No heat or cooling

6 years ago

So our blower turns on just fine but the igniter never lights, so no hot air. Also the a/c fan won’t kick on, so no cold air. no matter what settings we change we always just get a lukewarm air blowing into our house.


Any thoughts what could be causing this? Already replaced the high limit switch, and a new igniter is on the way. But that wouldn‘t seem to account for the a/c fan not turning on.


Any thoughts would be appreciated.



Comments (10)

  • PRO
    6 years ago

    So our blower turns on just fine but the igniter never lights, so no hot air. Also the a/c fan won’t kick on, so no cold air.

    which a/c fan? Let's play 101 guessing games as to what is wrong with a complicated system such as an HVAC system?

    I know you probably won't like that statement, but this is the land of 'keeping it real'.


    This isn't part changers express. In order to 'truly' fix an HVAC system it has to be diagnosed. It could be one thing or it could be multiple things. The more you mess with it --- the odds are you make it worse not better.

    The odds mentioned above: Are based on nearly 26 years of actually running HVAC service calls. If I go to a home in which the system is in pieces, it's going to cost that home more to fix it, than if they had just left it alone and called me first.

    You can start guessing which part to change next and be no where near closer to fixing it than when you started.

    I service the Katy, Texas area. (if you live outside my area: called a licensed HVAC contractor... not a fake license: a real one with a number assigned to it!)


  • 6 years ago

    I appreciate the comment, and I agree with the sentiment. That said I have young kids, one with a pre-existing condition and we’re not allowing anyone in our home that we don’t know at this time. So yes, I’m trying to troubleshoot on my own.


    Thank you.

  • 6 years ago

    Thank you so much for the reply. Unfortunately, no luck here as of yet. It’s not just a hot air problem, but cold air too. When set for a/c the fan outside won’t even kick on. No hum either so I’m pretty sure it’s not the capacitor. I tried spinning the blades to kick start it, and no luck.


    Even now the thermostat is set to off and auto (see picture) but room temperature air continues to blow. I was thinking it could be a bad thermostat, but then I should be able to jump start the furnace by connecting the fan and heat wires, and no luck with that either. So that makes me think it’s not the thermostat.


    I’ve exhausted all ideas I’ve been able to come up with. Thanks again.



  • 6 years ago
    last modified: 6 years ago

    This is one of those problems that one of our former members used to call "not internetable." There are so many variables that remote diagnosis is impossible.

    If you're a good troubleshooter, try to find an installation manual for your furnace online, and examine its control hardware for clues. If you don't have that kind of background, and you can't bring in an experienced service person, I'm afraid that you're more or less lost at sea.

    Where I am, the weather right now is such that heat isn't necessary. Some nights it might get a little cool in the house. So you put on a sweater, and add an extra blanket to each bed.

    Depending on where you live, you might be able to put off a service call for another month or two. Probably longer, if you haven't forgotten how to open windows and turn on fans when the weather gets hot in summer. :\

    If you absolutely can't live without heating and cooling, plenty of online merchants will ship you electric space heaters and window air conditioners. Make sure you distribute them evenly on different circuits, but don't use extension cords if you can possibly avoid it.

    EDIT: Oil filled radiator style heaters are relatively safe, compared to other types. I have several friends in Europe whose houses have no central heat at all. Radiator style portable heaters are their main sources of heat, at least when they aren't using their woodstoves.

  • 6 years ago

    Thanks David. I think we’ll just have to get by for now. We’re in California and a week ago it rained for about a week straight, pretty cold nights for the kids. But of course NOW it’s 90+ degrees so windows and fans are doing the job. Thanks for the advice.

  • 6 years ago
    last modified: 6 years ago

    Do you have a voltmeter? If you do I would check the thermostat wiring terminals at the control board. The blower works then so that means the G terminal is energized. The Y terminal needs to be energized for the AC, and the W terminal for heat. If you are not getting 24 VAC on those terminals then it is a thermostat or wiring issue.

    If you are seeing 24 VAC at the Y and W terminals, then the next suspect would be control board. The question is why would a control board suddenly stop working? Was there a recent electrical storm or power glitch?

    You should also check all circuit breakers .

    HU-528683068 thanked mike_home
  • 6 years ago

    Hi Mike, thanks for the advice. The a/c is back up and running. In fairness I disconnected that a couple days ago at the terminal and never reconnected it. So that was a dumb fix.


    But I played around with the multimeter as you suggested. when the a/c is on I get 24 VAC on the Y, R and G terminals.


    when running the heat I get 24 VAC but only on R and W. No reading on G, although the blower continues to run.


    I’d say it’s clear I’ve got a bad G wire, but it works ok with the a/c? Any thoughts?

  • 6 years ago
    last modified: 6 years ago

    Assuming a fairly normal thermostat, with typical forced air gas furnace and air conditioner:

    If you have a C (black wire) at the thermostat, put one probe of the meter on that for the following tests:

    You should measure 24 volts on R at all times.

    You should see 24 volts on W when the thermostat is calling for heat.

    You should see 24 volts on Y when it's calling for air conditioning.

    G should be at 24 volts when the fan switch is on.

    If you don't have a black wire at the thermostat:

    You should read 24 volts between R and W when the heat is OFF and 0 volts when the heat is on.

    You should read 24 volts between R and Y when the air conditioner is OFF and 0 volts when the air conditioner is on.

    Disconnecting the thermostat and jumping red to white should turn on the heat.

    Disconnecting the thermostat and jumping red to yellow should turn on the cool.

    Do NOT jump red to black or blue.

    The connections may be different for a heat pump. In that case, find out what you have, look up the installation manual on the net, and go by that for your tests.

  • 6 years ago

    Well damn. I think I ruled out the thermostat being the issue. Can’t even jump R to W. Cannot get the heat on at all.


    but the blower still runs Just by holding The button for the door down. And this is even with the thermostat completely disconnected.

  • 6 years ago

    Also have a blinking error light which means “no call for heat”