mikeyvon

need radiant heat help

19 years ago

So, even though I am super busy trying to beat winter and get a roof up, I know I have ot be ready to get my heating system in place soon.

We are planning on using underfloor radiant heat with Al plates. We want to use a Munchkin Contender Boiler (or something similar) and have indirect domestic hot water.

My engineer that did my energy Calcs came up with a minimum load total of 68,439 BTU per hour. Using Slantfin, I came up with 50,000 BTU's per hour.

We use a woodstove to provide much of our heat. It is rated at 60,000 btu's per hour. We would like to set (and leave) the radiant and a low temp (just comfortable) and then use the wood heat to bring the warmth to where we want it.

I have talked to a few companies and I have received many different answers. They range from using 1/2" pex with no plates to 7/8" pex with plates. Many also quoted me with tankless water heaters, even though I asked to be quoted with Mod/con boiler and indirect DHW.

I am uncertain if my heat load calcs are correct (the seem high). It is a two story house with the master bed and bath in the loft. It has a large vaulted dining and living room. It is 2025 sqft, basically a 28'x44' building with about 2/3rds of second floor a loft. We have a whole bunch of large windows. I am using R21 in the walls, R38 in the ceiling, and R19 in the floor. The second floor will not be heated and I want to use a single zone.

I guess I am looking for some direction. I will be doing the majority of the work by myself. What would you do in my position?

Comments (6)

  • 18 years ago

    In my area, most of the companies that sell PEX will do some load calculations for free.

    So I think I'd pick a local supplier with good prices, and make an appointment for a sit down meeting, where I'd go over the 2 sets of numbers and look for an explanation of the difference.

  • 18 years ago

    I would take my question to one of the pro forums on the web. I know I'm not supposed to direct you away from this site, but we got help that way. There are a lot of pros out there, esp. in the northeast and into Canada, who know a LOT about it.

    Including, they directed me to buy the Bible of hydronic heat: Modern Hydronic Heating, 2nd Ed. by Siegenthaler. He's apparently the go-to guy. We got a used copy. Finally decided it would be worth the $ and it is.

    We're having someone experienced in hydronic heating do the load calcs and the system design. We have a GC on our new house. But we will have right of approval on the system design. To be able to intelligently critique his design, we figure we need a good general education ourselves.

    I'd ask the pros about the calcs.

    Here is a link that might be useful: modern hydronic heating, 2nd ed

  • 18 years ago

    What methods did they use? Proper Floor heating requires much more than just BTU requirements. Everything can change from room to room. Required loops, GPM, fluid temp, etc.

  • 18 years ago

    rabadger - some of the companies that gave me quotes did figure required loops and other stuff. I will have to get it out when I am at home and look it up. We are doing a single zone.

    My problem is I have gotten different answers from different companies and need to figure out which way to go.

  • 18 years ago

    Diff. quotes with identical equipment?

  • 18 years ago

    A good site to visit is radiantpanelassociation.org - you can click on the radnet online link from there. I also enjoyed reading the info at radiantdesigninstitute.com.

    Just curious: what design temperature did you use for your heat loss calcs? In just a rough comparison of your house to ours, it does seem as if your calculated heat loss might be high. The heat loss calcs we did for our house 3 yrs ago came out to about 67,000 btu/hr at our design temp of -47F. We've been heating for two years now and, judging by duty cycles on the boiler during cold episodes below our design temp, our calcs were a bit higher than our actual heat loss has proven to be. Our system consists of an oil-fired boiler, a tekmar 260 controller and 10 zones (valve controlled, one pump), all thin-slab hydronic heating about 3,300 sq ft living space and 400 sq ft garage.