.

    So I am interested in people in the business and with maybe similar experiences.

    Is a feature that is called out in the drawings expected to be included in the build even tho it is not mentioned in the specs?

  • PRO
    10 years ago

    If it's in the drawings, it's in the construction documents which the builder agreed to provide by virtue of his bid and contract for construction, which is to provide what is shown and called for in the drawings AND specifications.

    The drawings identify what is to be constructed. The specifications identify the workmanship and standards for elements of the work illustrated on the drawings. Not everything in the drawings is included in the specifications.

    The fact that mention of the specific slab is not in the specifications does not constitute a conflict with the drawings.

    It's rather odd that the construction documents, which include the slab, were prepared by an agent of the builder, who now says he's not responsible for some of the work in those documents. The fact that the slab is not mentioned in the specifications in no way changes the scope of work illustrated by the drawings.

    It sounds as if the builder's agent made an error by including the slab, which the builder had not anticipated and was subsequently surprised.

    You have two choices: 1) Spell this out to your builder (who must already know); 2) Talk to your attorney. If will be better for everyone if you can persuade your builder to construct what are on the drawings.

    The cost of a patio slab is not that much.

  • 10 years ago
    last modified: 10 years ago

    We are currently building a large, high end Craftsman style home. According to our builder, house plans rule! If it's on the plans, contractor has to give it to you...and that's according to our contractor! If he's not including things, as in the case of some built ins, he mentioned it in the specs... "Built ins next to fireplace are the responsibility of the owner." If nothing is mentioned on the specs about omitting the slab, he should provide it.

  • 10 years ago
    last modified: 10 years ago

    Another example is my light switches. My house designer included in my drawings lighted rocker switches. I didn't know this, nor did I care what kind of switches I got. After house was bid out, contract signed, construction underway, contractor calls and says, "Your plans call for lighted switches." Okay? It was missed in the bid, but since it's on your plans, we'll have to give it to you." He said it was a $2500 difference. Found out later he tried to get the electrical company to eat it since they're the ones that missed it. They refused. So, guess what? I'm getting lighted rocker switches.

  • 10 years ago

    He bid the build based on drawings, therefore all slab work was included in his price.

  • 10 years ago

    thanks for the replies,.

    As far as getting the best house for the least amount of pain, I'm past that point.

    We sat down with Architect, GC and GC wife and went thru everything before quoting, we mentioned the slab, it was added to the drawings per our request. GC started with the position that if its not in the specs, its in conflict with the drawings and the specs rule over the drawings.

    I pointed out 2 other things that are in the drawings and not in the specs and am asking for an answer if these are not included also.

    One is French Doors between Vest. and Living area of house. GC interpretation of french doors is just a pair of doors. No glass. Not what I consider french doors. He is aware that some people think like me, but neither he nor the architect asked for clarification at any point of what I thought french doors meant.

    The other is sound deadening in certain walls. I specifically said I wanted Roxul Safe and Sound used.

    So the end result is he is going to look over his wife's notes and see what that says before deciding what to do.


  • PRO
    10 years ago

    If we show something in our plans then it is part of the scope of work. We make use of specifications to clarify construction details that would otherwise clutter the plans and make them less readable. For example, we might show a no. 4 rebar in a section view of a concrete footing and give the technical specs for the metal and how the rebar is to be installed in the specs.

    Since your plans show the slab, but it is not described along with the other slabs in your specifications, it is an omission. I suggest you inquire about how the designer (which I understand to be someone employed by your builder) remedies errors and omissions in the plans.