10' duct = too big??

17 years ago

Aargh.

So, just when I thought we had landed on hood (Independent, 42x27, 1200 cfm, chimney style), DH brings up a concern re. size of duct. He notes that 10" is a v. big hole and will lead to cold air coming in.

Researched extensively before choosing this one (Prestige and MA also contenders.) Stove = 36" BS, all burners, and I cook heavily. So, lots of smoke and smells with which to deal.

In our application, venting is to outside wall directly, after relatively short run up wall (to 9' ceiling).

Thoughts? Help!

Comments (6)

  • 17 years ago

    Umm. That should be 10"!

  • 17 years ago

    That's what a backdraft damper is for: it prevents cold air from blowing backwards down your vent. As long as you have that, it's no problem. And, in every other way, 10'' duct is superior to smaller duct.

    Sounds like a great choice of hoods and installation. Stick with it!

  • 17 years ago

    I have a 10" duct, but it is horizontal, running about 6 feet. I can imagine if a large duct with a long vertical run were to be installed, it could set up a plunge of cooled air falling through by convection. The damper on my duct flaps in the wind occasionally, but seems to exclude cold pretty well.
    Casey

  • 17 years ago

    Venice_2008
    I have a similar setup with a Wolf hood and don't have any issues with the cold here in Chicago. I have never had issues with the backdraft damper flapping either.

  • 17 years ago

    Thanks to everyone for your reassurance -- just what I was hoping to hear. I didn't see how it could be an issue, as it didn't come up in any of the extensive, near-obsessional research I did, but one never knows ...

    Will share with DH, and I think we'll be sticking to the plan!

  • 17 years ago

    Duct diameter should be sized so that the cfm that are actually pulled (pushed) by the fan keeps the effluent at a velocity that aids removal rather than condensation of grease in the duct. Historically, the preferred range per ASHRAE and others was 1000 to 2000 feet per minute. I recently came across, but haven't had time to read, a paper at www.Greenheck.com that asserted (IIRC) that new evidence points to 500 feet per minute as being better for kitchens. The older ASHRAE flow range was claimed to be optimal for industrial dusts. I can't recommend the new value without more investigation, but it should be considered.

    This drop in desired velocity implies using larger diameter ducts than needed before, given that cfm is determined more by the hood and cooking requirements. Bottom line is that if a 10-inch duct will physically fit, and you can move air at at least 500 fpm on maximum through it, then use it. As noted above, the damper will handle the backdraft, and insulating the duct up to the damper will help reduce any moisture condensation at sub freezing temperatures if the duct is subjected to them.

    kas