HVAC Quote-Please Review

6 years ago
last modified: 6 years ago

Does this look reasonable? It includes a load calculation as well. This is for a new custom home . First floor is 1800 sq ft, 2nd floor is 1700 sq ft and the basement is only 1300 sq ft finished. The location is in Atlanta.


Trane XR 16 95% Furnace 16 seer AC Rough Final Total

3 ton Main $6,135.00 $4,090.00 $10,225.00

3 ton Zone Up (1) Master, (2) Up $6,705.00 $4,470.00 $11,175.00

Trane XR14 seer Heat Pump

2 ton Basement Finish $2,370.00 $1,580.00 $3,950.00

Ultra Aire 70H Ducted Dehumidifier w/ Fresh Air $1,600.00 $1,600.00

Fresh Air Vents 4" (2) Main/ Up systems $300.00 $300.00

High Pressure gas design 2 PSI to include: $1,550.00 $1,550.00

(2) Furnaces, (1) Tank less water heater, (1) Cooktop, (1) Fireplace, (1) Fire pit, (1) Pool Heater

*Pricing do not include underground gas line additional fees would apply

* Includes Trane XL 824 Thermostats (3) Honeywell T4 Thermostat (1)

Total $18,660.00 $10,140.00 $28,800.00

Included in base price:

• Venting all bath fans and (1) dryer

• *Gas system installed: Gas line to Furnaces, (1) water heater, (1) log lighter, (1) cooktop or stove

• 1 year labor warranty

• 5 year parts warranty

• 10 year parts (Homeowner online registration required)

Comments (7)

  • 6 years ago

    Well, they certainly aren't doing you any favors. Pricing tends to be regional but you're not in NYC or California!

    What's this:

    "High Pressure gas design 2 PSI to include: $1,550.00 $1,550.00"?

    For that price, I'd want them to register the equipment and provide you with the documentation and throw in a 10 year labor warranty!

    Oh, and get the Trane thermostat, not the Honeywell. There's nothing wrong with Honeywell but if you have problems down the road, that's the first thing they'll blame!

  • 6 years ago

    That's for them to install the appropriate gas lines to serve the following:

    (2) Furnaces, (1) Tank less water heater, (1) Cooktop, (1) Fireplace, (1) Fire pit, (1) Pool Heater

  • 6 years ago

    No this does not look reasonable. If I am reading this correctly the contractor wants to install 8 tons of cooling in a 3500 sq foot new build custom home? Why would you want to install a heat pump if natural gas furnaces are being installed? It he basement is mostly underground and finished then it requires very little cooling. The basement could be a zone off the first floor. I also question the 3 ton sizes for the AC, and no size listed for the furnaces.

    I am skeptical this contractor has done a load calculation. If he has then ask for a copy. I suggest you get two additional quotes. Your first goal is to get a proposal with equipment which is appropriate for you house and location Once you have that then you can focus on the pricing.

  • 6 years ago

    Mike, yes the basement is entirely underground and we have very cheap gas in Atlanta. I’ll definitely get another quote with you suggestion to zone the basement from the main floor unit.
    Thanks very much.

  • 6 years ago

    If you are looking to reduce cost, then consider installing a hot water tank instead of a tankless version. If you spend the extra money on 2-stage variable speed AC condensers, then you probably will not need two dehumidifiers. You should get good humidity control if you have a tight house and the the AC equipment is properly sized and installed.

    I highly doubt you need 3 tons of cooling for the first floor. I think a properly done load calculation will show the cooling load to be less than 2 tons. That is another cost saving.

  • 6 years ago

    Thanks for this, Mike. I will surely discuss this with builder.

  • 6 years ago

    Why is there no mention of an HRV/ERV? This would also be useful with a humid basement and IAC in general.