webuser_925676996

A/c blows harder before shut off

8 years ago

We moved into this home a month ago so I don't know what's normal for the house.
The a/c blows harder for about 3 minutes before cycling off. I can hear the outside unit work harder too. I would compare it to accelerating your car as it gains "speed" until the moment it shuts off. Cools fine.

Comments (8)

  • 8 years ago

    is it a 2 stage unit?

  • 8 years ago

    Mine is a single-stage, variable fan speed unit. The fan does accelerate after running at low speed for a while. If yours is a 2-stage unit, the compressor will go to 2nd stage especially if it is set to do it via the control board (fixed time after starting in low stage). If it is set up to be controlled by the thermostat, it will go to 2nd stage if low stage is not sufficient to cool down (or heat up).

  • 8 years ago

    Thanks so much for your response. I looked up the model number and it says variable speed. It revs up everytime it's about to cycle off for about 3 minutes. So this is normal? That would be really good news.

  • 8 years ago

    Yes, it can be normal. Mine does this because the thermostat is not controlling the fan speed. The blower/furnace has a 'profile' that it runs for cooling where by it starts real slow, comes up a bit, holds that speed for a while, then comes up to full speed. Normally by this time, the cooling load has been met and it turns off.

  • 8 years ago

    OK, so the air handler is variable speed. Is the condenser (outside unit) 2 speed?

  • 8 years ago

    You may have a 2-stage AC condenser and multi-speed or variable speed blower where the staging is controlled by the furnace control board and not the thermostat. In this set up the AC starts off in the low stage and runs for a set period of time. If the room temperature has not reached the thermostat setting by the end of the time period, the control will move the AC into the high stage. Running in the 2nd stage may only take a few minutes for the room to reach the thermostat setting temperature and then shut down.

    This is normal behavior when the the control board does the staging, but it is not ideal. For best efficiency and comfort the thermostat should control the staging and not the control board.

  • 8 years ago

    "Debes configurar tutermostato asi vas adquirir todos los beneficion de tu sistema sin problemas."

    True, but why in Spanish?

  • 8 years ago

    Thanks again for the replies. The condenser (outside unit) is also a 2 stage power the manufacturer's website. I think the thermostat may be an issue as it is a generic one, from what I can tell for a traditional system, not a 2 stage or variable speed. What prompted me to post was our first power bill was ungodly high so I'm trying to root out the energy vampire in the house. Thanks again for your replies.