I am doing an home addition to add 1000sqf to the existing house. The total living area would be around 3100sqf. The previous owner installed a 80K BTU Trance 80% efficiency furnace 8 years ago. It's relatively new and quiet. The model number is TUE1c100a9481ab. I want to get some opinion whether I need to replace it with a bigger one. Contractor said it may not be enough for 3100sqf house. He also recommend to add a AC at the same time. If so, what kind/size of system do you guys recommend? 100BTU, 5ton?

Comments (10)

  • 9 years ago
    last modified: 9 years ago

    your location?...current design of your home?...tell us about your addition, going up or out?...generally, I think for comfort you would be better off having two separate systems. It would seem though that your existing furnace is oversized but could possibly handle the new addition strictly on a BTU basis. I think you should ask your dealer to run some load calculations on both existing structure and new addition both heating and cooling.

    you should know your existing furnace is a relatively low end Trane single stage with a conventional blower motor. It has a 4 ton rated blower that could accept up to a 4 ton AC condenser.

    IMO

  • 9 years ago
    last modified: 9 years ago

    I live in SF bay area. We have mild winter here but it was pretty rainy and cold in the past winter. I hired a general contractor. But all the contractors I talked to do not want to/willing to do a calculation. They just assume I need a bigger system with the addition. I don't know if they just want more work and less trouble.

    The current house is 1950 sqf with 300 bonus room (also heated with one register, it was a lousy addition by previous owner). It's single-story ranch house. The addition is to add another 800sqf living space and also legalize the bonus room. We extended to the front and also back in four places to add a exercise room, breakfast area, office, also converting part of the garage to living space. All single-story addition.

    I don't have AC as we barely need. We have a big oak tree in the backyard covering most of the house, very cool in the summer.

    Why do you think the existing system is oversized? The system was installed in 2009. It's very quiet (which I like). But there are two issues:

    1) It takes about 30mines to heat up the entire house from 50 to 66 degree. Is this normal?

    2) The furnace keeps turning on during winder nights, probably because the house is old and leaky?

    3) One of the room at the far end of house does not get heat up. It feels colder than other rooms. Not sure why.

    I can see if I can post a picture.


  • 9 years ago
    last modified: 9 years ago

    First of all, you can't size a system properly without knowing the heating and cooling load both for existing structure and new addition. Based on your Bay Area location and mild climate, yes, I would say you are oversized on heating. Where is furnace located? Do you have crawl space?

    legalize bonus room?

    1. Why would one drop temp down to 50 degrees-home sometimes unoccupied? Depending on outside temp, raising temp 16 degrees in 30 minutes seems quite normal.

    2. Windier? Where is furnace located? What are typical run times? I would expect shortcycling may be occurring at times depending on outside temp.

    3. Your dealer should address this issue, paying close attention and inspecting ductwork sizing/design and insulation properties.

    i think I would want to hear from an experienced dealer about the practicality of zoning existing structure and new structure. If not that, then 2 separate systems.

    IMO

    Tiewen Han thanked tigerdunes
  • 9 years ago

    General contractors know very little about HVAC. If they have to add to HVAC system they will hire the low cost subcontractor and budget as little as possible. You may want to hire your own HVAC contractor who can calculate what you need and offer a few options on how you want to heat and cool the addition.

    Raising the temperature from 50 to 66 degrees in 30 minutes is a sign that the furnace is over sized in my opinion. The winter outdoor design temperature for the SF area is 39 degrees. It does not take many BTUs to keep your house warm. The fact that your furnace is quiet means your duct work is probably large enough to handle the 80K BTU furnace, but without measuring it you can't be sure.

    You can get the software to do your own calculation for $49 from the HVAC calc website.

    Tiewen Han thanked mike_home
  • 9 years ago
    last modified: 9 years ago

    Guys, thanks a lot for the information! I really appreciate your help. I had a typo in my reply. What I mean is "winter", not "windy". I attached the picture of my addition. The shady areas are small additions adding to the house. We are relocating the kitchen from the front to the back where the bonus room was. The furnace is located in the garage on the right side. My daughter's room is the front room on the left side. It's the biggest bedroom in the house (15x16). I had my house remodeled 4 years ago and all the ductwork was replaced at that time. My contractor at that time told me the room is too big. He even bought in someone using a big box to measure the area flow at the register. He said it was normal. But it's not. My daughter complains every winter that her room is cold. It's frustrating that nowadays a lot of contractors like to make easy money rather than solving problems. They all suggest to replace the whole system, new duct work but I, in fact, already redid the ductwork a few years ago. I guess I have to keep trying. While interviewing contractors for the addition, they all told me that I need a even bigger system and maybe 2 systems to heat and cool the house. I am so confused.

    To answer a few questions that were brought up earlier:

    1) We are at work and kids are at school. During winter time, we just turned off the furnace to save energy. I am wondering if it is a good strategy. Maybe I should keep the furnace on but lower the temp instead?

    2) The furnace is located in the garage (picture below). During the coldest nights here (32C), I feel the furnace turn on every half an hour or so and run about 10 minutes. Is this normal?

    3) As for the system, besides the front room is cold, the air flow seems much stronger at the living room register near the furnace, but weak at the bedrooms. Is this expected? Maybe I have a leak somewhere?

    I originally thought maybe I need to have larger register at the front room. Or simply add another register? The reason is that my master bedroom is just slightly smaller but do not have the issue. I think maybe the extra register at the master bath actually helps?

    4) Last question: since this is hopefully my last remodeling project, should I consider upgrading the furnace to a 95% variable speed 2-stage unit for better comfort? It's cheaper to do it now than later. But if the current furnace is adequate, I would just save the few thousand dollars for something else. Also, if I ever decided to add a AC later, is this furnace good enough to pair with a AC unit?

  • 9 years ago

    Because the additions are not in a single location, it's not really amenable to simply adding a small system to the addition area and moving on. Sounds like you have some serious ductwork/airflow issues too. Unfortunately duct design is not really for the DIY-er - its as complicated (or more so) that accurate heating/cooling load estimation. We can't really solve your problems from a distance so I think you are going to have to find a good HVAC contractor (and it may take several interviews - sounds like the folks you've spoken to so far are worthless) to get a good system installed.

    Tiewen Han thanked sktn77a
  • PRO
    9 years ago

    They all suggest to replace the whole system, new duct work but I, in fact, already redid the ductwork a few years ago.

    Hopefully because their intent was to design a system. Design is many times the difference but often times not explained. It can often be the 'magic' ingredient that makes the system run completely different.

    If you just do a piece meal type repair... like just doing a 'redid' job as already mentioned by sktn77a duct work is complicated. Someone replacing it without duct system design experience can make a mess of a system.

    Often times it's best to relocate the HVAC system. It's typically unlikely a company will do this for old equipment. I don't know if the bids included this or not. So it's hard to say.

    Realize every company out there is competing not only with each other, but also the DIY crowd. If you think that free estimate is really free or a free source of information for you to have someone do it for you after the fact. Uh, no it rarely ever works out like that. (I don't know if this was the intent or not, but it also serves as a warning to those who are reading this.)

    My experience is there to help you do something the right way when you choose me to do the work. If you decide to grow a brain yourself and think you know better than me, I will let you travel that road on your own. Some people get the thought that 'It's my way or the highway' and it is... but this for your own protection, from yourself.

    With that said, there are other companies out there with alterior motives so you must do your homework before you make your decision on who to use to do the work.

    1. I do the same thing. It really doesn't matter as long as the home is kept warm enough to keep the pipes from freezing. Air conditioning and heating is made for your comfort. If you're not there the equation changes. People ask me all the time what temp they should set the thermostat at. My response --- pick a number. Spin the wheel and if you do everything right you might win a prize. (low utility bill.) If you're comfortable that's all that matters at the end of the day.

    2) short cycling. could be a design problem could be a multitude of things.

    3) very common problem - short runs will deliver more air especially if the duct system is unbalanced. In my opinion the best way to balance a duct system is thru design of that system. Others may elect to play with dampers. Problem with damper scenario is that as the season changes from heating to cooling the system will be out of balance again most likely. Remember the HVAC system is for your comfort.... not to sit there and have to play games with it every other season.

    By adding registers you may make it worse. Your system only has so much air, velocity of that air. You add a register and you deduct air from other areas and decrease velocity. This is why you may be looking at needing a complete HVAC system redesign.

    4) I don't know that it gets cold enough in SF area for 95% efficiency furnace. I guess if you like it nice and toasty maybe. But from your post I don't think toasty is your goal. All modern furnaces are at least 80% efficiency. So the difference is roughly 15% from 80 to 95.

    Find your gas bill take your coldest month and subtract this bill from your warmest month. This is what you pay for heat. Now deduct 15% from that and multiply it by number of cold months. That would be best case scenario what you will save via efficiency of the furnace.

    An 80% efficiency furnace can be bought in the variable speed configuration this will give you 2 stage gas function as well. If you were in a colder climate then the 95% might be the better option.

    I think it's more important for you to redesign this system. You should be looking for a pro that specializes in doing this. Your search may be long and hard so make sure you choose very carefully.

    Tiewen Han thanked Austin Air Companie
  • 9 years ago

    Thanks for the thoughtful reply. My intention here is to get a second opinion, not seeking for a free design consultation. Knowledge is power. I don't want to hire someone that's going to make the same mistake. I do know that building something new is easier than fixing the old, just like addition is more expensive than new construction due to the limitation of the existing structure. I guess I will just keep searching.

  • PRO
    9 years ago

    Yeah I understand but this thread will likely be read by others so it wasn't necessarily directed at you.

    Whatever you do you should consult with a provider that has service standards that you can live with. Service is a complex thing and their are variances to the level of service these companies have. The other thing is being able to fix what they service.

    If you had someone who had serviced your system or a repair person that is known for fixing things providing solutions that actually fix problems instead of making things worse or creating new problems then your job would be much easier.

    I know this isn't what you want to hear... but from your experiences so far it sounds like you've been duped before. The only worse thing than that is to get duped again.

    The HVAC business is a tough challenging business. Even tougher if you are looking for a reputable company worthy of their salt.

    Tiewen Han thanked Austin Air Companie