Hi all, I own recently installed all electric HVAC unit. Recently I started to smell plastic burn fumes indoors from the air handler and called the company which installed it. Upon arrival when the tech unplugged the unit, it turned out one of the 4 wires in the electric box on the wall was melting. The house is 13 y. old. The electric HVAC unit was installed in the summer. I was fortunate my house did not catch fire. According to the tech ( his wild guess) it was the faulty breaker in the garage which caused high amp draw. Now they ask $740 to replace the box, wiring, and a breaker. My electrician f

riend remotely looked at the issue and is assured it’s a faulty install, not the breaker. Please help, any advice is appreciated. Thank you!

Comments (9)

  • 6 years ago

    he said, you said...get your own electrician to take a look, not a friend...I suspect you are on shaky ground without proof...


    TD

  • 6 years ago

    If the installation was incorrect then the circuit breaker should have tripped and protected the wiring. Your electrician friend needs to come to your house in order to determine the root cause of the problem. A remote diagnosis is not going to work.

  • 6 years ago



  • 6 years ago



  • 6 years ago



  • 6 years ago



  • 6 years ago

    The breaker in the garage did not do this. What
    you see is overheating of the wiring from a bad connection immediately adjacent
    to the melted wire; the original A/C installation technician likely did not
    tighten the connection sufficiently in this disconnect box, if at all. If the garage breaker had
    failed, the heating would be at the garage breaker connection. It isn't. The
    heating comes about by what engineers call I-squared-R heating; the electrical
    draw of the equipment (I, in amps), then squared, times the electrical resistance
    of the connection (R, in ohms) equals heating (in Watts) at the connection.
    When installed last summer, the connection was probably poor (some lower amount
    of R), but it worked. As time went on and the joint was repeatedly heated
    during HVAC operation, the terminal and wires began to oxidize more and more,
    further increasing the resistance (R) and heating of the connection; it's the
    snowball effect. Ultimately, R increases to the point that heating of the
    connection reaches extreme levels and results in what you see now. Why wouldn't
    the tech tell you this? The polite thing to say is that not everyone in
    the trades understands the theory behind what they are doing. Bottom line is
    that the melted wires are from a bad electrical connection immediately adjacent
    to the melting; bad install last summer. But, to get any satisfaction from the
    HVAC company, you may still need a written statement from a licensed
    electrician to prove your point.

    sviatova2000 thanked formulaross20
  • 6 years ago

    Thank you so much!