LED 'fluorescent' bulbs for closets

16 years ago

i came across these in my travels while searching out acceptable (small) closet lighting that IS NOT fluorescent and can also be hardwired. it seems my GC is fixated on CFLs and seems to think they are the only means of illumination. i refuse to use them. hate the light, hate the mercury. anyway, it seems to me i could just swing by the home depot and buy a few fixtures that accept the fluorescent tubes and just stick these in and, voila! ...LED closet lighting at reasonable cost, that also should be deemed acceptable by code. i also should mention: i will wall mount above the inside of the closet door.

am i right, or am i missing something (which i admit, happens quite frequently).

thanks for any help.

Here is a link that might be useful: LED

Comments (14)

  • 16 years ago

    LED lighting is not included in the NEC.

    It will be up to the AHJ if it can be used, and they could decline.

  • 16 years ago

    Until the NEC includes these new lamps in their closet lighting section they must be considered as incandescent and would need to meet the distance requirements set forth for enclosed incandescent lamps in closets. In other words, if they are in enclosures, they would be allowed to take the place of enclosed incandescent fixtures in closets rather than fluorescent fixtures (which can be exposed and closer to the closet storage). Be aware that the cool white light is probably at least as unpleasant to most people as a fluorescent light.

    Since the fluorescent fixture must be be rewired to bypass the ballast and starter, this is not a DIY project and I doubt the fixture would be legal for use without a UL test sticker for the new configuration.

  • 16 years ago

    Actually LED lamps for closets are specifically included in the 08 edition of the NEC and it applies the same rules to LED lamps as for incandescent lamps.

  • 16 years ago

    In general, an enclosed incandescent or LED light fixture can be used above the door in a shallow (non-walk-in) closet if the depth of the closet is equal to or greater than 24" plus the thickness of the fixture (ie, 24" or more clearance between the face of the fixture to the back of the closet).

    Electricians sometimes need to be shown section 410.8 of the NEC since they are so accustomed to using fluorescent fixtures in closets (because most shallow closets are not more than 24" deep).

  • 16 years ago

    am i missing something

    I think so.

    Super bright white LEDs put out a harsh white light, in my opinion. You may not like it.

    That tube appears to have a directional light pattern. The light most likely would shine directly toward the back top of the closet if the fixture was mounted on the wall above the door, more so than a regular fluorescent.

    You must remove the starter and ballast from the T8 fixture or bypass them, according the the fine print at the bottom of the linked web page. Do you know how to do that? Would the installation still pass code if that was done? I don't know for sure, but probably not

    They claim long life and low total cost of ownership, but what else would they say at $55 a pop? Besides the LEDs in there, there is a driver board. If it isn't engineered properly and/or uses el cheapo components or construction, it might fail in a relatively short time. You would then be out $55 for light bulb. Since this product has no track record, that it a risk you would be taking.

  • 16 years ago

    Kate, no idea - on the LED lights, but just want to say I'm with you on the CFL's -- the light is horrible! Fortunately, my electrician doesn't like them! Good luck!

  • 16 years ago

    i ended up calling the township building department and left a message to speak with the electrical inspector. he called me back (can you believe it?!) and i just asked what i might use aside from CFLs and i just about fell on the floor: i made no mention of the possibility of using LED fluorescent tubes at ALL; he came right out and told me he uses the fluorescent tube fixtures with the LED tubes in his home! he was really great and gave me his local contact so we don't have to worry about having the LED tube work in the fluorescent fixture.
    happy to take this off my list of "things to do"!

  • 16 years ago

    kate, the electrical inspector did not mean to suggest that the LED fixture can be installed as if it were a fluorescent/CFL fixture, only that it can be installed as if it were an incandescent fixture which you already knew.

    What it appears you learned from the inspector is that he knows a source for an enclosed lamp UL labeled fixture that can take the LED lamp without modification and that is good news.

    However, a surface mounted LED fixture must still have an enclosed lamp and must be at least 12" from the storage zone (24" from the back and side walls of the closet below a height of 6 ft. and 12" above 6 ft.) therefore it can only be used above the door of a closet deeper than 27 inches (if the fixture is 3 inches deep) and 48 inches wide (if the fixture is 24 inches long).

  • 16 years ago

    The 2008 NEC does allow special LED fixtures to be surface mounted closer to and even within the "storage space" if it is specifically listed for that use and I believe the manufacturer would indicate any other limitations in their installation instructions.

    So far I have not found any of these fixtures for sale but perhaps you local inspector has. Be sure it operates on line voltage power. Using such a fixture would require that the 2008 NEC (NFPA 70) be referenced in the applicable building code.

  • 16 years ago

    To clarify: So far I've only found battery operated LED lights identified as suitable for use within a foot of a closet "storage space". If anyone knows of a line voltage version please let me know.

    2008 NEC:

    410.16 Luminaires in Clothes Closets.

    (A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
    -(1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
    -(2) A surface-mounted or recessed fluorescent luminaire
    -(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area

    (B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.

    (C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
    -(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
    -(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
    -(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
    -(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
    -(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.

  • 16 years ago

    from what i understand the LED tube i posted above is an enclosed tube; i also plan on getting an enclosed fixture. i admit however, you lost me on the rest. too technical!

  • 16 years ago

    It's not really complicated; LED light fixtures surface-mounted above the door of a closet must have a "completely enclosed" lamp/bulb and have a minimum 24 inch clearance from the back wall of the closet.

    This requirement is the same as has been required for incandescent fixtures for decades. Fluorescent fixtures can have an unenclosed/exposed lamp/bulb and can have 6 inches less clearance to the back wall.

    There is a clearance exception for LED fixtures that are "identified" for use in a closet. Information on such fixtures is very difficult to find so if you know of one that is not battery powered or part of the closet rod, I would be very interested to know the brand and model number.

  • 16 years ago

    got it. thanks very much, macv. and yes, i've not come up with an LED light made exclusively for closet use which is the problem. i've seen a few battery operated LEDs which hardly seem worth the effort since instead of changing bulbs, i'd be changing batteries. stupid. i'll let you know how this works out, or if i spot another solution. please do the same if you run across anything!

  • 16 years ago

    For new construction I just make the closets over 27 inches deep.