From Oil Heat/AC to Heatpump/Air Handler

6 years ago
last modified: 6 years ago

We are getting quotes to convert our HVAC system for oil heat/AC to heatpump/air handler. We are in Washington DC. Heating and cooling loads are 32,500 and 19992 respectively (Done independently. Big companies claimed to have done a load calculation but will not share with me till I sign with them). It's a semi attached townhouse with finished basement, 1st level (living room, dining room and kitchen) and 2nd level (four bedrooms and two bathrooms). Sq feet of first and second levels is about 1408. Most of them are not variable speed which from my search, is often recommended on this board. Thank you.


Solo Tech (One man Business)

American standard ($6000)

1- 4A6H4036G1000A

1- TEM4A0C37S31SB

1- BAYHTR1510BRKC


TRANE SYSTEM ($5,500)

1- A4HP4036A1000A

1-A4AH4P36A1B30A

1- BAYHTR1510BRKC


LENNOX SYSTEM (5000)

1- ML14XP1-036

1- CBA25UH-036

1- ECBA25-10CBRKC


RHEEM SYSTEM ($4500)

1- RH1V3617STANJA

1- RP1436AJ1NA

1- RHBA25-10ABRKC


BIG COMPANY A

CARRIER(16 SEER HIGH EFFICIENCY) ($9874)

Heat pump: Carrier 2.5 Ton (25HPB630)

System Features

• System package rating 16 SEER(16 SEER/13 EER/9 HSPF)

• Environmentally friendly R410a refrigerant

• Energy Star Rated

• Sound levels down to 67db

• Single stage scroll compressor

• Heavy gauge steel construction

Air handler: Carrier 2.5 Ton(FV4CNF005)

System Features

• Variable speed blower for improved comfort and quite operation

• All aluminum coil for enhanced corrosion resistance

• Ultra low power consumption

• Improved humidity control

• Includes electric strip heat

• Fully insulated cabinet (provides quieter sound)


BIG COMPANY B

American Standard ($6600)

2.5 Ton 14 SEER Heat Pump 4A6H4030G1000A/TEM4A0B30S31SB

Mechanical-Lineset, Drain, Electric, Control Wire

Lineset Replacement 3/4-3/8 Drywall Excluded

5 Year Labor Warranty

10 Year Limited Manufacturer Warranty


Goodman ($6900)

14 SEER 2 Ton Heat Pump GSZ140241/ ASPT25B14/ HKSC10XC

Mechanical-Lineset, Drain, Electric, Control Wire

Lineset Replacement 3/4-3/8 Drywall Excluded

5 Year Labor Warranty

10 Year Limited Manufacturer Warranty

Comments (49)

  • 6 years ago

    Thank you. Not sure how my response disappeared. We just want to get rid of oil heat and not have to deal with it anymore. Except, we have to figure out how to get the tank out of the basement as non of the contractors above would do it.

  • 6 years ago
    last modified: 6 years ago

    Big Company B's quotes including moving around breakers in our panel to make space for the new system. Which of their quotes should I be leaning towards? What things should I make sure that the quotes include or is there a system you recommend? Thanks.

  • 6 years ago
    last modified: 6 years ago

    You size a heat pump to the cooling load. None of your quoting dealers are doing this. What is size of your current AC and how did it perform as far as cooling your townhouse. What size heat strip are dealers quoting? i assume your quoting dealers have checked your electric service. You will also require a new HP thermostat. I prefer correct size American Standard. Post back.


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    If the cooling load load really 20,000 BTU, then a 2 ton AC would be sufficient. That is what I would expect for a 1400 sq foot semi-attached townhouse in DC. If it is an old structure with marginal windows then installing a 2.5 ton AC would still be reasonable. A 3 ton is over sized and should be avoided in my opinion.

    I like what Company B has quoted. They are going to replace the line set, and offering a 5 year labor warranty. What I don't like is they have quoted 2 ton and 2.5 ton sizes. That makes no sense.

    As for Company A, I don't see the point of spending a lot of money on a variable speed air handler and then installing a single stage condenser. Does a 16 SEER system qualify for a rebate or tax credit in your area?

    Family of Girls thanked mike_home
  • 6 years ago

    Thanks. We currently have a 2T. However, we've had window ACs in our bedrooms and sometimes in the sitting room for over 6 years so I guess that means it's not been cooling very well for a while. Now, it comes on but blows more like a fan than an AC. @Tigerdunes, Company B’s Goodman quote is with 10kw heatstrip. Not sure what size heatstrip for the AS quote. Company A has not responded to any of my follow up inquiries which means they’re probably too busy to bother. @Mike Homes, most of our neighbors have 2.5T and one has a 3.5T.

  • 6 years ago

    Given our heating and cooling needs, what American Standard or other models should I be on the lookout for or ask for a quote on?

  • 6 years ago
    last modified: 6 years ago

    What are the BTUs on your window units? You run them all the time?... I suspect your cooling load is not correct. How old is existing AC? Do you plan to be in TH for the foreseeable future? I’ll come back on a recommendation later today.


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    Where the bedrooms in relationship to the air handler? Many times the issue is leaky and undersized duct work and not the size of the AC. If your duct work is in an unconditioned attic then it should be thoroughly inspect and fixed as needed. If the duct work is marginal at 2 tons, then trying to force 3 tons of air flow is not going to work. If the the neighbors have the same townhouse then ask if their bedrooms are comfortable with the 2.5 ton AC. I would be concerned about going larger than 2.5 tons.

  • 6 years ago
    last modified: 6 years ago

    Company B is providing better quality Carrier components ("Performance" series condenser and variable speed FV4 air handler) but not $4000 better! I think you would be best suited with a 3 ton 2 stage heatpump and a variable speed air handler. The low stage is a little over 2 tons and the second stage is 3 tons. It also sounds like you may have a duct performance issue if your current system isn't cutting it on the top floor (bedrooms).

  • 6 years ago

    better quality?...sorry but I must disagree...the TRANE HP condensers are every bit as good as the Carrier except for efficiency and the matching var speed air handler...the $4k upcharge is ridiculous...for a two story TH, I think a sgl stage HP with fixed speed air handler with high eff blower motor is the way to go. Plus you get demand defrost with the Trane/AS which eliminates/reduces unnecessary defrost calls which are expensive and add to wear and tear...i would go with Trane or AM Standard 15 SEER HP model with fixed speed high eff air handler.


    TD

  • 6 years ago

    We have a 5000 BTU in the mb and in the kids bedroom on the 2nd level. We also an 8000 BTU on the main level. We run the ACs all the time now since the central AC was turned off cos it was not cooling. The air handler is located in the basement two levels below the bedrooms. The upper level ductwork is the crawl attic which has adequate insulation per an energy audit performed some years ago. The duct work for the main level is on the floor b/w the basement and the main level. @TIgerdunes, are you recommending not to go with a variable speed air handler as is your usual recommendation? Thank you.

  • 6 years ago
    last modified: 6 years ago

    Hello. The Goodman quote was a mistake and should have been a 2.5T. Any AS model recommendation? @Tigerdunes, “fixed speed air handler with high eff blower motor is the way to go”. That means you’re departing from your usual variable speed handler recommendation? May I ask why? Also, which model numbers should I ask for? Thanks.

  • 6 years ago

    Try Craigslist for oil tank removal.

  • 6 years ago

    "better quality?...sorry but I must disagree..."

    Perhaps "quality" was the wrong word. The "Performance" series is Carrier's mid/higher end series below their top of the line Infinity series - 2 stage, compressor blanket, filters, hi, lo pressure switches, etc, etc. Would be my choice if the price were more realistic. Demand defrost is nice to have.

    You pays your money, you takes your choice.

    Family of Girls thanked sktn77a
  • 6 years ago

    I'm still waiting for recommendations. Pretty Please?

  • 6 years ago

    Heat pumps are sized for AC cooling. I am confused about the correct AC sizing for your townhouse since you are running window units. I think your load calc for cooling offered by one of your quoting dealers is highly suspect. I would recommend AmStd Silver 15 Heat Pump with best matching fixed speed air handler that has high eff blower motor.. if cost is not a factor and you plan on living there for the foreseeable future, then the var speed air handler model. New HP thermostat. Heat strip. New refrigerant lineset. Work with the AMStd dealer you’re most comfortable with.


    TD

  • 6 years ago

    What’s HP Thermostat? We currently have a Nest thermostat, can we use that?

  • 6 years ago
    last modified: 6 years ago

    You need a heat pump thermostat for a new heat pump. Your existing AC thermostat will not work....They are not expensive. They are available in programmable or non programmable.


    TD

  • 6 years ago

    do you have a return on each floor? How are you filtering your return?

    Here are my recommendations. I still have questions though about your cooling load. I do not like the idea of using window units.


    AMStd Silver 15 HP 4A6H5


    Air handler GAM 5 high eff

    TEM 6 var speed


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    There’s a return on floor 1 and floor 2 but none in the basement. Another tech said we needed 2.5T Heatpump and 3T air handler. The window ACs will be removed once a new system is installed. Thanks.

  • 6 years ago

    Probably a 7.5 KW or 10 KW heat strip. Quoting dealer should check your breaker box for capacity. Air handler, HP condenser, and heat strip to be on separate circuits.


    TD

  • 6 years ago

    We were told we need about 60A for the new system and that they can move things around to get enough capacity. I tried finding an AHRI match for a 2.5T Silver 15 and a 3T Tem 6 but could not. Could I be doing it wrong? Thanks for your help.

  • 6 years ago
    last modified: 6 years ago

    I will check on matching number and come back later today....

    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    How do you filter your returns?


    here are the AHRI matching numbers.


    Am Standard AHRI matching numbers for 2 1/2 HP 4A6H5030H


    GAM5B0B30M21EA 15 seer ahri # 9033754 fixed speed
    TEM6A0B24H21SB 15 seer ahri # 9033755 var speed

    AHRI number 9033756 shows 4A6H5030H model instead of E model. VAR speed


    my choice would be the 54 or the 56.


    you should get better dehumidification in AC cooling with the var speed air handler


    TD


  • 6 years ago
    last modified: 6 years ago

    Found them. Thanks. Does this mean that there’s no AHRI match up for silver 15 2.5T and TEM6 3T?

  • 6 years ago

    I did not see a matching number for TEM 6 036 ...I would not be concerned....

    Family of Girls thanked tigerdunes
  • 6 years ago

    Thanks. So 2.5T air handler will be adequate?

  • 6 years ago

    Sizing is your responsibility. I have doubts about the accuracy of your load calc especially for cooling. I suggest you discuss this with dealer. dealer should also check size of your refrigerant lineset. What size outside condenser do your neighbors have on a similar TH?


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago
    last modified: 6 years ago

    Most neighbors have 2.5T. Not sure what size their inside units are.

  • 6 years ago

    A size of 2.5 tons for a semi-attached 1400 sq foot townhouse in DC would seem reasonable. Going to 3 tons seems over sized, and 2 tons would probably work, but it might be marginal on a 95 degree day. If you have a choice within the matches , then I would go with a 3 ton coil.

    Family of Girls thanked mike_home
  • 6 years ago

    Thanks. To get an AHRI match with TEM 6 3T, we would have to go up to a 2.5T Silver 16.

  • 6 years ago
    last modified: 6 years ago

    I think 2 1/2 ton size is correct...as stated previously, I have reviewed AHRI Directory again and there is not a matching system in the 036 (3 ton) air handler either in the GAM5 or TEM6 air handlers...the 030 is your best choice for a 2 1/2 ton Silver 15 HP.

    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    Thank you for your patience. What else should I make sure they include in our install?

  • 6 years ago

    Is current AC condenser R22 or R410 refrigerant? Refrigerant lineset should be checked for size and condition. If reused, it should be flushed out according to standards. I asked about how your return air is filtered, no answer. Good HP thermostat programmable or non programmable. I would want condenser placed on concrete pad. 7.5 KW or 10 KW heat strip, breaker box to be checked for capacity. I like to place condenser, heat strip, and air handler on separate circuits. Check ductwork for sizing; generally for a 2 1/2 ton system, you want a minimum of 11-1200 CFMs for both supply and return...


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    I suggest if possible replacing the line set. If it is not replaced then it has to be properly flushed if the you are going from R-22 to R-410A and it is the proper size (diameter). Ideally a 4 inch media filter, programmable thermostat, new pad for the condenser to sit on, parts and labor warranty, the sized of the heat strips, and the required permits. If the air handler is going to be in a place where condensate overflow will cause water damage to the house, then a condensate overflow alarm (shutoff) should be included.

    Family of Girls thanked mike_home
  • 6 years ago

    Thanks. To answer your question, "I asked about how your return air is filtered, no answer"

    I'm not sure I understand the question but there is a return on floor 1 and floor 2 but none in the basement. There is a filter located in the lower part of the oil furnace. That filter has not been changed in a very long while. @mike_home, the air handler will be located in the basement on concrete floor, less than two feet from the sump pump. Will we still need the overflow alarm shutoff?

  • 6 years ago

    Discuss Return filter cabinet with dealer, probably at air handler with good access. will air handler be located in basement?


    TD

    Family of Girls thanked tigerdunes
  • 6 years ago

    Yes, it will replace the oil furnace in the basement

  • 6 years ago

    If the air handler is not near any part of a finished basement, then it is not necessary. I assume the PVC drain pipe will flow into the sump pump. I like the clear EZ trap so you can visually see any debris. It has plastic caps which can be opened for easy cleaning.


    Every forced air system has to have at least one filter. In some cases the filer is located at the return grille. In other cases it is located where the return enters the furnace or air handler. In your case when they remove the oil furnace they will install the filter at the air handler. Filers come in many sizes. A 4 inch filter means it is 4 inches thick. A 4 inch thick filter does a better job of filtering and lasts longer than a 1 inch thick filter. If the space allows ask for a 4 inch filter. For a 2.5 ton system the filter should be 16 X 25 inches or an equivalent area. Bigger is better when it comes to filters. You need to be checking the filter on a regular basis. Whatever they install, it needs to be easy for you to check yourself. Replacing a filter should not be a difficult task for a homeowner.

    Family of Girls thanked mike_home
  • 6 years ago

    Whatabout a humidifier. We have an Aprilaire 500 we bought some years back but never used. Can we still use it or is it obsolete? Thanks.

  • 6 years ago

    I would take some humidity readings on both floors before I installed it. Why was it never installed?...

    Family of Girls thanked tigerdunes
  • 6 years ago

    We bought it in preparation for a Heatpump install some years back but we never did so it’s been sitting around since then. We do have a dehumidifier in the basement.

  • 6 years ago

    Of course you will need to make plans for decommissioning the oil furnace, tank, leftover oil, etc....

  • 6 years ago

    I would avoid installing a humidifier and only do it as a last resort.

    Family of Girls thanked mike_home
  • 6 years ago

    Last resort? I don’t understand.

  • 6 years ago

    Low humidity in the winter is due to leaky windows and doors. The cold dry air enters the house, and then is heated which lowers the humidity. You are better off making the house tighter than running a humidifier 24/7 to make it comfortable. Humidifiers need to be maintained and cleaned on a regular basis.

    Family of Girls thanked mike_home
  • 6 years ago
    last modified: 6 years ago

    Thanks. Is the 4” media filter the same as return filter cabinet? What thermostat and media filter cabinet do you recommend?

  • 6 years ago

    The cabinet is the rectangular box which holds the filter. The size of the filter and the box is determined by the air flow the air handler needs. You should be able to get the air handler's matching cabinet (Trane, Carrier, etc.), or you could get a third party cabinet from Aprilaire. Whatever you get you want to make sure it is easy for you to check and change the air filter as needed.

    You should get a programmable thermostat that is compatible with a heat pump and auxiliary heat strips. Honeywell makes several touch screen thermostats. I don't think you need to spend the extra money on a WiFi thermostat unless you have a need to control the temperature when you are not home. Installers typically want to install the same thermostat in order to not have to read the installation manual Find out what model they are proposing and we can look up the features to see if it is appropriate.

    Family of Girls thanked mike_home