Back Guards on Pro Ranges / Rangetops (eg: BlueStar) vs Consumer Grade

last month

Hi, all..considering the Blue Star Range (or more likely, Range Top) and am seeing some wildly conflicting info on Back Guard requirements.


I've called Blue Star to ask directly, but not easy AT ALL to get ahold of anyone who can answer as they say Tech Support is only for Installers, so am reaching out here also.


Range/Rangetop would be 30'' and installed directly against kitchen wall (ie: 0 clearance). It would appear from the Install instructions (which I've read many times, front to back) that you can use ceramic tile above (which we have) and below (which we'd need to add) for 6'' on top of a drywall/wood stud wall and be in compliance.


I've seen many older threads here disagreeing with that take, and telling people to either use the 6'' min steel backguard or tear apart the wall to rebuild with steel studs and cement board (crazy!) But if we read the CURRENT install requirements, they clearly say..


"When a unit is installed with any other back guard in a zero clearance condition, noncombustible/heat resistant materials are to be used in a vertical plane for a minimum distance of 6” below the top horizontal plane of the unit and at least equal in height to the back guard being used.


The non-combustible material need not extend horizontally past the initial barriers thickness. The initial barrier should consist of materials such as ceramic tile, cement backer board, stainless steel (.032” Thick) or other non-combustible material"


So, am I right in thinking the specs have been updated by BlueStar at some point after all the initial discussion here about steel stud/cement board walls, etc?


It would sure appear to be so.


BTW, I've seen the discussion about Mechanical Codes. But there does not appear to be ANYTHING in those codes that are specific to BTU output requiring the "minimum distances" documented. So, that would mean NO RANGE could be installed without a backguard/steel stud walls, etc. However, there are plenty of ranges as we all know that can, and the install docs for those ranges say absolutely nothing about not being able to install with zero clearance to rear wall without a backguard.


Strangely, some of those ranges (eg: GE Cafe Gas 30'') have similar rear burner BTU output to a BlueStar RCS or RNB 30''. The GE is 26.5K across all 3 rear burners on the six-burner range and the BlueStar RCS & RNB are both 24K total across the 2 rear burners. Yet, GE doesn't even MENTION a back guard, even though it's higher rear BTU.


Incidentally, the Thermador 30'' Dual Fuel also does not mention backguard requirements even though it's open burner (star burners) as well.


I've read the pyrolysis discussions, but it would appear from the BlueStar install doc specs that they are saying this is not an issue with 6'' of ceramic tile over drywall vertically above and below the cooktop surface.


Bottom line - the 6'' backguard is ugly and would cover a good amount of a backsplash design we currently have, and look ridiculous. So for that reason, I strongly want to avoid it if 6'' of ceramic tile vertically above and below burner surface will suffice, as it appears the docs indicate it will.


Appreciate any/all takes.


Thanks..



Comments (18)

  • last month
    last modified: last month

    Rangetops

    Page 12 of the Installation Guide is clear. You need a backguard. And the distance between the appliance and the rear wall determines whether or not the rear wall must be non-combustible.

    The Cafe spec sheet has a similar requirement.

    And there's Miele:

    • Please observe safe distances to rear combustible surfaces of 12" (305 mm) clearance. For zero clearance installation the Miele Backguards will satisfy the required distance to combustible surfaces. The Miele Backguard is available in 12" (305 mm) or 20" (508 mm) heights.


    Tile is a protective surface but tile over drywall does not create a non-combustible wall.

  • last month

    My take…better to be safe, than sorry, especially with a powerful Bluestar. Just install steel studs and the fireproof cement board. End of.

    In most instances, the concern is with heat coming through the rear vent of a range/ stove…especially when quartz is used as the backsplash. Rangetops, don’t have the rear vent, so there’s not usually a concern. However, I imagine there might be a concern if you use the rear burners on a high BTU Bluestar.

    Even though my rangetop is a lesser BTU Thermador…and, I was putting in a ceramic tile backsplash, my contractor still installed steel studs and fireproof cement board in the wall behind the rangetop. I’m grateful for his cautionary approach.


  • PRO
    last month
    last modified: last month

    I've got the 30" 6 burner Cafe range arriving tomorrow. From my read, it comes with a 7/8" spacer that's required to be installed behind the oven vents, but that's the only restriction on putting it against a combustible wall. In my case, the wall it's going against is tiled for 20" above counter height and 3" below in the range cutout (but I assume it's just drywall and wood studs behind the tile, I didn't put this wall in).

    The most powerful individual rear burner on the Cafe is only 12k BTU, compared to 15k for the Bluestar ranges. And the Cafe has more distance between the rear burners and the back wall, as the front to rear burner spacing is a little closer.

    Plus the oven vents are done differently. It's hard to tell in pictures where the oven vents exhaust on the Bluestar without one of the taller backguards.

    On the Cafe, the oven vents are right behind the burner grates pointed upward (and likely part of the reason for the extra trim spacer to keep them further from the wall, plus the spacer is slotted so some cooler air will likely be drawn up through it via stack effect to cool the air flowing up the wall).

    Most likely it's some combination of the burner to wall distance, more powerful rear burner on one side and oven venting considerations that drive the Bluestar requirements.


    EDIT: The 36" Cafe rangetop that was mentioned to have a similar clearance requirement to the Bluestar is one of the Cafe commercial style units. 2 of the 3 rear burners on it are 18k BTU, plus it's a rangetop, so no oven vents behind the burners (leaving the burners a bit closer to the wall). Those differences adding the clearance requirement seem to support that it's a combination of higher heat from a single point, and heat sources too close to the rear wall that are driving the requirement.

  • last month

    The requirement that the code enforcement officer will want to see complied with is the one in the installation guide. Why do some guides allow lesser installation conditions than the IMC implies are needed? Presumably because the manufacturer had UL or equivalent test the unit under various conditions and evaluate the resulting wall temperatures. Most codes allow for engineering evaluation to supersede general requirements. But the code enforcement officer has the last word.

  • last month
    last modified: last month

    @kaseki - except the installation guide doesn't say what some here seem to think it says.

    I read it many times (having also written & reviewed very large, complex contracts for a living & dealing as a result with precision of language), and it CLEARLY says to me that ceramic tile 6'' above the plane of the cooktop and 6'' below DOES MEET install requirements.

    Here's the relevant language from the Install Doc:

    "The non-combustible material need not extend horizontally past the initial barriers thickness. The initial barrier should consist of materials such as ceramic tile, cement backer board, stainless steel (.032” Thick) or other non-combustible material" .

    Emphasis: NEED NOT EXTEND HORIZONTALLY PAST THE INITIAL BARRIERS THICKNESS (where the initial barrier can be ceramic tile). Ergo, the composition of the wall (which for most people will be drywall and wood studs) beyond a layer of ceramic tile is not relevant.

    I suspect this language has been clarified in recent years and that the opinions of some who believe you need a minimum 6'' steel back guard or steel stud / cement backer board walls was formed prior to the Install Docs being made more clear.

    I have a call into BlueStar to confirm, but as many of you know, they're not really setup to answer pre-sales questions and it's been like pulling teeth to get confirmation.

  • PRO
    last month

    That wording from Bluestar makes me think their concern is more about short-term high heat events (like a pan fire) that might rapidly set a combustible surface on fire. And not so much about long term heating (like from the oven vents) getting things too hot and damaging the structure of the wall.


    As a reference point, I just ran the oven break in on my new 30" Cafe range. The range is pushed back against the tile backsplash with the provided 7/8" trim piece installed behind the oven vents. After 45 minutes at 400* the tile right above the oven vents was just barely warm to the touch, I'd say not over 100* F.

  • last month
    last modified: last month

    I don't know what you are reading or why you are calling Bluestar. Page 12 of the Installation Manual for Bluestar Rangetops is clear:

    • All rangetops require a backguard. Most models have the option of using: grate height trim; island trim; 6” inch standard; 17” inch hi-back; 24” inch high shelf.
    • If you are using an island trim or grate height trim, a six inch clearance between the back of the rangetop and a combustible surface is required. If an island trim is to be used without this six inch clearance, the back wall must be constructed using non-combustible and heat resistant materials that extend below the top surface of the range a minimum of six inches.


    You want to use the grate height trim because, you wrote, "the 6 [inch] backguard is ugly and would cover a good amount of a backsplash design we currently have, and look ridiculous. So for that reason, I strongly want to avoid it"

    Therefore you either need (a) the six-inch clearance or (b) a "back wall...constructed using non-combustible and heat resistant materials".

    Ceramic tile over drywall is NOT "non-combustible and heat resistant".

  • last month
    last modified: last month

    @wdccruise did you read my reply to @kaseki?

    The install doc for the Range (not Rangetop) clearly says on page 8 that the Range can be installed in a zero clearance if non-combustible/heat resistant materials are used in a VERTICAL PLANE for a min of 6'' below and 6'' above cooktop surface.

    Then goes on to say..

    THE NON-COMBUSTIBLE MATERIAL NEED NOT EXTEND HORIZONTALLY ***PAST THE BARRIERS THICKNESS**. The initial barrier should consist of materials such as CERAMIC TILE, ...

    Since the non-combustible material can be ceramic tile and NEED NOT EXTEND horizontally past the barrier's thickness, the construction of the wall is not relevant.

    THAT is why I am reaching out to Bluestar.

    Because I have a completely different read on this than you do.

  • last month

    And ceramic tile IS non-combustible and heat resistant (not that it matters as the BlueStar docs specifically list it as an acceptable material) that does NOT need to extend "horizontally pasty the barrier's thickness".

    Yes, ceramic tile is considered fireproof, non-combustible, and highly heat-resistant, as it is made from natural clays and minerals fired at high temperatures. They will not burn, melt, or release toxic fumes, making them ideal for kitchen backsplashes and fireplace surrounds.

  • last month

    @retiredinmi I think what is going on here is that there are different installation manuals. I bought a Bluestar Platinum range 8 years ago and it appears the installation instructions have changed.


    First link does not say anything about extending horizontally. This is the installation manual that was around when I purchased my range. Second link must be what you are referring to and the newer manual.


    https://www.bluestarcooking.com/wp-content/uploads/2016/02/FreeStanding-Range-Installation-Manual-750163-1.28.18.pdf


    https://www.bluestarcooking.com/wp-content/uploads/2019/03/BlueStar-FreeStanding-Range-Installation-Manual-750163-Rev3.28.19.pdf?utm_source=chatgpt.com

    retiredinmi thanked Clyde Kalvin
  • last month

    @retiredinmi

    I think your point made after my last message is consistent with what I wrote; if the testing has been performed and the implications of the results allow a lesser wall construction to meet safety requirements vis-a-vis wood degradation due to heat, inter alia, then the manufacturer can write requirements such as tile is good enough.

    Conceivably, an oven could be so well insulated that hot air rising up the back was tepid and no special precautions would be needed, other than for resisting pan flambès.

  • last month
    last modified: last month

    @retiredinmi Yes there is contradicting language. From reading the new manual clearance section it appears you are correct. If you used island trim as long as the back of the wall is covered in non combustible tile 6 inches below horizontal plane and 6 inches above you should be ok.

    Reading the newer manual my range installation would not be correct. It was at the time.

    When a unit is installed with any other back guard in a zero clearance condition, noncombustible/heat resistant materials are to be used in a vertical plane for a minimum distance of 6” below the top horizontal plane of the unit and at least equal in height to the back guard being used.

    I have the 24 inch backguard with shelf. My back wall is log as it is a log cabin. It is not noncombustible. Although my range is not directly against the wall. There is about a 2 inch gap(long story). The place hasn't burned down so I guess we are good.

    I am not even sure what the point of a backguard is because the newer instructions say you still need non combustible materials 6 inches below and atleast equal in height of backguard above. So according to those instructions I would need a 24 inch high non combustible surface behind my range which is more than what it says for island trim. So island trim 0 clearance only needs 6 inch high noncombustible surface but a 24 inch high backguard would need a 24 inch non combustible surface. I don't get it unless I am reading it wrong.



  • last month

    What we are trying to avoid with wall studs (and I suppose where applicable sheet rock paper) is long term pyrolysis that leads to potential combustion. The temperature that can induce this is believed to be well below that which causes wood to rapidly char. It seems to be a combination of temperature and time, and may be as low as 170F for a large number of hours (need not be continuous). Reviewing the document in the link below may help. If one's tile only reaches hot house water temperature of 120F, then I think you would be safe. Note that the temperature behind the tile may well be close to that on the exposed surface. Even 1.25-inch soapstone (rock) has fairly high thermal conductivity, so would need to be air gapped from wood if subject to high heat on one side.

    https://www.warrenforensics.com/wp-content/uploads/2016/06/PUBLICATION-Low_Temperature_Ignition_Wood-.pdf

  • PRO
    last month

    As @kaseki said, temperature the wall reaches and sustains in normal use is what would determine if the wall needs to be non-combustible or protected by an air gap.


    If normal operating temperatures aren't high enough to be an issue then the only concern is protection from transient events like a pan flare up. In that case a protective surface over a combustible wall is fine, as the high heat event isn't expected to last long enough to overheat the wall.

  • last month

    You wrote initially, " Hi, all..considering the Blue Star Range (or more likely, Range Top)". I thought that is what you were installing a rangetop and all my comments were about that.

    EOM.

  • last month

    If you e-mail Bluestar, they get back to you pretty quick. I just purchased the 30" open burner range, its an awesome cooktop! If you cook with a wok, just remove the grate and the wok sits right in the well directly on top of the burner! No need for a wok ring! The Garland open burners are in a class of their own! I know a range top is different, but Bluestar told me they want the range as close to the back wall as possible.

  • last month

    If the current BlueStar manual says 6 inches of noncombustible material like tile is acceptable for zero clearance, then that’s what counts. Installers and inspectors go by the manufacturer’s latest specs, not old forum posts. Just double check with your local inspector to be safe, but if you’re following the current manual you should be fine without the backguard