Replacing Heat Pump - Advice??

16 years ago

Hope I posted this question in the right place, if not please move to correct section...

I live in West Central Florida, 30 minutes north of Tampa. I'm looking to replace my 10 year old 5-ton Lennox heat pump. The compressor recently seized and is now grounded-out, at least that how it was explained to me by the technician who diagnosed the problem. Last spring, I had the my 3200 sqft house re-zoned and added a 2-ton HP (handles master BR & bath + bonus room = approx 900 sqft). So I'm looking to replace the old 5-ton HP with a 4-ton HP to handle the remaining 2300 sqft.

I have focused on selecting a reputable contractor first then equipment second.

I have narrowed down my search to 2 very reputable local contractors (NATE certified, A+ BBB ratings with many excellent referrals). I have listed below which models each one is recommending. Price wise, they are very close to one another.

FIRST Contractor;

Is recommending an AMERICAN STANDARD split system;

- Heritage 15 Heat Pump # 4A6H5048E10 (4-Ton / 16.5 Seer / Single Speed compressor)

- Ultimate Air Handler # 4TEE3F65B (4-Ton / Variable Speed/ 10KW strips)

--- Additional Services offered; Flushing of copper lines w/R11 & Nitrogen, fix and/or modify any duct work, also recommends adding additional return, will verify that proper static pressure is achieved.

SECOND Contractor;

Is recommending an BRYANT split system;

-Preferred Series Heat Pump # 226ANA048000 (4-Ton / 16 Seer / 2-Speed compressor)

-Preferred Series Air Handler # FV4CNF005T00 (5-Ton / Variable Speed / 10KW strips / UV Light)

--- Additional Services offered; Replacing all copper lines, fix and/or modify any duct work also recommends adding additional return, will verify that proper static pressure is achieved.

Now these are my questions and/or concerns;

- I believe (from what I have been told) that a 2 speed compressor will makes a system more efficient. By running a the lower speed more often that at high speed. Am I correct??

--- If so; I'm leaning towards the BRYANT system because of it has a 2 speed compressor. But my concern is that Bryant's website shows the Preferred Series compressors as ONLY being a single speed. I asked the 2nd contractor about this and he states that these are very new units (about 6 months old) and are based on the Evolution series compressor models (which are 2 speed). He also states that Bryant's website may not yet be updated with these newer units. Can anyone confirm this??

I'd like to make sure these are correctly matched systems? And I'm hoping these systems qualify for the $1500 Tax Credit?

Any and all advice is appreciated!

Comments (6)

  • 16 years ago

    Are they downsizing (likely correctly so) after verification that the system was oversized with a load calculation?

    The American Standard is a nice system, and that air handler is certainly not to be labeled as a "4 ton" though it is a proper match with that system and likely needed to make the tax credit requirements. It is a large air handler, and its factory airflow setting should be adjusted to meet a 4 ton's requirements (otherwise could be loud blowing its factory set airflow).

    The Bryant system model number is incorrect and should be 266ANA048000. I don't believe it's on the website yet since its a new model, so you were probably seeing the 265A single stage Preferred heat pumps when you were researching. The contractor is correct in a sense; these models were designed specifically to meet the tax credit requirements in the higher tonnages. I believe you were quoted the Legacy series 2-stage unit rather than the Performance series 2-stage unit, both of which are 2-stage.

  • 16 years ago

    The Bryant rates at 16 SEER, 12.60 EER and 9 HSPF. The A-S gets 15 SEER, 12.50 EER and 8.5 HSPF. Both qualify for the tax credit.

    As for single stage vs 2 stage, gotta look at the specs. The Heritage 15 has some good latent (humidity) removal ratios, better than their 2 stage. Not sure about Bryant. The low capacity on the 2 stage with the exception of the Heritage 20 is 75-80% of high so not a real big difference. So there may not be much of an advantage of the 2 stage, especially if the price is higher.

    How did they determine 4 tons? Bigger isn't better. Hopefully they measured the house and calculated.

  • 16 years ago

    Thanks for the quick responses!

    Both contractor didn't measure the house or use a Load Calculator, but both did offer to have it done if I really wanted one. I can understand their unwillingness to do a Load Calc test if they aren't guaranteed to get the job. They both used the the Square-Footage rule to come up the size of the unit. Both approximated about 550 sqft per ton.

    I did download a Load Calc program called "HVAC-Calc Residential 4". I ran thru it and plugged in all my house data (room sqft, window info...etc), it took me about 2+ hours to go thru the whole process. Granted I didn't know how to exectly answer every question (being a non-HVAC guy), so I used the default setting for the items I was unsure about. I can see why most dealers would charge for this up front. ;-)

    The HVAC-Calc program came up with a recommended 3 ton unit, but again, I not sure I have correctly entered all the data. If you guys would like I can post back the results, just let me know what figures you would like for me to post.

    As for a series related question...What's the major differences between the Preferred and Legacy lines?? Is it worth approximate 500 bucks to jump up to a Preferred from the Legacy series??

    Thanks again for your advice!

  • 16 years ago

    BTW...Both contractor did preform an extensive inspection of my current setup. They inspected the attic to see how my current duct system is configured and both recommended to add and additional return or enlarge of one of the 3 existing ones.

  • 16 years ago

    I would definitely suggest any modifications to the return air set up, because it is probably needed (whether they recommend it or not). I would not be surprised if the 4 ton is also a bit oversized (partially confirmed with your load calc), but only a load calculation will tell for certain. Oversized equipment does not run efficiently (so the 15 SEER doesn't mean much if it's running short cycles) and tends not to last as long. If either company got the job, I'd ask that a load calc be done.

    As for the Legacy vs. Preferred 2-stage units, I do not believe there is a large difference. I don't see any uploads added to the Bryant catalog website for the 226A Legacy unit, but off the top of my head, I believe the differences are the following: compressor sound blanket on the Preferred unit (so likely resulting in a little lesser sound rating, i.e. quieter) and Evolution interface capability on the Preferred unit (which doesn't mean much if you have no plans on using Bryant's Evolution control system).

  • 16 years ago

    Dear gtgoose, I am quoting a similar unit, you did not list prices above, do you mind giving some advice as far as price what you paid and if you were happy with system and did you go with the Bryant?