Which hood is more powerful?

8 years ago
last modified: 8 years ago

I was thinking of a low-profile hood like this until I read the CFM should be cooktop BTUs / 100.

The specs on our oven say 95,500 (NG) is total cooktop BTU. This is our oven: https://www.ajmadison.com/cgi-bin/ajmadison/PRG304GH.html


This is a slide-out hood more powerful than most low profile hoods at 600CFM. It's convertible and we would vent it.

https://www.ajmadison.com/cgi-bin/ajmadison/XOC30S.html


I think the above looks great but it's not at 1000CFM. What's confusing is this is the Thermador 30" hood which is also 600CFM.

https://www.ajmadison.com/cgi-bin/ajmadison/HPWB30FS.html


Am I missing something here? Are these equally powerful? And how is Thermador's hood only 600CFM?

Comment (1)

  • 8 years ago

    Powerful is not the term that applies, or even that gives insight into the hood operation. What hoods are intended to do is achieve capture and containment. Capture is successfully enveloping the rising and expanding cooking plume effluent. What misses the hood is not captured. Containment is successfully removing the captured effluent from the house.

    Capture requires a hood large enough to overlap the plumes. This usually requires a hood that is wider than the cooktop, and deeper (front-to-back) than the burner area. The higher the hood base is located the larger the plumes, and hence the larger the hood has to be.

    Containment depends mainly on the air flow rate of the hood measured in cubic feet per minute -- what you are calling power. Rated flow rate of blowers is generally measured with the blowers in open air (no pressure loss). Once a hood is pulling air through a filter (mesh or baffles) and driving air through some ducting to expel it, and also depending on there being sufficient low pressure loss replacement (make-up) air available, the actual flow rate is significantly reduced.

    At best (without forced make-up air), you will achieve an actual flow rate only 2/3 that of the blower rating. But how much do you need?

    For successful containment of hot greasy plumes from gas stoves rising at up to 1.2 m/s, the actual air flow should be approximately 90 CFM per square foot of hood base entry aperture. Dividing by 2/3 yields 135 CFM per square foot for the rated blower capability. So if your hood is 3 ft x 2 ft, for example, you have 6 square feet of aperture and need a blower rated at 810 CFM (more or less because this is extremely inexact).

    These values are more easily justified with baffle filters, as they maintain the same pressure loss whether dirty or not. With mesh filters, the pressure loss can be higher, and will rise with time due to lint and grease clogging, suggesting not only rigorous and relentless cleaning, but also some boost in the nominal blower flow rate -- perhaps 1000 CFM in this example.

    Describing the relationship of blower free air performance to motor size, blade shape and diameter is not really helpful in selecting a hood, other than to note that quieter blowers for a given flow rate are larger, and are better mounted externally than inside a hood.