A/C Ducts R6 vs. R8?

9 years ago
Our TX Builder put in R6 A/C ducts, but our inspector says the code for ducts is R8. Is it worth delaying closing on the house to have them redo all the duct work?

Comments (13)

  • 9 years ago
    last modified: 9 years ago

    "Each compliance path may have mandatory, prescriptive, or tradeoff requirements. ... Prescriptive requirements are requirements that either must be met by every building design, or if the requirement is not met, a tradeoff must be made to “make up” for not meeting that requirement."

    If the wood I see is the top of 2×4 ceiling joists, then I would probably opt for more insulation in the ENTIRE attic that would effectively cover and add to the duct insulation as well.

  • 9 years ago

    Where I live, if the house isn't up to code, you can't get a certificate of occupancy. So why would one "close" when one can't inhabit the house?

  • 9 years ago
    JMM1837--
    It looks like all of the new homes in our section have R6. I guess I should have posted the question differently. Perhaps--- "does anyone know a builder loophole that allows for R6 when R8 is code?"
  • 9 years ago
    last modified: 9 years ago

    YES. Central Texan (Austin) weighing in. Code in TX is there for a variety of issues, energy efficiency not the least of it. If the inspector says "nope", stop, get your contractor to fix it and don't look back. Do it now, while it's open and still "fixable" without tearing your walls/ceilings/drywall apart. If you ignore the inspector (and if you have a standard TX Builder's contract) the "fix", when needed, could fall on your pocketbook.

  • 9 years ago
    last modified: 9 years ago

    I suspect that "our inspector" is a private inspector that you hired, and not a city or state inspector.

    "does anyone know a builder loophole that allows for R6 when R8 is code?" - hopefully, my previous post gave you some insight into that. Insulation values are "prescriptive", not "mandatory".

  • 9 years ago

    @Kathy - the mind boggles. A builder ignoring code on not just one house but a neighbourhood.

    Maybe Fred has the best idea (if I understand his suggestion - upgrade the insulation around the R6 and it will meet code).

  • 9 years ago
    Fred S,
    Yes. Thank you for your post! Much appreciated. :-)
  • 9 years ago

    Something also to consider- HVAC, what's the SEER rating? Find that out- important, since the higher the SEER, the more you'll need 8 vs 6- at least.

  • 9 years ago
    @Laurie-
    Thank you. HVAC is SEER 16...
  • 9 years ago
    last modified: 9 years ago

    Now it's time to ask/determine (as you may already know) if these ducts are in conditioned or non-conditioned spaces. Makes a difference. SEER 16 can benefit from either, plus blown in insulation. But the last thing you want is to get stopped at the City inspection level, with something "off". That's a contractor chat.

    Be friendly, but firm. If you have a TX Builder's Warranty, that contractor know that if it goes wrong, (after accepting work) it's all on him, to fix. So what, really? You just want this done right, the first time.

    I'll tell you that for my last build, HVAC was huge in everybody's window- do it right, the first time. I was looking for quiet, energy efficiency. Contractor was looking not to be on the hook for years, within anything that failed, there.

    We worked together, got a great outcome.

    Good luck! Stay strong. It matters, in the end.

  • 9 years ago
    Here's the loophole in this case....
  • 9 years ago
    last modified: 9 years ago

    Yes, that is one of the methods for ensuring that a "tradeoff" is made for the "prescriptive" requirements that I posted earlier. Another is in Section R406.