Heatpump Single Stage vs Two Stage

5 years ago

Replacing a 19 year old 2.5 ton Rheem Heat Pump and air handler. Live in a two story 2,100 sq ft home in New Jersey. I've received some 3 ton single stage solutions along with two stage solutions with variable speed handlers. It sounded like two stage would afford better humidity control and increased comfort. BUT, I was also told (not by the contractors) that depending on the duct work the two stage solution could actually be a worse choice as it may not push enough air to the upstairs. Was also told that if we were happy with the 2.5 the 3.0 single stage without appropriate analysis potentially could be too big and cause short cycling. And that both the two stage and 3.0 (if too big) could actually be louder in the house which isn't all that welcome. Hopefully I've conveyed what I heard accurately


Any insights would be appreciated.

Comments (17)

  • 5 years ago

    Single-stage: Lower equipment cost, less likely to break, low repair cost, low to average efficiency and high electricity cost


    Two-stage: Moderate equipment cost, less likely to break, low to moderate repair cost, good to excellent efficiency and average electricity cost


    Variable capacity: Higher equipment cost, more likely to break, moderate-to-high repair cost, excellent efficiency and low electricity cost

    Variable-capacity heat pumps and ACs are also called “modulating.”


    In general, as performance goes up, cost and efficiency go up. The cost to run the AC or heat pump go down.

    dp ag thanked Franco Oyuela
  • PRO
    5 years ago

    Two stage is better as it will be more energy efficient and low maintenance with higher performance.

  • 5 years ago

    A 2.5 ton AC for a 2100 sq, foot house in NJ seems marginal. Are you able to maintain a 75 degree indoor temperature when the outdoor temperature is in the upper 90's like it is today? If so then the 2.5 ton is the correct size.

    The 3 ton 2-stage may give you better humidity control. If you have trouble maintaining a 50% humidity level in the summer, then consider getting the 2-stage AC. Most 2-stage AC operate at about 70% capacity in the low stage. This means the 3 ton would be at about 2.1 tons in the low stage. This is not much mess than your current system. I would not be concerned about not being able to push enough air. The contractor also needs to verify the duct work can handle the extra air flow required for 3 tons of cooling.

    If you live in are near Mercer county I can recommend the Carrier dealer who installed my equipment. He will do a load calculation to verify the sizing and offer several options of equipment.

  • 5 years ago
    last modified: 5 years ago

    Able to maintain 70 or 72 downstairs with a 5 - 7 higher temp upstairs. Humidity mid 50s to 60s. Can maintain 68 in the winter but system runs much more in cold temp. I'm in Burlington county. I've had one contractor perform manual J and confirmed 2 1/2 ton. I've had three other contractors come in without calc (to my knowledge) and state 3 ton would be better for my home.

  • 5 years ago

    Based on your experience and the Manual J calculation the 2 1/2 ton is the correct size. I am surprised the humidity level is as high as you state. What are you using for a humidity gauge?

    It is difficult for a single system to maintain even temperatures on both floors for a house of your size. You are not getting enough air flow to the second floor. Have you tried closing any of the vents on the first floor? How much insultation is in the attic? You should have at least R-30.

  • 5 years ago

    Current status upstairs (see attached)


  • 5 years ago

    Current status downstairs (see attached)


  • 5 years ago

    Yes, closed vents in room where downstairs thermostat is located. Have insulation in the attic (blown in) but don't know what the R value is.

  • 5 years ago

    Closing off the vents downstairs should help but may produce whistling noises as the air leaks past the vanes. Do you have dampers on the ducts where they come off the main trunk? closing them off would be more effective by producing additional resistance to airflow to the downstairs rooms (and conversely pushing more air upstairs). You would need to reverse this in the fall/winter.

  • 5 years ago

    Do you have a basement? If so what is the temperature and humidity level in the basement? You may need a dehumidifier in the basement to help lower the humidity level.

  • 5 years ago

    Don't believe I have dampers. Let me ask you this. If I decided on single stage (forget two stage) , could a 3 ton really cause any issues? I realize bigger isn't always better but I'm thinking (layman here) that the increase would be more positive than negative and this is the one opportunity I have to "enhance" what I have now. Wondering since I'm not looking to increase size dramatically it would probably be fine?????

  • 5 years ago

    No basement, on a slab

  • 5 years ago

    You first have to determine if the duct work can handle the additional air flow. If it can't it will be hear more air noise. The run times will be shorter which could cause a higher level of humidity.

    dp ag thanked mike_home
  • 5 years ago

    Thanks, I just measured the duct work that the air handler goes into and it's 20 x 8 rectangular. From what I can find that's 750 cfm (I think). Would those dimensions stand for the entire house? Anything we can take away from this?

  • 5 years ago

    Also, Return downstairs 30 x 6 (a lot of air moving)

    Return Upstairs (23 x 9) won't hold a piece of paper but there is some air moving - not sure if this is normal.

    There is a 2nd return downstairs approx 14 x 11. Rather odd, I feel some air moving but don't see that there is any ductwork it's connected to. This ls located as follows: Air handler | Wall | Open cavity | Return Vent.

  • 5 years ago
    last modified: 5 years ago

    The problem isn't the size of your heat pump, it's the ductwork. If a 2.5 ton otherwise works fine, I wouldn't get a 3 ton (single stage) - dehumidification will suffer and it will be noisy 100% of the time (as opposed to, maybe, 10%of the time with a 2 stage).

    dp ag thanked sktn77a